The day before yesterday, I tried to commission a grid-tied system with two 
Outback Radians and an Outback FM100. I got an event saying that it had a phase 
loss error on Port 2 (which is the slave). I tried looking online and in the 
manuals, and I checked all the wiring, but I could not determine the cause of 
the problem. It was after hours, so I returned to the site yesterday and spent 
2 hours on the phone with tech support, and I thought I had finally resolved 
it, but on Optics, I see that the system was throwing the same error today. It 
comes and goes. In my events history, it says "Inverter input on port 2 has 
lost phase." then it'll say "Phase Loss has cleared on Inverter port 2 input."

The interesting thing is that it continues working fine even when it says the 
fault is active. It's selling to the grid and everything just as you would 
expect it to without interruption. But of course, the flashing red light is a 
bit concerning to the customer, and I'm a bit perplexed about it myself.

Does anybody have any experience with anything like this? Does anybody have any 
ideas?

Thank you so much!!
Kienan


Maxfield Solar
maxfieldso...@hotmail.com<mailto:maxfieldso...@hotmail.com>
(801) 631-5584 (Cell)
_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to