I need to spec battery cable for a nominal 850 vdc LFP bank. Several brands of 
power cable list their rating at a dual 600/1000v. it is my understanding that 
to be listed in this manner, the cable must pass a test apply of over 600v for 
a short period  without breakdown. But under normal operation IMO, the voltage 
is not to exceed 600v. And this test is done with AC voltage, not DC.

"UL 1277: Power and Control Tray Cable

UL 1277, the standard for electrical power and control tray cable, was recently 
updated, allowing manufacturers with UL approved tray cable to market their 
product as 600V/1kV rated. To be dual rated, products must use a recognized 1kV 
rated conductor and pass a higher voltage AC Hipot test on the completed cable. 
This test requires each insulated conductor in finished cable to withstand a 
specified voltage range for one minute without breakdown. If a product passes 
the AC Hipot test, it is suitable for 1kV use."

Am I getting this right? And If so, one should not use this 600/1000v wire if 
normal operating voltage is above 600v as is my case? Proper rating should be 
dual 1000/2000v like PV wire?

What do you experienced high voltage battery gurus use in my application? 
Thanks.