You would need a shunt trip rated @600vdc , 25 amps I'm guessing. A DC rated 
contactor might be better, but where to find either? And what control voltage 
will the ST or contactor use? I assume its grid-tie if an AHJ is involved.
The LG RESU would also require both pos and neg be switched off (ungrounded 
neg) for code compliance. You are probably best off running the battery leads 
outside to a 600vdc dp safety switch. And then back it's only 10 ga, wire
back and forth.


Kirk Herander / kirkh@vermont.solar [mailto:kirkh@vermont.solar]
Owner|Principal, VT Solar, LLC
Celebrating our 29th Anniversary 1991-2020
www.vermont.solar 
[https://nam02.safelinks.protection.outlook.com/?url=www.vermontsolarnow.com&data=02%7C01%7C%7C9f0330d75a244870112408d685311841%7C84df9e7fe9f640afb435aaaaaaaaaaaa%7C1%7C0%7C636842843233477645&sdata=0NjyuKeQbEK6245SNnk8X4XnP9Q%2B%2BqtvcALkdDghvk4%3D&reserved=0]
dba Vermont Solar Engineering
802.863.1202
On 8/13/2020 2:08:33 PM, Jerry Shafer <jerrysgarag...@gmail.com> wrote:
Wrenches
Very interesting, l have a JHA that is requiring a shunt trip for the LG 
battery, any ideas here
Jerry

On Thu, Aug 13, 2020, 11:01 AM Kirk Herander, VT Solar, LLC <vtso...@icloud.com 
[mailto:vtso...@icloud.com]> wrote:

Hello,
Any of you ever use a 120vac-enabled shunt trip breaker on the inverter output 
at the main load panel, and have it controlled by a small AC disconnect switch 
outside?
I say offgrid because I doubt any utility would grid-tie approve as an outdoor 
disco, it since it does not visibly open the inverter output power wires.

But it wound save in round-trip inverter wiring outside and back in to the load 
center, and perhaps a big AC outdoor disco in larger systems.


Kirk Herander / kirkh@vermont.solar [mailto:kirkh@vermont.solar]
Owner|Principal, VT Solar, LLC
Celebrating our 29th Anniversary 1991-2020
www.vermont.solar 
[https://nam02.safelinks.protection.outlook.com/?url=www.vermontsolarnow.com&amp;data=02%7C01%7C%7C9f0330d75a244870112408d685311841%7C84df9e7fe9f640afb435aaaaaaaaaaaa%7C1%7C0%7C636842843233477645&amp;sdata=0NjyuKeQbEK6245SNnk8X4XnP9Q%2B%2BqtvcALkdDghvk4%3D&amp;reserved=0]
dba Vermont Solar Engineering
802.863.1202
_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org 
[mailto:RE-wrenches@lists.re-wrenches.org]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org 
[http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org]

List-Archive: 
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org 
[http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org]

List rules & etiquette:
www.re-wrenches.org/etiquette.htm [http://www.re-wrenches.org/etiquette.htm]

Check out or update participant bios:
www.members.re-wrenches.org [http://www.members.re-wrenches.org]


_______________________________________________ List sponsored by Redwood 
Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver 
email address & settings: 
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org 
List-Archive: 
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & 
etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant 
bios: www.members.re-wrenches.org
_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to