Hi Mac,

We worked for a while building controls for one company in Oz doing
small hydro, and I can share some observations, and things I learned
coming from a solar background:

> My first question is can you run a power system from hydro direct in the 10 
> -100 kW range?

Yes, I believe this is common in that power range to avoid battery and
BoS costs.  A DC-coupled/battery-backed approach could be used where
the water flow is seasonal or insufficient for loads, or where solar
is added.

> If so, how do you adjust for varying load?

For smaller systems with "normal" (i.e., not "low-head") turbines, the
water is pretty much either there or it isn't, so the turbine works
with constant head.  Typically, these are set up to run at full power,
and a diversion load is used to regulate RPM (and frequency for AC
systems).  For AC systems, rotor/field current can be adjusted to
regulate voltage, as you mentioned.

For the DC systems we supported, we built our control algorithm to the
turbine builder/installer's instructions, and rather than trying to
MPPT the turbine as we would for solar, the controller was set to
clamp the rectified turbine voltage to a fixed, user-adjustable value.
At installation, after the nozzles and penstock were adjusted, the
installer would manually adjust the turbine clamp voltage to maximize
charging current, then leave the voltage there indefinitely, in effect
doing MPPT once.  Our controller used a diversion load to regulate the
turbine voltage/RPM once the batteries were full.

As you scale things up, the diversion load approach would seem to get
a little silly, so adjusting the flow rate as Darryl suggested would
seem to be the better, if more complex approach.

Based on the info you gave for your customer's installation, it seems
like the automatic transfer switch is a great idea, but it's probably
not worth trying to DC-couple it if it's working well when not
clogged.

For some background and reference, here are some links to AC and DC
hydro products from the company we worked with, and an excellent
writeup of a personal small AC hydro installation that talks through
the transmission and control issues in great detail:

https://www.platypuspower.com.au/
https://ludens.cl/paradise/turbine/turbine.html
https://ludens.cl/Electron/picelc/picelc.html
https://ludens.cl/Electron/AVR/AVR.html

Again, thank you Wrenches for all the knowledge you share.

Alex MeVay

Blue Sky Energy * http://www.blueskyenergyinc.com
Genasun * http://www.genasun.com
_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to