Dan,

Since you are using 120Vac for the source, did you connect to just 1 AC input; 
AC1 or AC2?  You can not parallel same phase to both inputs or damage may 
occur. 

Have you measured the generator frequency and voltage at the inverter input? 
Make sure to reduce the charge rate to 50% or less when supplying 120V only. 

Larry Crutcher
Starlight Power Systems



On Oct 31, 2023, at 10:56 AM, Dan Fink via RE-wrenches 
<re-wrenches@lists.re-wrenches.org> wrote:

I have had issues before with Magnum inverter/chargers not accepting AC input 
from certain generators. In one case, it would not charge from a Honda 3kw 
cube, but worked fine with camp’s Honda 2kw. Magnum said it was a Honda 
problem, Honda said it was a Magnum problem. We ended up just rearranging 
generators and inverters between camps. Weird, we never detected anything odd 
in voltage or frequency from any of the generators.

Dan Fink
Owner, Buckville Energy Consulting LLC
IREC Certified Instructor for PV and Small Wind Installation
NABCEP Certified PV System Inspector
NABCEP PV Associate
danbo...@gmail.com <mailto:danbo...@gmail.com>
970-672-4342

 


On Tue, Oct 31, 2023 at 11:39 AM Ron Young via RE-wrenches 
<re-wrenches@lists.re-wrenches.org <mailto:re-wrenches@lists.re-wrenches.org>> 
wrote:
Hello Wrenches,

I am completely stumped. I built a Magnum 4448 panel for a client and it was 
installed by an electrician. It was thoroughly tested before going out the door 
on all functions and pre-programmed for the off-grid site. Electrician just had 
to hang it on the wall and make 4 connections, AC IN, AC OUT, BATTERY, PV. 
Somehow the system wouldn’t go into charge mode. The site is a 3 hour trip each 
way. The electrician was baffled, he had experience installing solar but very 
limited so I went to the site to see what the problem was. After spending a day 
checking out the inverter with two different generators, checking all the 
connections, AC at the inputs at the inverter and at the outputs on the 
breakers, and even removed the cover from the inverter to make sure some 
connections had not shaken loose inside the box on the long bumpy road into the 
property. Everything checked out. So assuming the AC board in the inverter was 
faulty I ordered a new unit to replace and that has now been done. SAME 
PROBLEM! I’m wondering now if it’s possible that the Magnum remote monitor 
could be the problem. It functions properly on every setting but is it possible 
there is an internal fault? Could it prevent the automatic charge cycle from 
initiating? Seems unlikely to me because the inverter can go into charge mode 
even without the monitor. I also tried replacing the connection cable between 
the monitor and inverter but no luck. 

The generators are both small, one a Honda 2kW and the other a Champion 3.8kW. 
Neither is ideal but I have had no issues with these types of generators in the 
past and the client has ordered a larger 10kW unit but we don’t have it yet to 
test. Generators have been run with Eco Mode off. Output to the house on bypass 
is consistent and without problem.

Any suggestions - this is just confounding.

Ron


earthRight Products - Solareagle.com <http://solareagle.com/>

_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org <http://re-wrenches.org/>

List Address: RE-wrenches@lists.re-wrenches.org 
<mailto:RE-wrenches@lists.re-wrenches.org>

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org 
<http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/ 
<https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/>
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org 
<http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org>

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm 
<http://www.re-wrenches.org/etiquette.htm>

Check out or update participant bios:
http://www.members.re-wrenches.org <http://www.members.re-wrenches.org/>

_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org


_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to