The thumper sounds like the one to use, but what does it destroy? Does
it induce a much higher voltage on the line than regular line voltage?
We are dealing with open circuit problems.
We can return to our original plan of digging up areas and checking for
voltage on the lines with a voltage sensor. Thanks, Drake _Drake Chamberlin_ _Athens Electric LLC_ _Ohio Electrical Contractor's License 44810_ _CO Master Electrician's License 4526_
_NABCEP Certified PV Installation Professional_

---

On 2023-04-18 12:04, Brian Mehalic via RE-wrenches wrote:

Not sure about rental sources in your area, but there are two options: 1) An underground cable fault locator, aka a "thumper," which only works on direct buried cables. It is a destructive test (at the fault location), and should only be performed when there is a known fault in order to locate it. It requires "walking" the cable run with a sensing device to hear the "thump" generated by the high current/high voltage induced on the line.
2) A time domain reflectometer (TDR), which is sort of like radar in that low energy signals 
are reflected by changes in cable impedance; it is non-destructive, but also not as accurate 
in terms of the location (providing a cable length to the fault, rather than a 
"thump" at the actual fault location) and typically cannot see higher resistance 
(≈>200 MΩ) faults that the thumper can.

Brian Mehalic NABCEP Certified Solar PV Installation Professional(tm) R031508-59 National Electrical Code(R) CMP-4 Member (520) 204-6639

Solar Energy International
http://www.solarenergy.org On Tue, Apr 18, 2023 at 8:27 AM Matt Sherald via RE-wrenches <re-wrenches@lists.re-wrenches.org> wrote: Hi Drake, I've rented a set-up from my electrical supply house. I'd check to see if Scott Electric/Advantage Rental serves your part of Ohio. If memory serves, it is two pieces of equipment that you need. One to trace the line and a second to find the fault. -Matt On Tue, Apr 18, 2023 at 11:20 AM Drake Chamberlin via RE-wrenches <re-wrenches@lists.re-wrenches.org> wrote: I understand that there is a tool that locates underground faults in buried cables. No one in our area has one. There are high tech cable tracers now, but they don't advertise that they can find underground breaks in wires.

One company online had one that advertised that function. The entire kit came to $5 or $6K.

Does anyone know where one can be rented.

Thank you,

Drake

Drake Chamberlin
Athens Electric LLC
Ohio Electrical Contractor's License 44810
CO Master Electrician's License 4526
NABCEP Certified PV Installation Professional

--
_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

--

Matt Sherald PIMBY Energy, LLC
304-704-5943 _______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try
the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org
_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to