Three Core 62s with a transformer is a great solution. Lots of Fronius 15s could work but you could buy a backup transformer for the difference. Contact me off-list if you need help finding transformers. SMA will also direct you to some good solutions if pressed.
Matt From: RE-wrenches <re-wrenches-boun...@lists.re-wrenches.org> On Behalf Of Chris Mason Sent: Friday, September 18, 2020 4:04 PM To: RE-wrenches <re-wrenches@lists.re-wrenches.org> Subject: [RE-wrenches] Commercial three phase inverter @208V I'm bidding a commercial rooftop of about 200KW using string inverters. The voltage is 208V 3Ph 60Hz, and I can't find an inverter over 15KW. I was hoping to use the SMA 50KW CORE 1 but everything is 480V. Any leads on a reputable inverter? -- Chris Mason Solar systems designer Generac Generators Industrial technician Comet Systems Ltd DBA Comet Solar Anguilla Cell 264.235.5670 WhatsApp 264.235.5670 Skype: netconcepts www.cometsolar.com<http://www.cometenergysystems.com/>
_______________________________________________ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org