Hello Drake,

Since the relay board is functioning some times, I would more suspect (1) an 
intermittent controller board or (2) corrosion on the contact area of the 
header connection. They are relatively easy to change and not too expensive. 

One thing I would test first is to unplug the ARC remote the apply AC power. 
The ARC has the ability to control when incoming AC is used. Unplugging it will 
bypass all remote function as a cause, though I highly doubt it is.

Larry Crutcher
Starlight Solar Power Systems



On Jan 18, 2023, at 7:42 PM, Drake Chamberlin via RE-wrenches 
<re-wrenches@lists.re-wrenches.org> wrote:

Hello Wrenches,

A Magnum 4024 won't charge batteries or transfer loads. The owner of the 
system, now well out of warranty, has spent hours on the phone with tech 
support and even took the unit into a Magnum authorized repair shop. The 
technician declared that it was working perfectly.

On connection to the utility grid, the ME-ARC shows no sign of seeing the 
power. Once in a great while, it will connect and start charging batteries. 
Then it will quit.

This seems to me like a matter of a relay not operating. The technician, who 
checked it out, believes that the problem is with the AC coming in. One tech 
support agent thought the same.

The inverter is 1000' plus from the transformer. The incoming voltage, with 
light loads, is 248 VAC. Shouldn't the ME-ARC at least show that it sees the 
grid, even if the voltage dropped upon connection to the point it couldn't hold 
it?

Isn't the Magnum charger pretty forgiving about voltage input? I've heard they 
can have issues with inverter-generators, but this is 60 Hz grid power.

Thank you,

Drake

Drake Chamberlin
Athens Electric LLC
Ohio Electrical Contractor’s License 44810
CO Master Electrician’s License 4526
NABCEP Certified PV Installation Professional

-- 
_______________________________________________
_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to