That's correct you only need one load controller to commission a sunlight
only backup system.

Strangely enough, I am sitting in the driveway of a sunlight only backup
system owner right now. I found a melted 60A solar breaker in the System
Controller (not my installation, contractor is on the run). The homeowner
said they have been hearing sizzling noises for 6 months! The solar breaker
wasn't tripping, but the 100A load breaker was, and was too hot to touch
when it did. I scolded them for not calling a licensed electrician earlier.
Yikes!

Anyway, they are another example of a dissatisfied owner. They said the
backup performance is way too intermittent. The only thing they are
powering is a refrigerator, some lights, and the 110 volt circuit for a gas
water heater. They have 29 x 400W panels. Yet, they are still dissatisfied.
I told them that a single 5P battery would transform their experience and
likely power all of those loads throughout the night.

As much as I loathe discontinuation of the IQ7, the IQ8 having no ratio to
battery power restrictions is great.

Jason

On Thu, Sep 26, 2024, 9:16 AM Dave Tedeyan <d...@sungineersolar.com> wrote:

> Hi Jason,
>
> Thanks for your detailed response here. What tech support told me was what
> I wanted to hear, although I just did not totally trust them.
>
> As for the powerline filter, I planned on that from the beginning, based
> on their planning guide. Having it in there cannot hurt, right?
>
> For the Sunlight Backup, I have found that having a detailed conversation
> about what it can and cannot do is quite helpful. If you keep the bar
> really low, its not difficult to step over it. I find some people here like
> it as an intermediate if they aren't quite ready for batteries for some
> reason or another. Also, note that you only need one load controller now.
> And I use that more to provide on/off load control rather than a turn on
> sequence. Theoretically, you could just have the sunlight backup provide
> power to an entire MSP (although that would not be a good idea).
>
> I'll be heading out to the site in the near future to try again to get the
> crosstalk issues sorted. I'll let you know if your sequence here works.
> I've talked to three of their storage techs about it so far, and none have
> suggested this. You would think they would have some more standardization
> around these sorts of issues.
>
> Cheers,
> Dave
>
> On Wed, Sep 25, 2024 at 5:15 PM Jason Szumlanski <
> ja...@floridasolardesigngroup.com> wrote:
>
>> With IQ8 series microinverters, there is an absolute limit of 64A
>> connected to the IQ Combiner input lugs of the System Controller. The DER
>> port is not for PV. It is for batteries that exceed the limits of the
>> storage port. You can have up to (8) 5P on the Storage lugs and (8) on the
>> DER lugs. But these will be power limited to the output of (4) 5P batteries
>> per input. In other words, this is a way to connect 80kWh of capacity to
>> the system, but you will only have 128A of power output even though the
>> (16) batteries are capable of 256A. Anyway, 64A is the PV limit for backup
>> systems, and there is no way around it with IQ8.
>>
>> You CANNOT connect any additional IQ8 microinverters on the load side of
>> the System Controller when there is backup involved. All IQ8 must be
>> connected to the IQ Combiner lugs on the System Controller. The relay in
>> the system controller must be able to turn off the IQ8 micros. This relay
>> also disconnects the rooftop micros when the RSD switch is turned off.
>>
>> The additional microinverters can be connected to the line side of the
>> System Controller (as a feeder tap or anywhere upstream of the System
>> Controller that complies with code). You do need a separate IQ Gateway,
>> because these microinverters need to be configured for grid-tie only. All
>> microinverters connected to the same Gateway must have the same mode. The
>> micros connected to the backup system will be set up as multi-mode.
>>
>> Don't bother with a line filter unless it becomes truly necessary. There
>> are things that Enphase can do on its end to reduce the crosstalk by
>> establishing separate domains. They SAY you need a line filter, but this is
>> rarely the case. Don't listen to anything that Tier 1 customer service
>> tells you regarding powerline communications. That's their go-to response
>> when they can't figure something out.
>>
>> As for the Sunlight Backup system, I don't have a single client that is
>> satisfied with this setup. It really needs at least one IQ Battery 5P to be
>> functional, in which case you can forget about the ridiculous limitations
>> of 8 x 120V or 4 x 240V circuits and the rigmarole of two load controllers
>> that Sunlight Backup requires, especially with that much PV. I would avoid
>> Sunlight Backup at all costs. It's not useful for anything but the smallest
>> loads during the best conditions
>>
>> As for your crosstalk issues, here is what I would do. Have customer
>> service retire one of the IQ Gateways and all associated microinverters.
>> Provision the other IQ Gateway and get those microinverters working. Then
>> turn OFF power to the working Gateway and microinverters. Turn ON power to
>> the other Gateway and microinverters and have customer service unretire
>> everything. Reprovision using ITK. Once everything is working on the second
>> Gateway, turn the first one back on and all microinverters, and you will
>> probably be up and running without further issues.
>>
>>
>> I was really disappointed with the discontinuation of the IQ7 because of
>> this 64A hard limit of PV on a backup system. With IQ7 you could have 96A
>> of PV with the previous generation battery. The IQ8 was a step backward for
>> large backup systems. I provided this feedback to Enphase, and they were
>> working on a possible workaround to make something work, but I would not
>> hold your breath. I even wrote this article when the issue first came to
>> light:
>>
>> https://floridasolardesigngroup.com/enphase-iq7-versus-iq8-microinverters/
>>
>>
>> Jason Szumlanski
>> Principal Solar Designer | Florida Solar Design Group
>> NABCEP Certified Solar Professional (PVIP)
>> Florida State Certified Solar Contractor CVC56956
>> Florida Certified Electrical Contractor EC13013208
>>
>>
>> On Wed, Sep 25, 2024 at 3:02 PM Dave Tedeyan via RE-wrenches <
>> re-wrenches@lists.re-wrenches.org> wrote:
>>
>>> Hi all,
>>>
>>> All this talk about Enphase recently and I have a design question that I
>>> am having trouble getting a straightforward answer to. The IQ system
>>> controller can take up to 64A of PV AC output on the DER port (coming from
>>> the IQ combiner for example). When there is more solar on site, the
>>> question is what do you need to do with the rest of the solar.
>>>
>>> They have a system planning guide that talks about some of this and you
>>> can find it here:
>>> https://enphase.com/download/planning-enphase-energy-system-tech-brief
>>>
>>> Page 59 bullet point 6 says that with IQ8 micros, the excess PV must be
>>> split into a grid-tied system. I recently did this, got a separate IQ
>>> gateway, and a power line filter, and the system continues to have cross
>>> talk issues between the two gateways, and the microinverters will just not
>>> report properly no matter how many times tech support re-provisions the
>>> devices and prevents each gateway from looking for more devices.
>>>
>>> Then I noticed that with M series micros (page 62 bullet point 9) it
>>> says that microinverters exceeding 64A can be added to the main panel. In
>>> this scenario, there will be more than 64A of solar flowing through the IQ
>>> system controller, even though the DER port is limited to 64A. I would like
>>> to do something similar to this for my system with crosstalk issues and get
>>> rid of the second IQ Gateway.
>>>
>>> I asked tech support why there was a difference in the planning document
>>> for IQ8 and for M series and whether I could add the extra IQ8 into the
>>> backed up subpanel (This is a Sunlight backup system). They did not give me
>>> a fully complete answer, but they did say this, "You can add the panels up
>>> to 64A into the system controller and exceeding PV can be connected to the
>>> backup subpanel."
>>>
>>> I fear that this was a level 1 tech and that they may not have
>>> completely understood the situation. This is the answer that I wanted, but
>>> I am not sure I trust it yet. Has anyone here tried something similar to
>>> this?
>>>
>>> Thanks!
>>> -Dave
>>>
>>> --
>>>
>>> [image: Logo] <https://www.sungineersolar.com/>
>>> Dave Tedeyan, P.E.
>>> Owner | Sungineer Solar
>>> p: he | him | his
>>> a: 1653 Slaterville Rd.
>>> <https://www.google.com/maps/search/1653+Slaterville+Rd.+%C2%A0+%7C%C2%A0Ithaca,+NY+14850?entry=gmail&source=g>
>>>
>>> <https://www.google.com/maps/search/1653+Slaterville+Rd.+%C2%A0+%7C%C2%A0Ithaca,+NY+14850?entry=gmail&source=g>|
>>>  Ithaca,
>>> NY 14850
>>> <https://www.google.com/maps/search/1653+Slaterville+Rd.+%C2%A0+%7C%C2%A0Ithaca,+NY+14850?entry=gmail&source=g>
>>> w: www.sungineersolar.com <http://www.sungineersolar.com/>
>>> c: (607) 270-0370
>>> _______________________________________________
>>> List sponsored by Redwood Alliance
>>>
>>> Pay optional member dues here: http://re-wrenches.org
>>>
>>> List Address: RE-wrenches@lists.re-wrenches.org
>>>
>>> Change listserver email address & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>
>>> There are two list archives for searching. When one doesn't work, try
>>> the other:
>>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>
>>> List rules & etiquette:
>>> http://www.re-wrenches.org/etiquette.htm
>>>
>>> Check out or update participant bios:
>>> http://www.members.re-wrenches.org
>>>
>>>
_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other: