Ive had more issues w/ propane gen sets here, then diesel, in the cold NE but, 
having been doing this for 30+  years, we’ve figured work arounds. We usually 
go w/ propane because the rest of the clients infrastructure is set up for 
propane. AND I don’t stink of diesel when the client hasn’t change the fuel 
filters or oil. Carb heaters, indoor enclosures w/ thermostatically controlled 
louvers, + 0 weight oil.  We always used the MQs or the Wackers in Humboldt, 
Ca. Bullet proof as long as one is aware of the alternator to engine crank 
bearing life span.
> On Jan 18, 2022, at 1:51 PM, Michael Morningstar <mjmornings...@gmail.com 
> <mailto:mjmornings...@gmail.com>> wrote:
> 
> I’ve installed Hundreds upon hundreds of diesel generators at elevation here 
> in the mountains of NorCal. Temps down to -15F. None have needed block 
> heaters. For under 40KW, Wrico International. Growers were getting 20-40K 
> hours out of them. They are open frame. MQ Power for an off the shelf 
> enclosed gen-set. Ray is correct in that there aren’t any decent (low rpm, 
> liquid cooled) propane generators. We won’t touch the disposable propane 
> generators like the Kohler RES and Genercrap equivalents. Oh, Wrico does 
> build legit <15kw propane generators…..they cost 14K
> 
> 
>> On Jan 18, 2022, at 10:15 AM, Ray <r...@solarray.com 
>> <mailto:r...@solarray.com>> wrote:
>> 
>> I won't go less than double the inverter rating anymore with gensets.  So 
>> the Kohler 12 kW is probably the lowest cost, decent match for the XW.  
>> Otherwise you're just over working the genset, which usually aren't designed 
>> for continuous duty.  It keeps the voltage stable enough to not disconnect 
>> when a surge (like that sewage pump) comes on.
>> 
>> As far as 1800 rpm, I don't know anything under 20 kw in propane.  The fuel 
>> consumption of a 20kw at 25% is very comparable to the 12kW at 50%.  I've 
>> been considering diesel, but just always have been worried about cold 
>> starting in the mountains.
>> Ray Walters
>> Remote Solar
>> 303 505-8760
>> On 1/18/22 9:17 AM, Tump wrote:
>>> Ray I would love to know which larger propane gen set you are suggesting. 
>>> 1800 or 3600 rpm. Air cooled or water cooled.  To my knowledge there are 
>>> very few L cooled 1800 rpm gen sets in the 12-15kW range. T
>>>> On Jan 17, 2022, at 11:11 PM, Ray <r...@solarray.com 
>>>> <mailto:r...@solarray.com>> wrote:
>>>> 
>>>> I have a question: why so small a generator?  I've always regretted under 
>>>> sizing the genny for battery charging.  Larger gensets are not as fuel 
>>>> hungry as you might think.  I was surprised recently when I did some 
>>>> calcs, and found that a larger genset would actually get slightly better 
>>>> fuel consumption at the proposed load.  
>>>> Plus the larger gensets are usually built to last longer than the portable 
>>>> stuff.
>>>> Ray Walters
>>>> Remote Solar
>>>> 303 505-8760
>>>> On 1/17/22 5:33 PM, Jeff Clearwater wrote:
>>>>> Hello Again All,
>>>>> 
>>>>> Or I'd consider suggesting propane to the customer as well.  Any 
>>>>> experience with know compatibles in propane?
>>>>> 
>>>>> txnks
>>>>> 
>>>>> jc
>>>>> 
>>>>>> Jeff Clearwater <mailto:je...@villagepowerdesign.com> January 17, 2022 
>>>>>> at 1:29 PM
>>>>>> Thanks All,
>>>>>> 
>>>>>> Aren't there any 5-8 KW gas gennys out there already set up for 2-wire 
>>>>>> start?  We do that all the time with bigger units.
>>>>>> 
>>>>>> Thanks again!
>>>>>> 
>>>>>> Best,
>>>>>> 
>>>>>> jc
>>>>> http://www.members.re-wrenches.org <http://www.members.re-wrenches.org/>
>>>>> 
>>>> _______________________________________________
>>>> List sponsored by Redwood Alliance
>>>> 
>>>> Pay optional member dues here: http://re-wrenches.org 
>>>> <http://re-wrenches.org/>
>>>> 
>>>> List Address: RE-wrenches@lists.re-wrenches.org 
>>>> <mailto:RE-wrenches@lists.re-wrenches.org>
>>>> 
>>>> Change listserver email address & settings:
>>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org 
>>>> <http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>
>>>> 
>>>> There are two list archives for searching. When one doesn't work, try the 
>>>> other:
>>>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/ 
>>>> <https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/>
>>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org 
>>>> <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org>
>>>> 
>>>> List rules & etiquette:
>>>> http://www.re-wrenches.org/etiquette.htm 
>>>> <http://www.re-wrenches.org/etiquette.htm>
>>>> 
>>>> Check out or update participant bios:
>>>> http://www.members.re-wrenches.org <http://www.members.re-wrenches.org/>
>>>> 
>>> 
>>>> Tump 
>>>> <blocked::mailto:t...@swnl.net%22%20%5Co%20%22blocked::mailto:t...@swnl.net>3...@gmail.com
>>>>  <mailto:3...@gmail.com>       www.SWNL.net 
>>>> <blocked::http://www.swnl.net/%22%20%5Co%20%22blocked::http://www.swnl.net/>
>>>>                 Solarwinds Northernlights       
>>>>        Serving Mid Coast Maine & Northern California
>>>>                          207-832-7574   Cl. 610-517-8401                   
>>>>            
>>>>                               Blair "TUMP" May
>>>>                ********  MAINE'S CHARTER ********
>>>>                       NABCEP    "Certified PV Installer" 
>>>>    
>>>>               ********  MAINE'S CHARTER ********
>>>>                   Trace Xantrex "Certified" Dealer / Installer"
>>>> 
>>> 
>>> 
>>> 
>>> 
>>> 
>>> _______________________________________________
>>> List sponsored by Redwood Alliance
>>> 
>>> Pay optional member dues here: http://re-wrenches.org 
>>> <http://re-wrenches.org/>
>>> 
>>> List Address: RE-wrenches@lists.re-wrenches.org 
>>> <mailto:RE-wrenches@lists.re-wrenches.org>
>>> 
>>> Change listserver email address & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org 
>>> <http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>
>>> 
>>> There are two list archives for searching. When one doesn't work, try the 
>>> other:
>>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/ 
>>> <https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/>
>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org 
>>> <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org>
>>> 
>>> List rules & etiquette:
>>> http://www.re-wrenches.org/etiquette.htm 
>>> <http://www.re-wrenches.org/etiquette.htm>
>>> 
>>> Check out or update participant bios:
>>> http://www.members.re-wrenches.org <http://www.members.re-wrenches.org/>
>>> 
>> _______________________________________________
>> List sponsored by Redwood Alliance
>> 
>> Pay optional member dues here: http://re-wrenches.org 
>> <http://re-wrenches.org/>
>> 
>> List Address: RE-wrenches@lists.re-wrenches.org 
>> <mailto:RE-wrenches@lists.re-wrenches.org>
>> 
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org 
>> <http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>
>> 
>> There are two list archives for searching. When one doesn't work, try the 
>> other:
>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/ 
>> <https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/>
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>> 
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm
>> 
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org
>> 
> 
> 
> 
> 
>       Michael Morningstar
> 
>       Morningstar Electric
>       PO Box 1494
>       Mount Shasta, California 96067
>       530-921-0560
>       CSLB 949635
>  
>   <SmallGif.gif>
> 
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> Pay optional member dues here: http://re-wrenches.org 
> <http://re-wrenches.org/>
> 
> List Address: RE-wrenches@lists.re-wrenches.org 
> <mailto:RE-wrenches@lists.re-wrenches.org>
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org 
> <http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>
> 
> There are two list archives for searching. When one doesn't work, try the 
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> http://www.members.re-wrenches.org
> 






"We must all learn to live together as brothers,
 or we all will perish as fools."
MLK







> Tump 
> <blocked::mailto:t...@swnl.net%22%20%5Co%20%22blocked::mailto:t...@swnl.net>3...@gmail.com
>        www.SWNL.net 
> <blocked::http://www.swnl.net/%22%20%5Co%20%22blocked::http://www.swnl.net/>
>                 Solarwinds Northernlights       
>        Serving Mid Coast Maine & Northern California
>                          207-832-7574   Cl. 610-517-8401                      
>         
>                               Blair "TUMP" May
>                ********  MAINE'S CHARTER ********
>                       NABCEP    "Certified PV Installer" 
>    
>               ********  MAINE'S CHARTER ********
>                   Trace Xantrex "Certified" Dealer / Installer"
> 



_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to