Hey now I didn’t say that!

Brian

> On Nov 3, 2019, at 10:01 AM, Mark Frye <ma...@berkeleysolar.com> wrote:
> 
> OK Brian,
> 
> So I think you are confirming that monitoring AC side voltage is an 
> acceptable way of deciding when to disconnect the GT inverters.
> 
> With my parts list, I have a delay time that would hold the GT inverters 
> off-line for some period of time (I would probably set to 1 hour) before 
> coming back on line after tipping off.
> 
> 
> Mark
> 
>> On 11/3/2019 9:53 AM, Brian Mehalic wrote:
>> With frequency-on/off, frequency power control, or other “inverter 
>> integrated” control based on battery voltage/state of charge there is also 
>> control in regards to when the ac coupled inverters come back on. And yes, 
>> this is definitely needed to prevent overcharge (or get three-stage charging 
>> from the  AC coupled system). Of course if it doesn’t work, yes the bus 
>> voltage will rise and trip the BB offline.
>> 
>> AC bus voltage will go down as soon as the ac couple inverters are kicked 
>> off, so if that’s your measured value unless your control system has a delay 
>> or other component to control reconnection and charging i think it could 
>> essentially chatter off and on and off and...
>> 
>> Brian
>> 
>>>> On Nov 3, 2019, at 9:38 AM, Mark Frye <ma...@berkeleysolar.com> wrote:
>>> 
>>> Hi William,
>>> 
>>> Thanks, you bring up issues that are important to me here.
>>> 
>>> In particular, my situation is that the GT inverter is inter-tied a couple 
>>> sub panels upstream of where I want to put the BB inverter. The distance is 
>>> long, so I am looking for a solution where I don't have to run a cable 
>>> between the two.
>>> 
>>> In general, I do wonder about using AC line voltage rise to take the Gt 
>>> inverters off line. The main goal is to prevent excess voltage at the 
>>> battery, so monitoring battery voltage is most direct, and there are simple 
>>> solutions for that.
>>> 
>>> Is AC line voltage a suitable metric for achieving the same goal?
>>> 
>>> Here is where I could use Wrench knowledge to confirm my thinking, that 
>>> being:
>>> 
>>> - With excess energy in the system, the charger moves it into the battery, 
>>> raising it's voltage until it reaches it high charging voltage set point
>>> 
>>> - Once the battery reaches it's high voltage set point, the charger stops 
>>> putting energy into the battery
>>> 
>>> - With no other place to put the excess energy, the AC voltage rises
>>> 
>>> Am I getting this right, the reason to disconnect AC coupled inverters when 
>>> the battery if full is not to prevent the batteries from being overcharged, 
>>> but rather to prevent the AC line from becoming unstable?
>>> 
>>> I am hoping this is correct and that with $200 of industrial grade devices 
>>> from Digikey I can implement a robust control that will disconnect the GT 
>>> inverters before the AC line goes so high that the BB inverter faults.
>>> 
>>> Mark
>>> 
>>> 
>>> 
>>> _______________________________________________
>>> List sponsored by Redwood Alliance
>>> 
>>> List Address: RE-wrenches@lists.re-wrenches.org
>>> 
>>> Change listserver email address & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>> 
>>> List-Archive: 
>>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>> 
>>> List rules & etiquette:
>>> www.re-wrenches.org/etiquette.htm
>>> 
>>> Check out or update participant bios:
>>> www.members.re-wrenches.org
>>> 
>> _______________________________________________
>> List sponsored by Redwood Alliance
>> 
>> List Address: RE-wrenches@lists.re-wrenches.org
>> 
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>> 
>> List-Archive: 
>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>> 
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>> 
>> Check out or update participant bios:
>> www.members.re-wrenches.org
>> 
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> List Address: RE-wrenches@lists.re-wrenches.org
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: 
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> www.members.re-wrenches.org
> 
_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to