I have been there too in most cases we have programmed in the VAC max/mins
with tighter setting so as the grid starts to go we just disconnect. I did
just do a charger instead of the inverter because the grid was generally
low on frequency but the charger just charged and l see it on optics when
that happens
Jerry

On Fri, Mar 13, 2020, 12:03 PM Jeff Clearwater <je...@villagepowerdesign.com>
wrote:

> Good Day Esteemed Wrenchers,
>
> So we are doing more work in developing countries where the grid is super
> unreliable but on for some hours almost daily.
>
> So let's say we have a grid that's on 9 AM - 11 AM and 4 PM - 7 PM each
> day but often browns-out during those hours and comes on and off during
> those hours. 230 VAC voltage can drop to 160-180 periodically or go above
> 260 in spikes.
>
> The present practice in many of these situations is for battery based
> system designers/installers is to set up an off-grid system in parallel to
> the mains but not relying on them - so the grid AC IN is not connected.
> They just install a transfer switch and manually switch or they wire a
> critical loads panel to the solar.
>
> This avoids constant switching and nuisance shut-downs from the battery
> inverter and protects it from burning out trying to handle the grid.
>
> MY QUESTION:
>
> I'm wondering what we can do to use the grid when it is up for opportunity
> charging of the batteries while at the same time not subjecting our nice
> new battery inverters to constant brown-out tripping and possibly long term
> damage.
>
> So question #1 - Is anyone using existing battery inverters but
> succesfully navigating such a grid variablity settings such that you are
> able to take advantage of the grid even if browning out often?
>
> or question #2 - Can we add some sort of high Voltage and Frequency
> tolerant battery charger to the system - keep the battery inverter/charger
> off grid - but charge the batteries from something able to handle the wonky
> grid without constantly nuisance charging or burning itself up?
>
> Your thoughts and wisdom I await!!!
>
> Best,
>
> Jeff
>
>
> --
> ~~~~~~~~~~~
> Jeff Clearwater
> Village Power Design
> linkedin <https://www.linkedin.com/in/jeff-clearwater-0622a312/>
> www.villagepowerdesign.com
> cell - 413-559-9763
> ~~~~~~~~~~~~~~~~~~~~~~~
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to