Morning all

 

  You may also want to look at the Victron products. They have a 1000 amp 
version called the Lynx distributor. 

 

Peter Giroux

ASAE

 

From: RE-wrenches <re-wrenches-boun...@lists.re-wrenches.org> On Behalf Of 
Bradley Bassett via RE-wrenches
Sent: Thursday, June 29, 2023 10:47 AM
To: RE-wrenches <re-wrenches@lists.re-wrenches.org>
Cc: Bradley Bassett <bbasse...@gmail.com>
Subject: Re: [RE-wrenches] Parallel Homegrid Stack'd Busbar

 

Note that MidNite now also makes 2000A and 500A versions of their BCB. With two 
Sol-Ark 15k you do need to use the 1000A version with 275A each inverter. I can 
also confirm that you do need to use both of the battery terminals in the 
Sol-Ark 15k for full power, or the Homegrid bus bars that Jason shows. 

 

Brad Bassett

 

 

On Thu, Jun 29, 2023 at 6:57 AM Jason Szumlanski via RE-wrenches 
<re-wrenches@lists.re-wrenches.org <mailto:re-wrenches@lists.re-wrenches.org> > 
wrote:

Lloyd,

 

Homegrid makes a busbar to combine the two terminals in the Sol-Ark 15k so it 
can accept a single 4/0 cable and retain the full output capacity. Apparently, 
Homegrid is the only battery on the market with the output capacity to do this. 

 

https://www.homegridenergy.com/stackd-series 
<https://mailtrack.io/trace/link/a0cf1afc125652c2027c1cbd7d5458266a2d118b?url=https%3A%2F%2Fwww.homegridenergy.com%2Fstackd-series&userId=1613865&signature=28245d1e93ba151a>
 


Jason Szumlanski

Principal Solar Designer | Florida Solar Design Group
NABCEP Certified Solar Professional (PVIP)
Florida State Certified Solar Contractor CVC56956

 

 

On Thu, Jun 29, 2023 at 9:43 AM Lloyd Hoffstatter via RE-wrenches 
<re-wrenches@lists.re-wrenches.org <mailto:re-wrenches@lists.re-wrenches.org> > 
wrote:

Hi Maverick,

 

Per tech support, you need to buss battery output(s) to both input breakers to 
get the full 275 Amp output.

 

Best regards,

Lloyd 

 

Lloyd Hoffstatter, M.S. Applied Solar Energy

NABCEP Inaugural Certified PV Installer Emeritus

Director, Sunstruck Consulting

ll...@sunstruckconsulting.com <mailto:ll...@sunstruckconsulting.com> 

845-657-8132 (office)

914-844-3404 (mobile)

 

From: Mac Lewis via RE-wrenches <mailto:re-wrenches@lists.re-wrenches.org> 
Sent: Thursday, June 29, 2023 8:27 AM
To: RE-wrenches <mailto:re-wrenches@lists.re-wrenches.org> 
Cc: Mac Lewis <mailto:maclew...@gmail.com> 
Subject: Re: [RE-wrenches] Parallel Homegrid Stack'd Busbar

 

Hi Jason,

 

The Sol-Ark 15k has dual battery input terminals so they can be combined right 
inside.  This could be a good option to consider.

 

Thanks

 

 

On Thu, Jun 29, 2023 at 6:17 AM Maverick Brown via RE-wrenches 
<re-wrenches@lists.re-wrenches.org <mailto:re-wrenches@lists.re-wrenches.org> > 
wrote:

I recommend the Victron Lynx Power In or the Lynx Distributor. 

Thank you,

 

Maverick

 

 

On Jun 29, 2023, at 6:55 AM, Jason Szumlanski via RE-wrenches 
<re-wrenches@lists.re-wrenches.org <mailto:re-wrenches@lists.re-wrenches.org> > 
wrote:



Hi all,

 

I'm doing my first installation with two 24 kWh Homegrid stacks. They will feed 
two Sol-Ark 15k. I'm seeking recommendations on busbars for connecting this up 
in the most elegant way possible.

 

Pictures speak 1,000 words, so if you have any I would appreciate it (off-list 
is fine).

 

Jason Szumlanski

Florida Solar Design Group

 

 

_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org 
<mailto:RE-wrenches@lists.re-wrenches.org> 

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to