What about installing a 200 amp breaker in the 400 amp buss box?  

We talk a lot about doing it for smaller boxes, is there a reason it won’t work 
here?

Jay
Peltz power

> On Oct 17, 2019, at 1:30 PM, Glenn Burt <glenn.b...@glbcc.com> wrote:
> 
> 
> Hi Jeff,
>  
> Seems to me if allowed in your jurisdiction, you might be best served by 
> installing a new 200A fused service disconnect ahead of the existing main 
> service panel. Or even a 400A one to allow for additional work inside (CT’s), 
> then perform a supply side connection in it. Some manufacturers of switchgear 
> have an option for lugs that accept multiple conductors, so no piercing of 
> conductors needs to happen.
>  
> Good luck,
> Glenn
>  
> From: RE-wrenches <re-wrenches-boun...@lists.re-wrenches.org> On Behalf Of 
> Jeff Clearwater
> Sent: Thursday, October 17, 2019 3:20 PM
> To: RE-wrenches <re-wrenches@lists.re-wrenches.org>
> Subject: [RE-wrenches] SolarReady Service Panel vs adding Supply Side 
> connection?
>  
> Esteemed Wrenches,
> 
> I am in need of changing out an existing 200 Amp service entrance in order to 
> accommodate a bus capable of handling a a 200 Amp Solar backfeed (41 KW 
> system) .  
> 
> PG&E is upgrading the transformer to handle the backfeed but when I proposed 
> a Siemens SolarReady 400 Amp service entrance they couldn't approve it cause 
> since the building is a shop - they classify it as commercial and require a 
> panel that can handle CTs when there is a 400 Amp service involved.
> 
> Anyone else faced with this have solutions?  What is the cheapest equipment I 
> can provide to satisfy all requirements?
> 
> We don't need to upgrade the existing 200 amp service entrance equipment for 
> load purposes - only to meet the bus requirements of backfeed.
> 
> Would it be cheaper and easier to use the existing (or new) 200 Amp 
> residential panel - not call it a 400 Amp upgrade but simply add a 200 Amp 
> Supply Side Connection?  Suggested equipment to do that in the most 
> economical manner?
> 
> Any help well appreciated!
> 
> Jeff 
> 
> 
> 
> 
> 
> 
> 
> 
> -- 
> ~~~~~~~~~~~
> Jeff Clearwater
> Village Power Design
> linkedin 
> www.villagepowerdesign.com
> cell - 413-559-9763
> ~~~~~~~~~~~~~~~~~~~~~~~
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> List Address: RE-wrenches@lists.re-wrenches.org
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: 
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> www.members.re-wrenches.org
> 
_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to