William,

The start voltage is 285v from what I see covered on the specifications in manual.
Data sheets are not specifications, I have seen many a error on these over the years.

This voltage is way low regardless if the start voltage was 220v.
By the time the PV voltage gets dragged down when finding the VMPP it is going to be down near the low end of the range anyway.

I always like to see the VMPP up near the top of the VMPP point(but not to high!).
This means less current, which means less heat, which means longer life.

Looks like the is either a PV problem or a bad design in the first place.

Louis Segarra


-------- Original Message --------
Subject: Re: [RE-wrenches] SMA Micro-grid
From: William Miller <[email protected]>
Date: Tue, April 23, 2019 11:40 am
To: Harry Mahon <[email protected]>
Cc: RE-wrenches <[email protected]>

Mike:

Thanks for the reply. Good information. 

The AC system is 208. The data sheet indicates that for 208 the PV startup is 220. Today we have 260 VDC. That should be enough!?

I checked EMT he AC frequency in case it was on shift mode. It is right at 60.00. 

Still in waiting mode. I had always thought “waiting” was for grid reconnect timeout...

William

On Apr 23, 2019, at 8:47 AM, Harry Mahon <[email protected]> wrote:

William –
Waiting mode means the DC voltage is below the inverter start.  For SB 4000-12, that would be 285 VDC (and will work to 250VDC once that is hit).
 
If you knock on the inverter lid, the display will cycle and you will see the DC voltage displayed.
 
If the yellow LED is not on, this should not be an AC side issue.
 
I do not think the “Backup Mode” parameter would be the cause, but if the voltage check shows well above PVstart, it would be worth a call to service.  If the inverter was left in on grid mode, then it will work when the SI is creating a micro-grid with frequency within UL1741 limits.  If the system is off-grid, I would think the SB would have been set to off-grid mode rather than enabling Backup Mode to “on all” that allows switching from on-grid to off-grid parameter sets by RS485 command.
 
Best-
Mike
 
From: RE-wrenches <[email protected]> On Behalf Of William Miller
Sent: Monday, April 22, 2019 6:54 PM
To: RE-wrenches <[email protected]>
Subject: [RE-wrenches] SMA Micro-grid
 
Friends:
 
I am working on an AC coupled SMA system in an off-grid setting.  We have an SB4000-12 that was disconnected for a number of years and we reconnected it.  The inverter is stuck in the waiting mode and  will not generate power.  The Sunny Islands and Sunny Boys are connected via an RS485 communication system.
 
I suspect there is a programming step I have not yet accomplished.  I recall some years ago I programmed the other Sunny Boys for off-grid operation.  I can’t find anything in any of the manuals about how to check the programming.  I also suspect SAM tech support talked me through this and the information may not be published.
 
Does this ring a bell with any of you?  Any advice? 
 
Thanks in advance.
 
William Miller
 
Miller Solar
17395 Oak Road, Atascadero, CA 93422
805-438-5600
CA Lic. 773985
 
Quote of the day:  “If there is a job you hate, get really,
really good at it. Maybe you will hate it less.“ W. Miller
 

_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to