Kirpal:


Thanks for that suggestion.  The AP Smart system modules are certainly more
compact and this is a plus for me.



Do you have to have a sensor transformer and logic unit on each string?
Could more than one string be routed through one sensor coil?  This
installation will have 10 strings so that could be a lot of hardware.



Some here have asked if RSS is required on a non-dwelling unit.  My reading
of the code indicates indeed it is.  The only buildings exempt are
buildings used solely for solar equipment that are fed by ground mount
arrays.  So theoretically our ground mount systems that feed equipment in a
barn or garage should also have RSS.  Right?  This does not make sense to
me for protecting fire-fighters.  Seems like an over-reach.  Bill Brooks,
could you comment on this?  Anyone?



William



Miller Solar

17395 Oak Road, Atascadero, CA 93422

805-438-5600

www.millersolar.com

CA Lic. 773985





*From:* Kirpal [mailto:solarwo...@gmail.com]
*Sent:* Monday, January 31, 2022 5:21 PM
*To:* RE-wrenches; William Miller
*Subject:* Re: [RE-wrenches] Rapid Shutdown for Off-grid systems



Hi William.

We have had good luck with the AP Smart Rapid shutdown system.  It is
similar to the Tigo in that it sends a "heartbeat" signal to the units up
behind each solar panel over the power wires. I haven't tried the Tigos yet
but would be open to it if the opportunity presented itself.  The thing we
like about the AP Smart shutdown units is they can be attached to the solar
panels before the panels are brought up to the roof.  Makes for a quick and
tidy installation.  We found the Fire Raptor units with their incredible
amount of extra wiring and cables to be a real pain in the ass to install.
It typically takes longer to install the Fire Raptor units and manage the
wiring than it does to install the solar panels themselves. The fire
raptors are more expensive and require a seperate control wire to be run
upto the roof.  We haven't had any failures on either the fire raptor or
the AP Smart units with probably a dozen installs of each style installed
to date.  Brad Bassett at AEE has some great easy to use wiring diagrams
for both systems with Outback or Sol Ark.  All the above systems have some
requirement for either 12V or 24V power to power the signal generator.  We
typically use some version of din rail mounted 48-24v or12V power supply
and power it from the batteries so that if the inverter were to fail or the
grid the solar can still stay on..  At this stage we have settled on any of
the rapid shutdown systems except Fire Raptor.  - if you do use the Fire
Raptor - calculate a  bunch of extra time into the install for wire
management.

Hope that gives you some food for thought.

Cheers,



Sunny Regards,
Kirpal Khalsa

Oregon LRT#25
Oregon Solarworks LLC
www.oregonsolarworks.com
541-299-0402
_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to