Hi, Mechanix~ Kirk Herander asked about cable trays & basing the wire calculations as if the wires are in "free air". The 2023 Article 100 definition of Free Air is unchanged from the 2020 NEC:
2023: "Open or ventilated environment that allows for heat dissipation and air flow around an installed conductor." However at the 2020 sessions for CMP6 Code Making Panel 6, the original draft language was: 2020 first draft: "Open or ventilated environment that allows for air flow around an installed conductor with no other conductors closer than one cable diameter and no insulation or building materials in contact with the conductor insulation for more than 75 mm (3 in.) for every 3 m (10 ft) of conductor." This is not the letter of the law since it was changed in the second draft but it does show the thinking process. I specified some cable tray recently which was "solid" on the sides & bottom (unlike some other types that are perforated or ladder style). This tray was for AC wires & the electricians did support the wires so there's ~ one cable diameter of air space around each insulated conductor. There's no forced air ventilation on this project; only natural convection via the open top of the trays. The wires were sized for "free air" conditions & there was no pushback from the AHJ. As with so many cases, this goes to the individual AHJ's interpretation, but the air-gaps seem more appropriate (compared to laying the wires in a heap) if one wants the installation to be interpreted as "free air", especially when the tray sides & bottom surface are solid as in this example. I hope this will be helpful; the Wrench List is the Bomb! Mick Abraham, Proprietor www.abrahamsolar.com Landline: 970-731-4675 Cell phone or for text messaging: 970-946-6584 ᐧ
_______________________________________________ List sponsored by Redwood Alliance Pay optional member dues here: http://re-wrenches.org List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org There are two list archives for searching. When one doesn't work, try the other: https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/ http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: http://www.re-wrenches.org/etiquette.htm Check out or update participant bios: http://www.members.re-wrenches.org