I would add to the chorus that it probably is a battery issue. Here are the symptoms that lead to that conclusion:

A) it started occurring recently,
B) it is somewhat intermittent,
C) the system has aging L 16s  (failures at 4 to 5 years are pretty  common)
D) they are the Trojan RE series  (dead cells at less than 2 years has been documented several times on this list) E) the customer is trying to equalize regularly. (which causes over heating, and accelerates cell failures)

Besides checking battery voltages, an infared camera can quickly show over heating, bad cells.  Also, I would advise the customer to only equalize when the batteries are unequal, based on specific gravity readings.

Ray Walters
Remote Solar
303 505-8760

On 4/28/20 12:20 PM, Dave Tedeyan wrote:
Steve and Jerry,
Thanks for the suggestions. I'll have to take a closer look at the battery bank next time I am out there. The solar setup is 4 strings of 3 kyocera 270's into each charge controller. So that is almost 65A @50V coming out of each charge controller for bulk. The parallel battery strings all have the same length of premade cable, so current should be balanced (unless there is a dead cell or two in there...).
Cheers,
Dave

*Dave Tedeyan, PE*
Senior Engineer | Taitem Engineering, PC

110 South Albany Street | Ithaca, NY 14850
o. _607.277.1118 x121_  f. 607.277.2119
www.taitem.com <http://www.taitem.com>

Solar •Sustainability • Energy • Design
Certified B-Corporation since 2013


On Tue, Apr 28, 2020 at 11:52 AM Jerry Shafer <[email protected] <mailto:[email protected]>> wrote:

    Sounds like a battery issue at first glance, as you EQ a battery
    it gets warm or even hot and this will effect ability to charge.
    If e en one of the L-16 is not exactly the same voltage you will
    not get to EQ untill another battery over voltages to show your
    overall volts. Need to look at each battery volts under this
    charge condition. Also if you have a battery acting up be very
    careful working around them.
    Jerry

    On Tue, Apr 28, 2020, 6:50 AM Dave Tedeyan <[email protected]
    <mailto:[email protected]>> wrote:

        Hi All,

        I've got an outback system (Radian 8048A, 2 FM80, 16 Trojan
        L16RE-B) where when the customer equalizes, the batteries
        hover right around the EQ voltage, but will often dip to 0.1v
        less. Because of this, the EQ timer does not count down
        properly, and so left to its own devices the system would
        equalize for way longer than it should, potentially forever.
        This will happen when doing an EQ from the solar on a bright
        sunny day, or the generator, or both. The customer can
        manually keep track of the time and manually stop the EQ after
        3 hours, but that is not ideal. Has anyone dealt with this
        before and have any suggestions on how they fixed it?

        This system is 3-4 years old, and the issue only started in
        the past year or so.

        Cheers,
        Dave

        *Dave Tedeyan, PE*
        Senior Engineer | Taitem Engineering, PC

        110 South Albany Street | Ithaca, NY 14850
        o. _607.277.1118 x121_  f. 607.277.2119
        www.taitem.com <http://www.taitem.com>

        Solar •Sustainability • Energy • Design
        Certified B-Corporation since 2013
        _______________________________________________
        List sponsored by Redwood Alliance

        List Address: [email protected]
        <mailto:[email protected]>

        Change listserver email address & settings:
        http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

        List-Archive:
        
http://www.mail-archive.com/[email protected]/maillist.html

        List rules & etiquette:
        www.re-wrenches.org/etiquette.htm
        <http://www.re-wrenches.org/etiquette.htm>

        Check out or update participant bios:
        www.members.re-wrenches.org <http://www.members.re-wrenches.org>

    _______________________________________________
    List sponsored by Redwood Alliance

    List Address: [email protected]
    <mailto:[email protected]>

    Change listserver email address & settings:
    http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

    List-Archive:
    http://www.mail-archive.com/[email protected]/maillist.html

    List rules & etiquette:
    www.re-wrenches.org/etiquette.htm
    <http://www.re-wrenches.org/etiquette.htm>

    Check out or update participant bios:
    www.members.re-wrenches.org <http://www.members.re-wrenches.org>


_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to