That is correct, Jay.  You only need the rapid shutdown switch if you have IQ 
8s and an IQ System Controller.

One of the big advantages of the IQ 8 over IQ 7 when paired with storage is 
that the 1.5 PV to storage ratio does not apply, so you can install larger PV 
systems with smaller battery systems.


Cordially,

Nick Soleil

Enphase Energy Senior Product Manager

(707) 763-4784 x7267  // office

(707) 321-2937  // cell

Powering What’s Next™ | The Enphase Energy Management 
System<https://enphase.com/en-us/products-and-services/envoy>

NABCEP Certified Solar PV Installer #03262011-300

California C10 Licensed Electrician #986315

________________________________
From: RE-wrenches <re-wrenches-boun...@lists.re-wrenches.org> on behalf of Jay 
via RE-wrenches <re-wrenches@lists.re-wrenches.org>
Sent: Tuesday, July 12, 2022 3:54 PM
To: RE-wrenches <re-wrenches@lists.re-wrenches.org>
Cc: Jay <jay.pe...@gmail.com>
Subject: Re: [RE-wrenches] Enphase IQ7 versus IQ8

EXTERNAL EMAIL - Use caution when responding, clicking, and/or downloading 
attachments.





Hi Jason

And if you don’t have the smart controller/battery system then you do not need 
this proprietary rapid shut down switch correct?

Jay



On Jul 12, 2022, at 3:25 PM, Jason Szumlanski via RE-wrenches 
<re-wrenches@lists.re-wrenches.org> wrote:


Yes, they require a proprietary rapid shutdown switch that connects to the 
smart controller. This would be in addition to a visible load break disconnect 
if the utility requires it. You cannot fulfill both requirements with one 
switch, and it requires a line voltage circuit be run from the smart controller 
to the rapid shutdown switch.



On Tue, Jul 12, 2022, 5:15 PM Mark Frye via RE-wrenches 
<re-wrenches@lists.re-wrenches.org<mailto:re-wrenches@lists.re-wrenches.org>> 
wrote:

Do you need the additional switch if you use the Enphase battery?



From: RE-wrenches 
<re-wrenches-boun...@lists.re-wrenches.org<mailto:re-wrenches-boun...@lists.re-wrenches.org>>
 On Behalf Of Jason Szumlanski via RE-wrenches
Sent: Tuesday, July 12, 2022 11:38 AM
To: RE-wrenches 
<re-wrenches@lists.re-wrenches.org<mailto:re-wrenches@lists.re-wrenches.org>>
Cc: Jason Szumlanski 
<ja...@floridasolardesigngroup.com<mailto:ja...@floridasolardesigngroup.com>>
Subject: [RE-wrenches] Enphase IQ7 versus IQ8



I am trying to figure out why it is a good idea we use the IQ8 in anything 
other than a solar only backup scenario. If there are Enphase batteries 
involved, wouldn't the IQ7 do the same job on the roof? In a straight grid tied 
scenario, again the IQ7 would do the exact same thing. You would not have an 
upgrade path to solar only backup, of course.



I'm just having a hard time understanding the value proposition of the IQ8 in 
most of the situations I encounter. They cost significantly more, and you need 
an additional rapid shutdown switch when using batteries that can be quite a 
pain in some scenarios.



Am I missing something about the switching speed, energy harvest capability, or 
the way they interact with batteries that makes them better?



P.S. I am aware of the very small power output differences by model number and 
I am referring exclusively to 240 volt applications. I understand the 208 volt 
advantages of the IQ8.



Jason Szumlanski

Florida Solar Design Group

_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: 
http://re-wrenches.org<https://urldefense.com/v3/__http://re-wrenches.org__;!!J0D89H32QIeNiQ!0V6Viupc-8VYORVECQATdMKaJOpXjH6JOmgnqjF5RjB9RVhhygBgq0JWVaLGtsftGOsVhvP3evFLa1AbslfUJT9ZrYJe0CfSyQ$>

List Address: 
RE-wrenches@lists.re-wrenches.org<mailto:RE-wrenches@lists.re-wrenches.org>

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org<https://urldefense.com/v3/__http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org__;!!J0D89H32QIeNiQ!0V6Viupc-8VYORVECQATdMKaJOpXjH6JOmgnqjF5RjB9RVhhygBgq0JWVaLGtsftGOsVhvP3evFLa1AbslfUJT9ZrYISvg0nOQ$>

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/<https://urldefense.com/v3/__https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/__;!!J0D89H32QIeNiQ!0V6Viupc-8VYORVECQATdMKaJOpXjH6JOmgnqjF5RjB9RVhhygBgq0JWVaLGtsftGOsVhvP3evFLa1AbslfUJT9ZrYJj_4eGKg$>
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org<https://urldefense.com/v3/__http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org__;!!J0D89H32QIeNiQ!0V6Viupc-8VYORVECQATdMKaJOpXjH6JOmgnqjF5RjB9RVhhygBgq0JWVaLGtsftGOsVhvP3evFLa1AbslfUJT9ZrYIMpOrPjw$>

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm<https://urldefense.com/v3/__http://www.re-wrenches.org/etiquette.htm__;!!J0D89H32QIeNiQ!0V6Viupc-8VYORVECQATdMKaJOpXjH6JOmgnqjF5RjB9RVhhygBgq0JWVaLGtsftGOsVhvP3evFLa1AbslfUJT9ZrYICPduJGQ$>

Check out or update participant bios:
http://www.members.re-wrenches.org<https://urldefense.com/v3/__http://www.members.re-wrenches.org__;!!J0D89H32QIeNiQ!0V6Viupc-8VYORVECQATdMKaJOpXjH6JOmgnqjF5RjB9RVhhygBgq0JWVaLGtsftGOsVhvP3evFLa1AbslfUJT9ZrYKHzGjYsQ$>

_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: 
http://re-wrenches.org<https://urldefense.com/v3/__http://re-wrenches.org__;!!J0D89H32QIeNiQ!0V6Viupc-8VYORVECQATdMKaJOpXjH6JOmgnqjF5RjB9RVhhygBgq0JWVaLGtsftGOsVhvP3evFLa1AbslfUJT9ZrYJe0CfSyQ$>

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org<https://urldefense.com/v3/__http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org__;!!J0D89H32QIeNiQ!0V6Viupc-8VYORVECQATdMKaJOpXjH6JOmgnqjF5RjB9RVhhygBgq0JWVaLGtsftGOsVhvP3evFLa1AbslfUJT9ZrYISvg0nOQ$>

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/<https://urldefense.com/v3/__https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/__;!!J0D89H32QIeNiQ!0V6Viupc-8VYORVECQATdMKaJOpXjH6JOmgnqjF5RjB9RVhhygBgq0JWVaLGtsftGOsVhvP3evFLa1AbslfUJT9ZrYJj_4eGKg$>
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org<https://urldefense.com/v3/__http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org__;!!J0D89H32QIeNiQ!0V6Viupc-8VYORVECQATdMKaJOpXjH6JOmgnqjF5RjB9RVhhygBgq0JWVaLGtsftGOsVhvP3evFLa1AbslfUJT9ZrYIMpOrPjw$>

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm<https://urldefense.com/v3/__http://www.re-wrenches.org/etiquette.htm__;!!J0D89H32QIeNiQ!0V6Viupc-8VYORVECQATdMKaJOpXjH6JOmgnqjF5RjB9RVhhygBgq0JWVaLGtsftGOsVhvP3evFLa1AbslfUJT9ZrYICPduJGQ$>

Check out or update participant bios:
http://www.members.re-wrenches.org<https://urldefense.com/v3/__http://www.members.re-wrenches.org__;!!J0D89H32QIeNiQ!0V6Viupc-8VYORVECQATdMKaJOpXjH6JOmgnqjF5RjB9RVhhygBgq0JWVaLGtsftGOsVhvP3evFLa1AbslfUJT9ZrYKHzGjYsQ$>

_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to