Victron has the Quattro 10kW inverters w/ 100A pass thru and they have a good battery management for their Li battery line. They have also started to have their products UL listed. GOOD robust product and good support. Allen formerly of Magnum is cc ed here. Up to 6 Quattro units can operate in parallel. Six units 48/10000/140, for example, will provide 48kW / 60kVA output power and 840 Amps charging capacity.
> On Jul 20, 2019, at 5:13 PM, Mac Lewis <maclew...@gmail.com> wrote: > > I think Outback is the only major inverter manufacturer that can do split > phase 120/240 to that size. You have to go 3 phase for 36 kW continuous > capacity with either Schneider or SMA. > > Good luck, sounds like a fun system to design. > > On Sat, Jul 20, 2019 at 2:50 PM Lou Russo <l...@spreesolarsystems.com > <mailto:l...@spreesolarsystems.com>> wrote: > Blue Ion 2.0 with Outback or SMA. Works every time. > Blue Planet's tech support is great, the warranty is even better. > > Aloha, > > Lou Russo > l...@spreesolarsystems.com <mailto:l...@spreesolarsystems.com> > 808 345 6762 > Spree Solar Systems LLC > CT-34322 > > > > On Sat, Jul 20, 2019 at 10:36 AM Jay <jay.pe...@gmail.com > <mailto:jay.pe...@gmail.com>> wrote: > Hi Marco, > > Is the max surge 7kw, which is what is listed on line? > > Jay > Peltz Power > > On Jul 19, 2019, at 3:10 PM, Marco Mangelsdorf <ma...@pvthawaii.com > <mailto:ma...@pvthawaii.com>> wrote: > >> Seven to eight Tesla Powerwalls will get you that assuming that the service >> entrance is no bigger than 200A. >> >> marco >> >> On Friday, July 19, 2019, Jason Szumlanski >> <ja...@floridasolardesigngroup.com >> <mailto:ja...@floridasolardesigngroup.com>> wrote: >> What are current popular options for battery based systems in the 100kWh >> range? Preferably Lithium. >> >> Also, what inverter pairing is suggested with total stacked capacity of >> 36kW, 120/240V? >> >> This is slightly larger than some of the systems I have worked with >> recently. I'm a bit out of the loop, particularly on the battery side of >> things. >> >> Jason Szumlanski >> Florida Solar Design Group >> >> _______________________________________________ >> List sponsored by Redwood Alliance >> >> List Address: RE-wrenches@lists.re-wrenches.org >> <mailto:RE-wrenches@lists.re-wrenches.org> >> >> Change listserver email address & settings: >> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org >> <http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org> >> >> List-Archive: >> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html >> <http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html> >> >> List rules & etiquette: >> www.re-wrenches.org/etiquette.htm <http://www.re-wrenches.org/etiquette.htm> >> >> Check out or update participant bios: >> www.members.re-wrenches.org <http://www.members.re-wrenches.org/> >> > _______________________________________________ > List sponsored by Redwood Alliance > > List Address: RE-wrenches@lists.re-wrenches.org > <mailto:RE-wrenches@lists.re-wrenches.org> > > Change listserver email address & settings: > http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org > <http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org> > > List-Archive: > http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html > <http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html> > > List rules & etiquette: > www.re-wrenches.org/etiquette.htm <http://www.re-wrenches.org/etiquette.htm> > > Check out or update participant bios: > www.members.re-wrenches.org <http://www.members.re-wrenches.org/> > > _______________________________________________ > List sponsored by Redwood Alliance > > List Address: RE-wrenches@lists.re-wrenches.org > <mailto:RE-wrenches@lists.re-wrenches.org> > > Change listserver email address & settings: > http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org > <http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org> > > List-Archive: > http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html > <http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html> > > List rules & etiquette: > www.re-wrenches.org/etiquette.htm <http://www.re-wrenches.org/etiquette.htm> > > Check out or update participant bios: > www.members.re-wrenches.org <http://www.members.re-wrenches.org/> > > > > -- > > > > Mac Lewis > > "Yo solo sé que no sé nada." -Sócrates > > _______________________________________________ > List sponsored by Redwood Alliance > > List Address: RE-wrenches@lists.re-wrenches.org > > Change listserver email address & settings: > http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org > > List-Archive: > http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html > > List rules & etiquette: > www.re-wrenches.org/etiquette.htm > > Check out or update participant bios: > www.members.re-wrenches.org > > t...@swnl.net > <blocked::mailto:t...@swnl.net%22%20%5Co%20%22blocked::mailto:t...@swnl.net> > www.SWNL.net > <blocked::http://www.swnl.net/%22%20%5Co%20%22blocked::http://www.swnl.net/> > Solarwinds Northernlights > Serving Mid Coast Maine & Northern California > 207-832-7574 Cl. 610-517-8401 > > Blair "TUMP" May > ******** MAINE'S CHARTER ******** > NABCEP "Certified PV Installer" > > ******** MAINE'S CHARTER ******** > Trace Xantrex "Certified" Dealer / Installer" >
_______________________________________________ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org