Kris: So many variables and potential performance concerns with fire damage depending of the number of modules involved, and how close the modules were to the fire, and/or the ambient temperature and duration to which the modules were subjected. Depending on the duration of high temperature exposure, there could be module laminate, micro-cracking, or other mechanical concerns, as well as PV wire and/or connector problems. None of which may show up with a visual inspection or a simple Isc/Voc test. An Isc and Voc test would be woefully inadequate. I highly recommend an on the ground in-situ performance assessment using an IV Curve Tracer like a Solmetric PV1000. Where are you located? PV module / string level performance assessment is a service my firm provides. I am located in the DFW TX area. Please contact me off-list if you think your client is interested. Regards, Gary Willett PE Icarus Engineering & Solar Services LLC Irving TX On 5/4/18 12:07 PM, Kristopher Schmid
wrote:
|
_______________________________________________ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org