So to be clear, the inspector is wrong:  it is NOT an NEC requirement.  It is only a California requirement.   NEC 2023 only requires a 100 A main load center and disconnect per 225.39(C). Further, 710.15(A) allows the inverter and feeder to the Load center to be even less in off grid applications.   The rest of us in the other 49 states are Not required to comply with the 200 A requirement.

Good Luck out there.


Thank you,


Ray Walters
Remote Solar



On 3/28/2024 12:33 PM, Lloyd Hoffstatter via RE-wrenches wrote:
William,

Here is the CA Energy Code with the upsized busbar requirements under solar / ess readiness:

https://title24energyreports.com/articles/basic-facts-changes-2022-energy-code.php

Best regard
Title 24: 2022 Energy Code - Basic Facts | CompuCalc <https://title24energyreports.com/articles/basic-facts-changes-2022-energy-code.php>
Summary of changes and updates in the 2022 California Energy Code
title24energyreports.com



Lloyd Hoffstatter, M.S. Applied Solar Energy

Inaugural NABCEP Cetrified PV Installer Emeritus

Director, Sunstruck Consulting

ll...@sunstruckconsulting.com

845-657-8132 (office)

914-844-3404 (cell)

------------------------------------------------------------------------
*From:* RE-wrenches <re-wrenches-boun...@lists.re-wrenches.org> on behalf of William Miller via RE-wrenches <re-wrenches@lists.re-wrenches.org>
*Sent:* Thursday, March 28, 2024 1:00 PM
*To:* RE-wrenches <re-wrenches@lists.re-wrenches.org>
*Cc:* William Miller <will...@millersolar.com>
*Subject:* [RE-wrenches] Minimum bus size, new requirements

Friends:

A local building official recently wrote this:

This is to comply with the new codes (California Energy Code and the Nation Electric Code) that require this minimum buss rating regardless of the service size or main size.

The new code allegedly requires a minimum bus rating of 225A in all new services of 200A rating or less.

Do any of you know what new code this might be?

Thanks in advance for your time.

William

Miller Solar

17395 Oak Road, Atascadero, CA 93422

805-438-5600

www.millersolar.com <https://urldefense.proofpoint.com/v2/url?u=http-3A__www.millersolar.com_&d=DwMFaQ&c=euGZstcaTDllvimEN8b7jXrwqOf-v5A_CdpgnVfiiMM&r=p2tHyHEAjVe2zSh4C_236V4KkHnn0z0ynUvWz0mobds&m=9uejohzp8xlaOjgzFRzK5pSkQX5Jtrq-KM0zg-kn9sGvQF-Ezmo9hA2K0hbNA1ns&s=7RIp61FIGVkUrnLeJuaaLlwwPwqGeMEQXVgB04GNECk&e=>

CA Lic. 773985


_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here:http://re-wrenches.org

List Address:RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org
_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to