William,
Sol-Ark says they can only connect to a Wye, and that they need a
neutral.
Thanks,
Drake
---
On 2023-06-06 11:34, William Miller via RE-wrenches wrote:
Drake:
You should be able to connect to a 120/240 split phase feeder. Avoid the stinger. I have done it with FXRs , works just fine.
Wm
On Tue, Jun 6, 2023 at 8:11 AM Drake Chamberlin via RE-wrenches <re-wrenches@lists.re-wrenches.org> wrote:
Hello All,
We are looking for a transformer to connect Sol-Ark inverters to an open
delta service. The Sol-Ark can only connect to a Wye configuration.
We found one which the supplier says will do the job. It is an MGM, 240
Delta to 208Y/120 Volt, 3-Phase.
The supplier says this will derive a neutral which can be grounded for a
solid neutral connection.
My concerns with what we have found so far are:
1) How much efficiency will be lost due to connecting to an open delta?
2) Will the derived neutral really be sufficient?
3) The cost of the unit we found is high. Does anyone know of a source
for economically priced transformers.
Thank you,
Drake
Drake Chamberlin
Athens Electric LLC
Ohio Electrical Contractor's License 44810
CO Master Electrician's License 4526
NABCEP Certified PV Installation Professional
--
_______________________________________________
List sponsored by Redwood Alliance
Pay optional member dues here: http://re-wrenches.org
List Address: RE-wrenches@lists.re-wrenches.org
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
http://www.members.re-wrenches.org
--
William Miller
Miller Solar.com
805-438-5600
www.millersolar.com [1]
_______________________________________________
List sponsored by Redwood Alliance
Pay optional member dues here: http://re-wrenches.org
List Address: RE-wrenches@lists.re-wrenches.org
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
http://www.members.re-wrenches.org
Links:
------
[1] http://www.millersolar.com
_______________________________________________
List sponsored by Redwood Alliance
Pay optional member dues here: http://re-wrenches.org
List Address: RE-wrenches@lists.re-wrenches.org
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
http://www.members.re-wrenches.org