Most firefighters are not electrical engineers; nor are most insurance agents. However both of those groups are stakeholders with influence over codes and standards. Some may say too much influence, but the fact of the matter is that code making is a group/consensus process, and very often none of the groups get exactly what they want (in fact sometimes a group accepts exactly what it doesn't want to leverage that for something they do; yes it often smacks of politics). I would appeal to y'all to submit a proposal for the 2026 NEC® - they are due by September of this year. Better yet would be to circulate language that this, or some other, group can work on, agree on, write a solid technical justification for, and sign their names to and submit - the more stakeholders that support a proposal the more weight it has.

It seems that the PV Industry Forum, or another similar body, may again begin work to develop PV and storage industry stakeholder-consensus PIs to submit; in the past this was a very successful endeavor. I'll post on this list if and when that happens so that anyone that is interested can get involved, but don't let that possibility keep you from submitting any PIs on your own.

Maybe in the meantime, a control system that shuts off the PV, and then the batteries, would be worth designing.

Brian Mehalic




On Wed, Feb 1, 2023 at 2:10 PM James Jefferson Jarvis via RE-wrenches <re-wrenches@lists.re-wrenches.org> wrote:



    On 2/1/2023 2:58 PM, Starlight via RE-wrenches wrote:
    > Have you (or any) installed surge suppression on the PV input
    side to
    > clamp the open circuit voltage surge?

    That's not where the issue is and isn't really a solution. As I
    explained in my previous e-mail, the issue is the open circuit on the
    output leaves no where for the energy in the MPPT controllers
    inductor
    to go and the only option is for the voltage to rise until it finds
    somewhere to go.

    Surge suppressors, such as sold by Midnite Solar, are nothing more
    than
    Metal Oxide Varistors. Or in the case of Delta, they are pieces of
    wire
    in sand. They require large rise in voltage before they conduct.

    MOVs are sometimes found on the battery side of inverters and charge
    controllers, but their clamp time and voltage before clamping
    requires
    additional circuitry that works faster to protect fragile
    semiconductors.


    If you are proposing using a surge supressor to regulate the
    voltage of
    an island between a charge controller and an inverter when the
    battery
    is disconnected, that's also a no go. Once the MOV clamps, it stays
    clamped until voltage goes essentially to zero or until it blows up.
    It's not a regulator.

    -

    To further stir the pot, it is definitely possible to design
    electronics
    that can deal with load dumps and survive most anything. Aerospace
    electronics come pretty close. But all that costs money and takes
    space
    to do. Are we comfortable with requiring $16,000 charge
    controllers so
    they can handle load dumps reliably from a poorly thought out NEC
    requirement? I think the fossil fuel industry would be very happy
    with
    the cost of renewable energy electronics being an order of magnitude
    more expensive.




    >
    > Larry Crutcher
    > Starlight Solar Power Systems
    >
    >
    >
    > On Feb 1, 2023, at 1:23 PM, William Bryce via RE-wrenches
    > <re-wrenches@lists.re-wrenches.org
    > <mailto:re-wrenches@lists.re-wrenches.org>> wrote:
    >
    > I can also backup what Jim has said, and have seen the same gear
    > destroyed by removing the battery abruptly when the controller
    is under
    > heavy load. They can die, and sometimes die spectacularly.
    >
    > Have seen SolArk inverters integrated MPPT controllers blow up when
    > lithium battery BMS disconnects. Not a field fixable issue.
    >
    > Just flip off the breaker when the solar is working hard and and
    the
    > SolArk will give up the smoke.
    >
    > Like I originally said, it’s the non talked about issue that is
    a big
    > issue depending on what gear your using.
    >
    > On Wed, Feb 1, 2023 at 2:49 PM James Jefferson Jarvis via
    RE-wrenches
    > <re-wrenches@lists.re-wrenches.org
    > <mailto:re-wrenches@lists.re-wrenches.org>> wrote:
    >
    >
    >
    >     On 2/1/2023 12:25 PM, Alex MeVay via RE-wrenches wrote:
    >      > Although our controllers are probably smaller than what
    you would be
    >      > considering in this discussion, surviving a load dump
    (suddenly
    >      > disconnected battery) is an engineering requirement for
    us, and
    >     likely
    >      > would be for other responsible MFG's on this list
    (boB?).  The charge
    >      > controller can either handle full input voltage on the
    output, or
    >      > there is a comparator that will shut the controller down
    instantly
    >      > when the output voltage gets too high.
    >
    >     So that's part of the picture.
    >
    >     The other part of the picture is the rest of the system. The
    discussion
    >     and what NEC is mandating is that the battery be
    disconnected. As
    >     far as
    >     I can tell, there isn't an explicit requirement in all cases
    that
    >     all of
    >     the power inputs into the system are all going to go away at
    exactly
    >     the
    >     same time .... or ever. This leaves things like charge
    controllers
    >     getting input power potentially from PV or wind or grid or
    generator or
    >     something else. And nothing in the NEC, as far as I can tell, is
    >     mandating that all of the DC loads be disconnected. So the
    loads are
    >     online. Now the regulation circuit (switching power supply
    in the case
    >     of a MPPT controller) is regulating variable loads and
    nothing is
    >     providing substantial resistance to change. Normally the
    battery is
    >     acting like a very very very big capacitor. But without the
    battery,
    >     there isn't enough damping in the control loops and voltage
    stability
    >     will suffer. This is where you get 250 volts on your
    normally 48 volt
    >     battery bus. Or 3 volts. Or -80 volts. Or all of those in a
    fraction of
    >     second. This sort of thing is hard on electronics and will cause
    >     failures.
    >
    >
    >     Alex's comment about Genasun's controllers handling full
    input voltage
    >     on the output is probably unique to their niche product.
    Looking at
    >     their biggest controller, it appears to support VOC of 34
    volts. At 34
    >     volts, he can use 50V or 100V rated components on his
    output. For a
    >     150V
    >     input controller, you probably can. But you wouldn't because it
    >     would be
    >     too expensive. But on a 600V or 1000V controller, there's
    just no way
    >     that you do that because 1000V rated components are big and
    expensive
    >     and their spacing requirements are huge compared 100V level
    sort of
    >     stuff. So the way bigger MPPT controllers deal with load
    dump is with
    >     transient voltage supression or other diodes to handle the
    voltage
    >     spike
    >     caused by the inductor when the load goes away. When operated in
    >     parameters, these parts don't wear out. But it can be
    interesting to
    >     size them adequately to account for inductance elsewhere in
    the system
    >     adding to voltage and energy that has to be absorbed.
    >
    >
    >     There is a very simple experiment that anybody can perform
    to see how
    >     equipment handles a load dump: Simply wait for a sunny day
    and turn off
    >     the battery breaker. If no magic smoke was released, turn
    back on
    >     battery breaker. If still no magic smoke was released, then
    great, your
    >     system survived a load dump.
    >
    >     If you are at all uncomfortable doing this and/or your
    system gets
    >     destroyed in the process, think back to my earlier security
    comments
    >     about having a self destruct switch on the outside of your
    building
    >     allowing anyone walking by to do this experiment for you.
    >
    >     I have personally destroyed Outback, Midnite, and Morningstar
    >     controllers inadvertently or intentionally doing load dumps
    by shutting
    >     off their output breaker. Typically the TVS diodes short out and
    >     secondary over current protection (circuit breaker) trips
    before things
    >     catch on fire. Usuaully the UL94V0 rating on the circuit
    board and the
    >     box the circuit board is in prevents fire from spreading
    when things do
    >     get wild.
    >
    >     But I've also seen all of those brands survive a load dump.
    >
    >     I have multiple customer who have fielded lithium battery
    systems to
    >     cold locations and have had battery BMS disconnect the
    battery from the
    >     rest of the system. Ten's of thousands of dollars of
    equipment has been
    >     destroyed in these islanding events.
    >
    >
    >     Some thoughts, for what they are worth.
    >
    >     -James Jarvis
    >     APRS World, LLC
    >
    >
    > _______________________________________________
    > List sponsored by Redwood Alliance
    >
    > Pay optional member dues here: http://re-wrenches.org
    >
    > List Address: RE-wrenches@lists.re-wrenches.org
    >
    > Change listserver email address & settings:
    > http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
    >
    > There are two list archives for searching. When one doesn't
    work, try the other:
    > https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
    > http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
    >
    > List rules & etiquette:
    > http://www.re-wrenches.org/etiquette.htm
    >
    > Check out or update participant bios:
    > http://www.members.re-wrenches.org
    >
    _______________________________________________
    List sponsored by Redwood Alliance

    Pay optional member dues here: http://re-wrenches.org

    List Address: RE-wrenches@lists.re-wrenches.org

    Change listserver email address & settings:
    http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

    There are two list archives for searching. When one doesn't work,
    try the other:
    https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
    http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

    List rules & etiquette:
    http://www.re-wrenches.org/etiquette.htm

    Check out or update participant bios:
    http://www.members.re-wrenches.org


_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here:http://re-wrenches.org

List Address:RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

--
            Christopher Warfel
                     ENTECH Engineering, Inc.
PO Box 871, Block Island, RI 02807
                                401-466-8978
<http://entech-engineering.com>

BEGIN:VCARD
VERSION:4.0
N:Warfel;Christopher;;;
TEL;VALUE=TEXT:401-447-5773 (c)
NOTE:Use the cell phone number for all communications.  Thank you.
URL:https://www.entech-engineering.com
END:VCARD
_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to