I was just at a site last week where the Enphase branch circuit breaker, outside utility disconnect breaker, and feed breaker in the main panel all tripped simultaneously, and it happened about 1 hour before I showed up onsite. The customer said it had happened 1 other time last fall but that time it was just the 1 branch circuit in the Enphase combiner panel. Interestingly the customer mentioned that he had just washed off the panels, also about 1 hour before I got there. I went on the roof and found that the installing contractor had not put on the Enphase termination caps. 1 string was wire-nutted with regular wire nuts and sitting on the roof, and the roof was damp right there. This was a fairly flat roof. The other micro trunk cable was just cut with no protection at all, tied to the rail…
Amos Post Integrity Energy W 802.763.7023 C 802.291.2188 ienergyVT.com <http://www.ienergyvt.com/> Facebook <https://www.facebook.com/integrityenergyllp?ref=hl> > On Jun 3, 2020, at 2:05 PM, Jason Szumlanski > <ja...@floridasolardesigngroup.com> wrote: > > The breaker in the main panel IS tripping simultaneously with one of the > branch circuit breakers each time. > > > > > > > On Wed, Jun 3, 2020 at 12:43 PM Jay <jay.pe...@gmail.com > <mailto:jay.pe...@gmail.com>> wrote: > A question that keeps nagging me is why do these breakers trip and not the > breaker in the main panel? > Presuming there is a 40 amp in the main > > I would have thought that given all the times the breakers have tripped at > some point that one would have tripped and I can’t understand why not? > > Jay > >> On Jun 3, 2020, at 8:27 AM, Jerry Shafer <jerrysgarag...@gmail.com >> <mailto:jerrysgarag...@gmail.com>> wrote: >> >> >> Wrenches >> Looking g at the bigger breaker tripping at the same time is very likely do >> to response time of the breaker nothing more. As l suggested in a previous >> message. Use a non bridged breaker to see if it is one or both legs that >> trip. Also an eguage will help to see what if anything leads up to the >> failure and when. >> Jerry >> Jerry >> >> On Wed, Jun 3, 2020, 7:58 AM Jason Szumlanski >> <ja...@floridasolardesigngroup.com >> <mailto:ja...@floridasolardesigngroup.com>> wrote: >> I wonder about that. Of course, it could be the "inverter output circuit" >> having a fault in the wiring still (an intermittent issue somewhere within >> the IQ cable or home run wiring). But internal to the microinverter, is it >> possible that a fault could still occur at night? I had a suggestion from >> another wrench that there are film capacitors on the AC output side, but are >> these isolated when there is no DC input? It seems unlikely that this would >> be an issue, but I have seen microinverters reporting a couple of watts at >> night (in Enlighten). I'm not sure how real that is. >> >> The overriding question I have is what kind of fault would cause BOTH a >> branch circuit and the main solar breaker to trip simultaneously? That seems >> odd to me. If any normal load branch circuit has a fault, you don't often >> see premises main breakers tripping, or even feeder circuit breakers. >> >> I got to thinking that maybe there is some kind of issue between the BR220 >> and CH240 breakers not playing nicely together. But I would think this would >> be a well-known issue because I'm sure there are tons of CH feeder breakers >> in the wild with BR branch circuits downstream. >> >> >> >> On Tue, Jun 2, 2020 at 9:25 AM <drake.chamber...@redwoodalliance.org >> <mailto:drake.chamber...@redwoodalliance.org>> wrote: >> If it trips at night, we know it is not the output from the inverters >> causing the tripping. The current must be coming from the grid. >> >> --- >> >> >> >> On 2020-06-01 12:05, Jason Szumlanski wrote: >> >>> >>> It's not weather. It's at all times of the day and night, and I confirmed >>> that there is no correlation to rain or high winds. That was my first >>> suspicion. >>> >>> >>> On Mon, Jun 1, 2020 at 10:27 AM Ray <r...@solarray.com >>> <mailto:r...@solarray.com>> wrote: >>> Is it at all weather related? Rain, or high humidity? High temperatures? >>> Do you have any indication what time of day it trips off at? >>> >>> Ray Walters >>> Remote Solar >>> 303 505-8760 >>> On 6/1/20 10:23 AM, Jason Szumlanski wrote: >>>> Well, that didn't resolve it. The main breaker and a branch circuit >>>> breaker tripped again a few days ago. It was the same branch this time. >>>> >>>> As my next diagnostic step I swapped two circuits (on which breaker they >>>> are landed). If history is a guide, it will work for about two weeks and >>>> then trip again. >>>> >>>> I'm dumbfounded. I really don't want to have to tear this whole system >>>> apart. At this point, if I have to remove all the modules, I feel that I >>>> need to replace all of the trunk cable which is an expensive proposition. >>>> I really don't know what else to do at this point. >>>> >>>> Jason >>>> >>>> >>>> On Mon, May 25, 2020, 10:43 AM Jason Szumlanski >>>> <ja...@floridasolardesigngroup.com >>>> <mailto:ja...@floridasolardesigngroup.com>> wrote: >>>> I strongly suspect the CH240 combined breaker was compromised (we will >>>> see). Since it happened that two different strings tripped, I doubt I have >>>> two microinverters with internal faults. It has to be the combined >>>> breaker. I was just surprised that branch circuit breakers were tripping >>>> simultaneously with the combined output breaker. >>>> >>>> Of all the supply side connected systems I have installed, I have never >>>> seen a combined output fusible disconnect fuse blow, but I have seen many >>>> combined output breakers tripped. I was worried early on that I would be >>>> replacing fuses constantly, but that has not been an issue whatsoever. >>>> >>>> >>>> >>>> >>>> >>>> On Thu, May 21, 2020 at 11:15 AM <scot.a...@solarcentex.com >>>> <mailto:scot.a...@solarcentex.com>> wrote: >>>> Actually, we had a IQ7 string loaded up to its max panel size and max >>>> string length and in the spring on cool, clear day, it tripped the >>>> string's associated breaker in the Enphase combiner. >>>> >>>> >>>> We reset but of course that breaker was impaired and it tripped again. We >>>> replaced and never had an issue going forward. We suspect the breaker was >>>> less than perfect from the start as we've add equally nice days since. >>>> >>>> >>>> This almost reminds me of loading up Outback FM80. It says 4,000 watts but >>>> in reality, 3,600 is the max when amps spike. I will be extra careful >>>> going forward on IQ7 string length when going to the max published... >>>> >>>> >>>> My story. >>>> >>>> >>>> Scot >>>> >>>> >>>> From: RE-wrenches <re-wrenches-boun...@lists.re-wrenches.org >>>> <mailto:re-wrenches-boun...@lists.re-wrenches.org>> On Behalf Of Jason >>>> Szumlanski >>>> Sent: Thursday, May 21, 2020 8:57 AM >>>> To: RE-wrenches <re-wrenches@lists.re-wrenches.org >>>> <mailto:re-wrenches@lists.re-wrenches.org>> >>>> Subject: [RE-wrenches] Enphase intermittent breaker trippjng >>>> >>>> >>>> I'm trying to resolve an intermittent frustrating problem with and Enphase >>>> IQ system. There are three AC Branch circuits of 9 microinverters each >>>> coming into an Enphase AC combiner. >>>> >>>> >>>> What has been happening is one of the BR220 branch circuit breakers and >>>> the combine CH240 breaker in the main backfed load center have been >>>> tripping simultaneously. It has happened about four times in the last 6 >>>> months. It was always the same branch circuit breaker, so we kept >>>> investigating that string, checking the junction box, trunk cable, and >>>> cap, etc. Finally we swapped out the BR220 breaker. >>>> >>>> >>>> Fast forward 4 weeks, and we got another call. This time a different >>>> branch circuit breaker and the main breaker tripped simultaneously. We >>>> checked that branch circuit and could not find any fault. It seems >>>> unlikely that two branch circuit breakers would be faulty, so we have now >>>> switched out the CH240 main breaker in hopes that it is the culprit. >>>> >>>> >>>> I'm not totally confident in this resolution and I have my fingers >>>> crossed. If that doesn't work, does anyone have any suggestions on another >>>> diagnostic step? These intermittent problems are a major hassle. One >>>> thought I had was to switch to a supply side interconnection with a >>>> fusible disconnect. Maybe the intermittent fault would blow one of the two >>>> line fuses so at least I could narrow it down to which line the fault is >>>> on if there is in fact a fault. >>>> >>>> >>>> I have experienced two other tripping breaker issues with Enphase systems >>>> in the past. Neither of them were systems I installed. One turned out to >>>> be branch circuits that were not properly paired up and landed on >>>> different breakers. Another time we had an inverter with an internal fault >>>> which eventually"blew up" with a loud popping noise and smoke billowing >>>> out of it. That happened after resetting a trip breaker multiple times. >>>> This case seems to be unrelated to those issues. I'm perplexed. >>>> >>>> >>>> Jason Szumlanski >>>> >>>> Florida Solar Design Group >>>> >>>> >>>> >>>> _______________________________________________ >>>> List sponsored by Redwood Alliance >>>> >>>> List Address: RE-wrenches@lists.re-wrenches.org >>>> <mailto:RE-wrenches@lists.re-wrenches.org> >>>> >>>> Change listserver email address & settings: >>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org >>>> <https://mailtrack.io/trace/link/59a7e9d723e158998873ca5baa7a638767134d27?url=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=007df91bacd1323a> >>>> >>>> List-Archive: >>>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html >>>> >>>> <https://mailtrack.io/trace/link/003d3bab0f8d81b9e77f0e336fe0653fa6b72db7?url=http%3A%2F%2Fwww.mail-archive.com%2Fre-wrenches%40lists.re-wrenches.org%2Fmaillist.html&userId=1613865&signature=60a2f4ad62308706> >>>> >>>> List rules & etiquette: >>>> www.re-wrenches.org/etiquette.htm >>>> <https://mailtrack.io/trace/link/3284432edf0e54def1f98550159b81006d7955c5?url=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm&userId=1613865&signature=c088400cda1aedeb> >>>> >>>> Check out or update participant bios: >>>> www.members.re-wrenches.org >>>> <https://mailtrack.io/trace/link/2fc898c4231f5b5aee26e16d3b288a64fe7c17f3?url=http%3A%2F%2Fwww.members.re-wrenches.org&userId=1613865&signature=05bd9402b755e279> >>>> >>>> >>>> >>>> _______________________________________________ >>>> List sponsored by Redwood Alliance >>>> >>>> List Address: RE-wrenches@lists.re-wrenches.org >>>> <mailto:RE-wrenches@lists.re-wrenches.org> >>>> >>>> Change listserver email address & settings: >>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org >>>> <https://mailtrack.io/trace/link/d46f3f44f64e6372efd2794d4d6c17baf68fbb43?url=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=b65fd411eb242ea7> >>>> >>>> List-Archive: >>>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html >>>> >>>> <https://mailtrack.io/trace/link/2c5aa8cf7a2077366b70724f854e09c89da47ac7?url=http%3A%2F%2Fwww.mail-archive.com%2Fre-wrenches%40lists.re-wrenches.org%2Fmaillist.html&userId=1613865&signature=3a7266131380e65f> >>>> >>>> List rules & etiquette: >>>> www.re-wrenches.org/etiquette.htm >>>> <https://mailtrack.io/trace/link/a3a4bb1c1a5d466c25dce75c84f438618ef73f8d?url=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm&userId=1613865&signature=95894279ccfabb34> >>>> >>>> Check out or update participant bios: >>>> www.members.re-wrenches.org >>>> <https://mailtrack.io/trace/link/413c44feecb8180ef2abedf5ae94b6fd6d9a1110?url=http%3A%2F%2Fwww.members.re-wrenches.org&userId=1613865&signature=b139dcc7b94a10d8> >>>> >>> _______________________________________________ >>> List sponsored by Redwood Alliance >>> >>> List Address: RE-wrenches@lists.re-wrenches.org >>> <mailto:RE-wrenches@lists.re-wrenches.org> >>> >>> Change listserver email address & settings: >>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org >>> <https://mailtrack.io/trace/link/62fd4148b0bc6a855a3e5d33e745dd67dea74199?url=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=991be995cf70aaf6> >>> >>> List-Archive: >>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html >>> <https://mailtrack.io/trace/link/e35567d9a108f5e52af80b7bfdb9165c3c8bdbdc?url=http%3A%2F%2Fwww.mail-archive.com%2Fre-wrenches%40lists.re-wrenches.org%2Fmaillist.html&userId=1613865&signature=eeb6342a28178352> >>> >>> List rules & etiquette: >>> www.re-wrenches.org/etiquette.htm >>> <https://mailtrack.io/trace/link/92fa6a8bde050b49d8ec1a64205892e188742a03?url=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm&userId=1613865&signature=4208b53e4a315da0> >>> >>> Check out or update participant bios: >>> www.members.re-wrenches.org >>> <https://mailtrack.io/trace/link/b626a119f96ab5c7696c3f4cfc73d0c1c8b0dafa?url=http%3A%2F%2Fwww.members.re-wrenches.org&userId=1613865&signature=2c74837929d3e812> >>> >>> <blocked.gif> >>> >>> _______________________________________________ >>> List sponsored by Redwood Alliance >>> >>> List Address: RE-wrenches@lists.re-wrenches.org >>> <mailto:RE-wrenches@lists.re-wrenches.org> >>> >>> Change listserver email address & settings: >>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org >>> <https://mailtrack.io/trace/link/b908d8767f4935c3886ebe9001d538f330d12b20?url=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=8e39eec1c56421db> >>> >>> List-Archive: >>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html >>> <https://mailtrack.io/trace/link/16965d2373a318af82cf069bea32162ad75cbe47?url=http%3A%2F%2Fwww.mail-archive.com%2Fre-wrenches%40lists.re-wrenches.org%2Fmaillist.html&userId=1613865&signature=870b4655b78e79f8> >>> >>> List rules & etiquette: >>> www.re-wrenches.org/etiquette.htm >>> <https://mailtrack.io/trace/link/a31c352c8b2966ebd43abc34865e2c4c5ce70aae?url=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm&userId=1613865&signature=d26a4a64d4957cbd> >>> >>> Check out or update participant bios: >>> www.members.re-wrenches.org >>> <https://mailtrack.io/trace/link/767a09d3a743da10080dc5f780aa2794a92720f1?url=http%3A%2F%2Fwww.members.re-wrenches.org&userId=1613865&signature=dc6a874b300dc656> >>> >> _______________________________________________ >> List sponsored by Redwood Alliance >> >> List Address: RE-wrenches@lists.re-wrenches.org >> <mailto:RE-wrenches@lists.re-wrenches.org> >> >> Change listserver email address & settings: >> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org >> <https://mailtrack.io/trace/link/51db132bfd3691cc73ae37e2ef941c888ef13948?url=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=afafa8adda749a93> >> >> List-Archive: >> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html >> <https://mailtrack.io/trace/link/bfce5e940bbedaab1e75048018b6994a5b9197e2?url=http%3A%2F%2Fwww.mail-archive.com%2Fre-wrenches%40lists.re-wrenches.org%2Fmaillist.html&userId=1613865&signature=1d0aa1a85a003066> >> >> List rules & etiquette: >> www.re-wrenches.org/etiquette.htm >> <https://mailtrack.io/trace/link/5f14ca54215f680e9a22c36b7bfefbef8063a364?url=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm&userId=1613865&signature=53df7ac8789e98df> >> >> Check out or update participant bios: >> www.members.re-wrenches.org >> <https://mailtrack.io/trace/link/bbb56d9c03c7083bf87619b1b08c8559fb0b21e3?url=http%3A%2F%2Fwww.members.re-wrenches.org&userId=1613865&signature=86fc9c809809d01d> >> >> _______________________________________________ >> List sponsored by Redwood Alliance >> >> List Address: RE-wrenches@lists.re-wrenches.org >> <mailto:RE-wrenches@lists.re-wrenches.org> >> >> Change listserver email address & settings: >> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org >> <https://mailtrack.io/trace/link/51db132bfd3691cc73ae37e2ef941c888ef13948?url=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=afafa8adda749a93> >> >> List-Archive: >> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html >> <https://mailtrack.io/trace/link/bfce5e940bbedaab1e75048018b6994a5b9197e2?url=http%3A%2F%2Fwww.mail-archive.com%2Fre-wrenches%40lists.re-wrenches.org%2Fmaillist.html&userId=1613865&signature=1d0aa1a85a003066> >> >> List rules & etiquette: >> www.re-wrenches.org/etiquette.htm >> <https://mailtrack.io/trace/link/5f14ca54215f680e9a22c36b7bfefbef8063a364?url=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm&userId=1613865&signature=53df7ac8789e98df> >> >> Check out or update participant bios: >> www.members.re-wrenches.org >> <https://mailtrack.io/trace/link/bbb56d9c03c7083bf87619b1b08c8559fb0b21e3?url=http%3A%2F%2Fwww.members.re-wrenches.org&userId=1613865&signature=86fc9c809809d01d> >> >> _______________________________________________ >> List sponsored by Redwood Alliance >> >> List Address: RE-wrenches@lists.re-wrenches.org >> <mailto:RE-wrenches@lists.re-wrenches.org> >> >> Change listserver email address & settings: >> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org >> <https://mailtrack.io/trace/link/8bb541ba99717ada1867f5a429b07edcab4c3104?url=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=532c834dc90f032d> >> >> List-Archive: >> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html >> <https://mailtrack.io/trace/link/d54b14d5cd46011596ef52ce4f5f0f8b0b7216c4?url=http%3A%2F%2Fwww.mail-archive.com%2Fre-wrenches%40lists.re-wrenches.org%2Fmaillist.html&userId=1613865&signature=228d92cf759e33e9> >> >> List rules & etiquette: >> www.re-wrenches.org/etiquette.htm >> <https://mailtrack.io/trace/link/f45c754a1f3ecd228a8d48e2d814af57ad021e32?url=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm&userId=1613865&signature=5c28fda394300e50> >> >> Check out or update participant bios: >> www.members.re-wrenches.org >> <https://mailtrack.io/trace/link/27bf5f4ddebcf4a11740381410f90a036b292358?url=http%3A%2F%2Fwww.members.re-wrenches.org&userId=1613865&signature=bc003d6f9c33ffa1> >> > _______________________________________________ > List sponsored by Redwood Alliance > > List Address: RE-wrenches@lists.re-wrenches.org > <mailto:RE-wrenches@lists.re-wrenches.org> > > Change listserver email address & settings: > http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org > <https://mailtrack.io/trace/link/8bb541ba99717ada1867f5a429b07edcab4c3104?url=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=532c834dc90f032d> > > List-Archive: > http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html > <https://mailtrack.io/trace/link/d54b14d5cd46011596ef52ce4f5f0f8b0b7216c4?url=http%3A%2F%2Fwww.mail-archive.com%2Fre-wrenches%40lists.re-wrenches.org%2Fmaillist.html&userId=1613865&signature=228d92cf759e33e9> > > List rules & etiquette: > www.re-wrenches.org/etiquette.htm > <https://mailtrack.io/trace/link/f45c754a1f3ecd228a8d48e2d814af57ad021e32?url=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm&userId=1613865&signature=5c28fda394300e50> > > Check out or update participant bios: > www.members.re-wrenches.org > <https://mailtrack.io/trace/link/27bf5f4ddebcf4a11740381410f90a036b292358?url=http%3A%2F%2Fwww.members.re-wrenches.org&userId=1613865&signature=bc003d6f9c33ffa1> > > _______________________________________________ > List sponsored by Redwood Alliance > > List Address: RE-wrenches@lists.re-wrenches.org > <mailto:RE-wrenches@lists.re-wrenches.org> > > Change listserver email address & settings: > http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org > <http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org> > > List-Archive: > http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html > <http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html> > > List rules & etiquette: > www.re-wrenches.org/etiquette.htm <http://www.re-wrenches.org/etiquette.htm> > > Check out or update participant bios: > www.members.re-wrenches.org <http://www.members.re-wrenches.org/>
_______________________________________________ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org