Sounds like you are working with a 120/208V system?
What do you get from line to ground?

Benn Kilburn
SkyFire Energy
780-906-7807

> On Feb 13, 2018, at 9:53 AM, Eric Stikes <e...@harvesthesun.com> wrote:
> 
> I am troubleshooting a SolarEdge system with 9kW 3-Ph inverters. The system 
> is working OK but production is a bit low. There may be other factors and I 
> am looking into those too but I want to sort out this one issue: I am not too 
> familiar with 3-phase and when I ask SolarEdge about best way to connect to a 
> 3-Ph delta, they advise to stay away from the stinger and connect a 1-ph 
> inverter to L1 & L2 only, and that has worked out fine. However, This system 
> has a 3-ph inverter and L1 to L2 is reading about 215 volts from the utility. 
> L1 to L3 is the same and L2 to L3 is also about 215 volts. Perhaps this is a 
> 3-Ph WYE with just a higher than typical voltage coming from the utility 
> t-former. My thought here is that maybe the 3-ph inverters are only providing 
> 2/3 power back to the utility, or if there's some way to get to 240v L-L. The 
> existing loads are serviced by both 2-pole and 3-pole breakers but everything 
> is pretty much 1-phase I believe. I'm wondering if I should consider 
> reconfiguring the system with 1-Ph inverters tied in to only 2 of the utility 
> legs. I asked SolarEdge weeks ago but getting nothing from them. Any 
> thoughts? Thanks!
> 
> Eric Stikes
> SunHarvest Solar
> +1 (530) 798 - 3738
> www.harvesthesun.com
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> List Address: RE-wrenches@lists.re-wrenches.org
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: 
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> www.members.re-wrenches.org
> 
_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to