Hi Jeremy,

I am under the impression that leaving at least 10% of capacity will extend 
total cycle life. 
The chart states 50.4 volts is a 10% SOC. 
 Then there is the LBCO delay time that may allow battery shutdown before the 
inverter does.

Of course the  OB FX LBCO upper limit is at 48 volts thus the recent search and 
discussion for a seamless external inverter shutdown to get users attention if 
an AGS is not in the mix.

Wallace Stahle
Future Electric Energy Co
PO Box 236
Willits, CA 95490
707-459-0474
Lic.#C10-762093
[email protected]

> On Feb 3, 2025, at 7:11 PM, Jeremy Rodriguez via RE-wrenches 
> <[email protected]> wrote:
> 
> Today I installed 3 of the MN 
> POWERFLO 5 batteries with an OBVFX3648 
> Per the battery label I was able to set the inverter LBCO to 46 vdc. 
> I see that the battery BMS range 
> Is 44.8-58 vdc 
> We should be good to go. 
> 
> 
> Jeremy Rodriguez 
> Solar Installation / Design
> All Solar, Inc.
> 1453 M St. 
> Penrose Colorado 81240
> 
> Sent by Jeremy's iPhone. Sorry for typos and shorthand. 
> 
>> On Feb 3, 2025, at 1:47 PM, Nick Lucchese via RE-wrenches 
>> <[email protected]> wrote:
>> 
>> 
>> Here is the voltage vs SOC approximation chart from Midnite. Was helpful for 
>> me on my first couple installs as I awaited some additional details about 
>> their batteries.
>> 
>> Nick
>> 
>> On Mon, Feb 3, 2025 at 6:50 AM William Bryce via RE-wrenches 
>> <[email protected] 
>> <mailto:[email protected]>> wrote:
>> Hi Jay
>> 
>> The settings for the MNS Batteries are on a sticker on each battery.
>> 
>> BMS- LVCO 44.8 HVCO 58V (The HVCO is not on the sticker) 
>> LVCO (inverter) 46.0
>> Float 54V
>> Bulk 56.1V
>> 
>> The rest of the  you can set to what you want, the battery does not care.
>> All Prismatic cells operate mostly the same, and the MNS Batteries use A+ 
>> Automotive cells MFG by EVE.
>> 
>> Thanks
>> 
>> Logan
>> 
>> 
>> On Mon, Feb 3, 2025 at 8:47 AM Jay via RE-wrenches 
>> <[email protected] 
>> <mailto:[email protected]>> wrote:
>> Hi Bill
>> 
>> I tried and failed to find any setting information on that battery besides 
>> charge and float. 
>> Kinda need to know things like LVD, recommended LBCO, etc. 
>> But if it’s similar to other prismatic cells you should be able to set the 
>> OB inverter to a LBCO that works without having to go through a aux relay. 
>> 
>> Jay
>> 
>> > On Feb 2, 2025, at 9:53 PM, Bill Battagin via RE-wrenches 
>> > <[email protected] 
>> > <mailto:[email protected]>> wrote:
>> > 
>> > Have any off-gridders done a system with Powerflo16's to power pre-LFP 
>> > OB/FX inverters?  The FM80's LFP settings in this system are compatible 
>> > with LFP but I'm looking for options other than using the Aux in the CC's 
>> > wired to a NC relay and from there to the inverter on/off landings in the 
>> > green terminal of the OB/FX for the LBCO and reconnect function.
>> > 
>> >             I've been down this road before, though a different equipment. 
>> >  I've used the Aux from a Classic for inverter LBCO and reconnect though 
>> > its never been fully "tested", although I read "open" and closed" at the 
>> > un-wired aux landing when I forced it with a high LBCO setting.  Just 
>> > thinking about the highest reliability.
>> > 
>> >         Thanks in advance.
>> > 
>> > Bill
>> > 
>> > Feather River Solar Electric
>> > Bill Battagin, owner
>> > 4291 Nelson St. (Shipping)
>> > 5575 Genesee Rd. (USPS, UPS)
>> > Taylorsville, CA  95983
>> > 530-284-7849, 258-1641(cell)
>> > CA. C10 Lic # 874049
>> > Solar Powered since 1982
>> > Home of the Sunny Side Up
>> > 
>> > 
>> > --
>> > This email has been checked for viruses by Avast antivirus software.
>> > www.avast.com <http://www.avast.com/>
>> > _______________________________________________
>> > List sponsored by Redwood Alliance
>> > 
>> > Pay optional member dues here: http://re-wrenches.org 
>> > <http://re-wrenches.org/>
>> > 
>> > List Address: [email protected] 
>> > <mailto:[email protected]>
>> > 
>> > Change listserver email address & settings:
>> > http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org 
>> > <http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>
>> > 
>> > There are two list archives for searching. When one doesn't work, try the 
>> > other:
>> > https://www.mail-archive.com/[email protected]/ 
>> > <https://www.mail-archive.com/[email protected]/>
>> > http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org 
>> > <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org>
>> > 
>> > List rules & etiquette:
>> > http://www.re-wrenches.org/etiquette.htm 
>> > <http://www.re-wrenches.org/etiquette.htm>
>> > 
>> > Check out or update participant bios:
>> > http://www.members.re-wrenches.org <http://www.members.re-wrenches.org/>
>> > 
>> _______________________________________________
>> List sponsored by Redwood Alliance
>> 
>> Pay optional member dues here: http://re-wrenches.org 
>> <http://re-wrenches.org/>
>> 
>> List Address: [email protected] 
>> <mailto:[email protected]>
>> 
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org 
>> <http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>
>> 
>> There are two list archives for searching. When one doesn't work, try the 
>> other:
>> https://www.mail-archive.com/[email protected]/ 
>> <https://www.mail-archive.com/[email protected]/>
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org 
>> <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org>
>> 
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm 
>> <http://www.re-wrenches.org/etiquette.htm>
>> 
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org <http://www.members.re-wrenches.org/>
>> 
>> _______________________________________________
>> List sponsored by Redwood Alliance
>> 
>> Pay optional member dues here: http://re-wrenches.org 
>> <http://re-wrenches.org/>
>> 
>> List Address: [email protected] 
>> <mailto:[email protected]>
>> 
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org 
>> <http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>
>> 
>> There are two list archives for searching. When one doesn't work, try the 
>> other:
>> https://www.mail-archive.com/[email protected]/ 
>> <https://www.mail-archive.com/[email protected]/>
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org 
>> <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org>
>> 
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm 
>> <http://www.re-wrenches.org/etiquette.htm>
>> 
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org <http://www.members.re-wrenches.org/>
>> 
>> <Powerflo16 Battery SOCvsVoltage.jpg>
>> _______________________________________________
>> List sponsored by Redwood Alliance
>> 
>> Pay optional member dues here: http://re-wrenches.org
>> 
>> List Address: [email protected]
>> 
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>> 
>> There are two list archives for searching. When one doesn't work, try the 
>> other:
>> https://www.mail-archive.com/[email protected]/
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>> 
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm
>> 
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org
>> 
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> Pay optional member dues here: http://re-wrenches.org
> 
> List Address: [email protected]
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> There are two list archives for searching. When one doesn't work, try the 
> other:
> https://www.mail-archive.com/[email protected]/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> http://www.members.re-wrenches.org
> 

_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to