Hi Wrenches -

Occasionally we will do supply side connection for our PV systems. As of
1/1/2023 in CA, we follow the 2020 NEC 705.11 Supply-Side Source
Connections section. Recently, an inspector asked us to comply with the
following:

230.46 Spliced and Tapped Conductors
Service-entrance conductors shall be permitted to be spliced or tapped in
accordance with 110.14, 300.5(E), 300.13, and 300.15. Power distribution
blocks, pressure connectors, and devices for splices and taps shall be
listed. Power distribution blocks installed on service conductors shall be
marked "suitable for use on the line side of the service equipment" or
equivalent.
Effective January 1, 2023, pressure connectors and devices for splices and
taps installed on service conductors shall be marked "suitable for use on
the line side of the service equipment" or equivalent.



When we reached out to one supplier of insulation piercing connectors
(ILSCO), they responded: "We are still in testing, I just checked and from
what I see there are no products listed for this new requirement yet by any
manufacturer."

Has anyone bumped into this before and/or have any proposed solutions?

Best, August
Luminalt
_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to