The intent of the line side tap, was to allow larger pv systems to interconnect to the SE conductors and not have to consider the service panel. So, I agree with others that the service panel has no consideration for what you are doing. The panel is protected by the MSP Breaker.  Chris

On 10/12/2023 8:06 PM, Drake Chamberlin via RE-wrenches wrote:
We have a design where the conductors will come out of a 400 A meter base to a junction box. Splices in the box will allow for the PV to feed the meter.
A maximum of 312 Amps can come from the inverters to feed the grid.

The loads on the existing main service are significantly less than 200A. The service is rated at 200 A, 3 phase delta.



The conductors from the meter would be rated at 400 A to the splice, as would the conductors to the photovoltaic system. The conductors to the existing service would be downsized to 200 A.

We were told that the bus bar rating of the service must also be 400 A, even though the output of the PV does not feed through that box. Is there a rule that says this? What would be the logic?
Thank you,
Drake

/Drake Chamberlin/

/Athens Electric LLC/

/Ohio Electrical Contractor’s License 44810/

/NABCEP Certified PV Installation Professional/


_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here:http://re-wrenches.org

List Address:RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

--
            Christopher Warfel
                     ENTECH Engineering, Inc.
PO Box 871, Block Island, RI 02807
                                401-466-8978
<http://entech-engineering.com>

BEGIN:VCARD
VERSION:4.0
N:Warfel;Christopher;;;
TEL;VALUE=TEXT:401-447-5773 (c)
NOTE:Use the cell phone number for all communications.  Thank you.
URL:https://www.entech-engineering.com
END:VCARD
_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to