On Jan 28, 2023, at 5:58 PM, James Jarvis via RE-wrenches
<re-wrenches@lists.re-wrenches.org> wrote:
It would be nice if the decision was up to the owner / occupant
of the property. I, for one, do not want any random person to be
able to turn off my house or business with the flick of a
switch. I feel strongly that there is far too much fear
mongering in NEC with relation to renewable energy.
-James Jefferson Jarvis
APRS World, LLC
+1-507-454-2727
http://www.aprsworld.com/
On Sat, Jan 28, 2023 at 6:22 PM William Miller via RE-wrenches
<re-wrenches@lists.re-wrenches.org> wrote:
Esteemed wrenches:
Well if my house is on fire and the entry of fire responders
is delayed for lack of a disconnect, I choose having the
disconnect. I can worry about the charge controllers later.
Others may prioritize their charge controller over their homes…
Put a cable-tie lock in the closed position to discourage
kids from messing with it. Test it only after dark.
William
On Sat, Jan 28, 2023 at 2:32 PM William Bryce
<wlbr...@pineridgeproducts.com> wrote:
All
One thing that no one is talking about is what happens
to the MPPT charge controllers when the Battery
Disconnect trips when the charge controllers are under
full load.
Many will blow up. Try turning off the battery breaker
on a SolaArk when the charge controllers are maxed, and
see if you get lucky.
On Sat, Jan 28, 2023 at 3:27 PM William Miller via
RE-wrenches <re-wrenches@lists.re-wrenches.org> wrote:
Jeremy:
Thanks for posting the code references for those
that had never looked them up.
Chris:
What do you mean by “a disconnect for AC wiring, not
specific to which or both panel types”?
All:
Code references are handy when receiving edicts from
building officials, but not required, IMHO, for two
reasons: The contractor should already be versed in
the codes and, building departments can mandate
their own requirements above and beyond the code.
It may seem redundant to require an AC disconnect
for premise wiring as well as a DC battery
disconnect. In most cases if you disconnect the
inverter from the batteries the AC power goes off.
However if the generator is running at the time,
some battery inverters can operate when disconnected
from batteries. So to completely de-energize all
components of an off-grid home you need to
disconnect the generator and the battery leads.
In this case the home is required to have fire
sprinklers. There is pressure pump to provide flow
to these fire sprinklers-- said pump being powered
by the inverter/battery system. I am going to apply
for a waiver to remove the DC disconnect requirement
on the grounds that the pressure pump is essential
fire suppression equipment. Instead I will propose
to supply an AC disconnect (meeting all requirements
for accessibility and marking) that will disconnect
all premise wiring except the pressure pump.
By the way, I will of course be trying to apply the
logic that the voltage specification is for nominal
battery voltage and this project having a nominal 48
volt bank does not require the battery disconnect.
I will let the group know what response I receive.
Regardless of how this works in this jurisdiction, I
think these are both valid arguments worth trying in
any jurisdiction requiring the battery disconnect.
Some officials are amenable to dialog and
negotiation and some are less so.
William Miller
Miller Solar
17395 Oak Road, Atascadero, CA 93422
805-438-5600
www.millersolar.com <http://www.millersolar.com/>
CA Lic. 773985
*From:*RE-wrenches
[mailto:re-wrenches-boun...@lists.re-wrenches.org]
*On Behalf Of *Jeremy Rodriguez via RE-wrenches
*Sent:* Saturday, January 28, 2023 10:12 AM
*To:* cwar...@entech-engineering.com; RE-wrenches
*Cc:* Jeremy Rodriguez
*Subject:* Re: [RE-wrenches] Remote battery disconnects
*2020 Code Language:*
/*480.7 DC Disconnect Methods.*/
/*(A) Disconnecting Means.*/*//*/A disconnecting
means shall be provided for all ungrounded
conductors derived from a stationary battery system
with a voltage over 60 volts dc. A disconnecting
means shall be readily accessible and located within
sight of the battery system./
/*N*/*//*/*(B) Emergency Disconnect.*/*//*/For
one-family and two-family dwellings, a disconnecting
means or its remote control for a stationary battery
system shall be located at a readily accessible
location outside the building for emergency use. The
disconnect shall be labeled “EMERGENCY DISCONNECT”./
*/N/*/*(C) Disconnection of Series Battery
Circuits.*/*//*/Battery circuits exceeding 240 volts
dc nominal between conductors or to ground and
subject to field servicing shall have provisions to
disconnect the series-connected strings into
segments not exceeding 240 volts dc nominal for
maintenance by qualified persons. Non-load-break
bolted or plug-in disconnects shall be permitted./
Jeremy Rodriguez
Solar Installation / Design
All Solar, Inc.
1453 M St.
Penrose Colorado 81240
Sent by Jeremy's iPhone. Sorry for typos and shorthand.
On Jan 28, 2023, at 7:28 AM, Christopher Warfel via
RE-wrenches <re-wrenches@lists.re-wrenches.org> wrote:
Seems confusing that the AHJ is requiring a
disconnect for AC wiring, not specific to which
or both panel types, and then a dc disconnect
with no code reference. Was trying to convey a
reasonable, safe approach. A lot of bad
information from fire department solar
consultants making a lot of money fear
mongering, which has led to this type of
situation. Chris
On 1/27/2023 3:35 PM, William Miller via
RE-wrenches wrote:
Glenn:
As I wrote, a DC disconnect is required.
Here is an excerpt from the Q&A with the
building official:
4.Will you be requiring an external
disconnect to disconnect the AC output of
the inverter system from premise wiring?
Yes, as required per 230.85
5.Will you be requiring an external
disconnect to disconnect batteries from the
inverters?
Yes
If the DC disconnect was not required I
would not be wasting everyone’s time with my
post. I try to be careful about that,
researching on my own before posting and
trying to make my questions very clear. I
also try not to embarrass myself with dumb
questions, but that does happen occasionally…
William
Miller Solar
17395 Oak Road, Atascadero, CA 93422
805-438-5600
www.millersolar.com
<http://www.millersolar.com/>
CA Lic. 773985
*From:*RE-wrenches
[mailto:re-wrenches-boun...@lists.re-wrenches.org]
*On Behalf Of *Glenn Burt via RE-wrenches
*Sent:* Friday, January 27, 2023 11:46 AM
*To:* William Miller via RE-wrenches
*Cc:* Glenn Burt
*Subject:* Re: [RE-wrenches] Remote battery
disconnects
Does the AHJ really want the batteries
disconnected from conductors, or does he
really just want the inverters to stop
operating and producing AC within the house?
Obviously there is a big difference here and
it may be changing as the code evolves.
-Glenn
Sent from my 'smart'phone, so please excuse
typos and spelling errors.
------ Original message------
*From: *William Miller via RE-wrenches
*Date: *Fri, Jan 27, 2023 2:26 PM
*To: *RE-wrenches;
*Cc: *William Miller;
*Subject:*[RE-wrenches] Remote battery
disconnects
Friends:
We have a large-ish residential off-grid
system install coming up. The AHJ has said
they will require a remote battery
disconnect. I suspect there will be fire
sprinkler controls and a pressure pump that
would become inoperable if this system were
engaged. In this case we will apply for a
waiver.
The last time this was discussed here as far
as I can find was October of 2020. At that
time no one suggested any specific battery
disconnect equipment.
To further clarify my needs: There will be 4
or 5 Radian 8048 inverters (5 or 6 4/0
battery circuits, ~350A each) and two 175
amp PV recombiner outputs. That is 6 poles
of high amperage DC disconnects.
The battery array will be either a UnigyII
VRLA or a lithium of a brand yet to be
determined. In the case of lithium we will
look for a system that can remotely enable a
BMS shutdown. In the case of a VRLA
lead-acid, we will not have that luxury.
I have done some considerable research and
have not found viable, high amperage,
remotely activated shutdown equipment.
I am wondering what hardware others may be
using to achieve remote battery
disconnecting in these types of cases..
William
Miller Solar
17395 Oak Road, Atascadero, CA 93422
805-438-5600 <tel:805-438-5600>
www.millersolar.com
<http://www.millersolar.com/>
CA Lic. 773985
_______________________________________________
List sponsored by Redwood Alliance
Pay optional member dues here: http://re-wrenches.org
List Address: RE-wrenches@lists.re-wrenches.org
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
There are two list archives for searching. When one
doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
http://www.members.re-wrenches.org
--
William Miller
Miller Solar.com
895-438-5600
www.millersolar.com <http://www.millersolar.com>
_______________________________________________
List sponsored by Redwood Alliance
Pay optional member dues here: http://re-wrenches.org
List Address: RE-wrenches@lists.re-wrenches.org
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
There are two list archives for searching. When one doesn't
work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
http://www.members.re-wrenches.org
_______________________________________________
List sponsored by Redwood Alliance
Pay optional member dues here: http://re-wrenches.org
List Address: RE-wrenches@lists.re-wrenches.org
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
There are two list archives for searching. When one doesn't
work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
http://www.members.re-wrenches.org