Is there a NEC reference for that you know of?, as I see Romex brought down to switches very often, and I've not found a reference prohibiting that.  As far as a ground mounted solar system being climbed on, anything is possible, but hopefully trees are of more interest.  Thank you, Chris

On 2/18/2025 11:38 AM, Tyrone Houck wrote:

My understanding of code is that all circuits need to be protected from physical damage. It's the same with AC circuits in an unfinished garage..can't have exposed romex under 8' in that scenario either.



On Tue, Feb 18, 2025, 8:34 AM Christopher Warfel via RE-wrenches <[email protected]> wrote:

    Well, I think if wiring of a ground mounted system looks like a
    jungle gym, then something is wrong.

    On 2/18/2025 11:32 AM, Glenn wrote:
    Rarely are AC electrical circuits and equipment placed adjacent
    to a residence in a cleared field where there may be children
    thinking it looks like a jungle gym either...

    -Glenn

    On Feb 18, 2025 11:23, Christopher Warfel via RE-wrenches
    <[email protected]>
    <mailto:[email protected]> wrote:

        I think the 8' rule for this is a little bizarre. I can have
        ac circuits lower than 8' all through my basement, attic and
        so forth, but this barrier requirement for dc conductors that
        have robust jackets and no exposed live connections has been
        hard to justify. Christopher Warfel

        On 2/18/2025 12:25 AM, William Miller via RE-wrenches wrote:

            Tyrone:

            You raise an excellent point. Wire guarding is required
            on ground mount arrays
            
<https://millersolar.com/MillerSolar/case_studies/18%20Wire_shielding_on_ground_mounted_PV_arrays/Wire_shielding_on_ground_mounts.html>,
            although the language is vague and the industry does not
            provide many hardware solutions.  Also, in our area the
            enforcement
            
<https://millersolar.com/MillerSolar/case_studies/18%20Wire_shielding_on_ground_mounted_PV_arrays/SLO_County.html>
            of the code on this practice is non-existent.  I suspect
            this is true in many regions.  Improvements need to be made.

            William Miller

            Miller Solar

            17395 Oak Road, Atascadero, CA 93422

            805-438-5600

            www.millersolar.com <http://www.millersolar.com/>

            CA Lic. 773985

            *From:*Tyrone Houck [mailto:[email protected]]
            *Sent:* Monday, February 17, 2025 8:59 PM
            *To:* [email protected]; RE-wrenches
            *Subject:* Re: [RE-wrenches] RSS: Is it necessary?

            As far as ground mounted arrays are concerned there is
            one clear protection mandated by the NEC-the requirement
            for protection from physical damage for all conductors
            under 8'.. although this isn't as specific or redundant
            as rapid shutdown requirements, it typically means
            conduit or at least some kind of physical barrier with
            the intention often referenced as protection for children
            or other unqualified personnel. Not sure if that fits
            into the point you were making but it seems worth mentioning.

            Sunny Regards,

            Tyrone Houck

            Oregon Solarworks LLC

            CCB #204937 LRT #076

            541-787-1366

            [email protected]


            On Mon, Feb 17, 2025, 8:42 PM William Miller via
            RE-wrenches <[email protected]> wrote:

                Rebekah:

                Thank you for your post.

                I have looked at UL3741 over and over.  Here is what
                I have gleaned:  After module level RSS was mandated
                there was a reevaluation of what voltages were
                actually dangerous for firefighters to be exposed
                to.  It turns out 80 VDC is not dangerous and, given
                all of the circumstances for firefighters, exposure
                to voltages that are much higher is safe enough.  For
                some reason I have not yet grasped, all of the
                components need to be matched and tested to achieve
                the hallowed UL3741 rating.

                Module level RSS would have presented a big enough
                upheaval in the industry if the equipment needed to
                comply was safe and reliable.  There is evidence that
                in many cases it may not be, and that amplifies the
                skepticism many feel about the current solutions, and
                frankly, any future solutions.

                It appears the code making panel, when writing the
                original module level RSS requirements, may have been
                a bit “chicken little” about the need for RSS.  This
                presents a real credibility issue for code makers. 
                You are seeing that credibility problem reflected in
                the discussions here on this forum.  Given the
                back-peddling, how can we understand and believe what
                is really necessary?

                Forgive me for being skeptical, but why is it that
                systems with components that have been tested
                together are demonstrably safer than any collection
                of high quality components installed carefully and
                competently?

                In my mind there is another disconnect here (pun
                intended):  I can put high voltage, arc producing and
                sustaining wiring on a residential roof or
                free-standing rack and not be required to protect
                that wiring in any specific manner.  If I were to
                install a 240VAC, over-current protected and
                de-energizeable air conditioning feeder without
                conduit, I would be red-tagged in a hot second.  It
                may be that fire-fighters in protective clothing can
                withstand voltage above 80VDC, but can children not
                wearing protective “turn-out” clothing?  Children
                mess around on roofs and underneath ground-mount
                arrays.  Why is the NEC not protecting them by
                mandating specific, listed and tested wire management
                and guarding systems?

                Thank you very much and I look forward to your reply.

                Sincerely,

                William Miller

                Miller Solar

                17395 Oak Road, Atascadero, CA 93422

                805-438-5600

                www.millersolar.com <http://www.millersolar.com/>

                CA Lic. 773985

                *From:*RE-wrenches
                [mailto:[email protected]]
                *On Behalf Of *Rebekah Hren via RE-wrenches
                *Sent:* Monday, February 17, 2025 10:26 AM
                *To:* RE-wrenches
                *Cc:* Rebekah Hren
                *Subject:* Re: [RE-wrenches] RSS: Is it necessary?

                I read the wrenches post regularly, as does Brian
                Mehalic. We have both been on CMP-4  (responsible for
                Article 690) for the past three code cycles. I
                believe a few other CMP members probably read too.
                The International Association of Firefighters
                ("largest and most influential labor unions in North
                America") is represented on CMP-4 and yes they do
                have had a lot to say about this issue.

                This is definitely not the first time we have heard
                that certain RS devices are on balance causing more
                trouble than they are curing  - though on the other
                hand some manufacturers have certainly figured out
                how to make safe and effective MLPE.


                I'm a big fan of UL3741, I have been on that UL
                technical committee for about 5 years, and it is the
                best approach I see to expand both off-grid and
                grid-interactive solutions that don't require MLPE
                for RS. SMA for example is very present and working
                hard at revisions on that standard right now. At this
                point I can't see us having any luck in removing
                690.12 requirements, except perhaps to replace the
                inside the array boundary voltage limit with only
                option as 3741 listing). So please keep asking
                manufacturers (inverter/rack) to pay attention to
                UL3741 and design products to meet the standard.

                Best

                Rebekah

                Licensed Electrical Contractor
                NABCEP Certified Solar PV Installation Professional™
                091209-85

                Tel: 336.266.8800

                On Mon, Feb 17, 2025 at 10:59 AM Amos Post via
                RE-wrenches <[email protected]> wrote:

                    Seems like there has been talk of rescinding RSD
                    requirements before on this forum.  It also seems
                    that it might gain some traction if a dedicated
                    group of installers spoke up to the right people
                    (Code Making Panel for instance) and put some
                    time into it.   I agree that at the very least we
                    need reliable RSD equipment, and my preference
                    would be less vs more.

                    Does anybody know if any sort of RSD is being
                    required in Europe (not that we follow their
                    electrical codes/ideas…just curious)???



                           Amos Post
                       Integrity Energy
                      W 802.763.7023
                       C 802.291.2188
                    ienergyVT.com <http://www.ienergyvt.com>

                    Facebook
                    <https://www.facebook.com/integrityenergyllp?ref=hl>

                    On Feb 17, 2025, at 12:30 PM, david quattro via
                    RE-wrenches <[email protected]>
                    wrote:

                    It seems anecdotal until it happens to you.

                        My mention of civil disobedience has been
                    answered clearly with a “No” in this forum, and
                    I'm fine to hear that.

                       I'll clarify a few points as to why I honestly
                    think RSD has been a huge and costly mistake. I
                    genuinely think RSD requirements should be
                    terminated immediately. If the technology were
                    more robust and if it worked consistently I
                    wouldn't protest. But *all* the products I've
                    tried have been trouble.

                       William, respectfully your analogy to seat
                    belts is not an appropriate comparison to Rapid
                    Shutdown. Seat-belts were required in all new
                    cars starting in 1968 because there was
                    statistical evidence supporting their tremendous
                    efficacy in saving human life. Currently seat
                    belts save about 15,000 lives per year.

                        Contrasting to RSD: was implemented because
                    of the following paranoid fairytale scenario - “A
                    firefighter is on a burning solar roof in the
                    daytime, and wearing a metal axe at their hip.
                    the poor guy/gal falls into live solar glass, and
                    shatters it. The fall is so forceful that the
                    heavy-duty fireman’s suit is punctured.
                    Electricity conducts through the axe blade,
                    through the suit, contacts the skin, and a DC
                    circuit is completed through their body.”

                       As far as I know, this has never happened once
                    anywhere on earth. Let’s be honest - this
                    scenario has an incredibly low chance of ever
                    happening in all the future of humanity. So
                    considering that RSD has never helped anyone yet,
                    and probably never will... How many fires can be
                    attributed to RSD? How much property damage has
                    occurred because of these fires?

                    The best path to safety for firefighters is by
                    preventing fire disasters in the first place.
                    Fires spread. Any fire that happens
                    endangers property owners, tenants, business
                    owners, neighbors, shoppers, bystanders, nearby
                    forests, etc.  RSD manufacturers aren't doing a
                    good job right now, so we are seeing low quality
                    unreliable electronics on the roof. I will stick
                    my neck out and admit that installers are not
                    always perfect. Humans make mistakes - sometimes
                    in initial construction, and sometimes during
                    repair and maintenance (i.e. when hunting down
                    failed RSD's which happens far more than it should).

                       At this time, these devices are not being
                    designed to withstand reality. When problems
                    happen, manufacturers are quibbling. They ignore
                    you until you go away, or until you sue them.

                      This level of "safety" is not important, and in
                    fact RSD is causing fires every year.

                    On Sat, Feb 15, 2025 at 11:38 AM William Miller
                    <[email protected]> wrote:

                        David, Ray:

                        I have not had any problems with the Tigo RSS
                        equipment I have installed and I have had
                        minimal problems with optimizers and
                        micro-inverters (which are also RSS
                        equipment).  Apparently others have had
                        failures. We don’t know statically how
                        serious this problem is—the posts here are
                        purely anecdotal.

                        We also have not heard from the other side of
                        the debate: the fire fighters.

                        Based on lack of verifiable information I can
                        not personally conclude that RSS is all
                        problem and no benefit.

                        To declare that the concept is flawed because
                        the equipment available is not reliable is
                        like saying we should not be required to
                        install airbags because a bad batch of them
                        was manufactured. We are seeing problems with
                        the equipment needed to implement a safety
                        requirement. That observation does not
                        logically conclude the safety requirement is
                        not valuable.

                        I hesitate to dismiss any safety requirement
                        out of hand. Safety systems are designed to
                        save lives and protect from injury, and most
                        of them do.  I am glad to have anti-lock
                        brakes, smoke detectors and air bags.   I
                        have also found it quite handy to initiate
                        RSS to allow me to work more safely on solar
                        circuits.

                        Does anyone on this installers forum have
                        contacts in the fire-response community that
                        can comment on the their side of the issue?
                        If RSD is really necessary for safety, then I
                        will do my best to install good equipment
                        properly and hold manufacturers accountable
                        for shoddy solutions.  If RSD is not that
                        effective we need to discuss undoing the code
                        requirements.

                        Sincerely,

                        William Miller

                        Miller Solar

                        17395 Oak Road, Atascadero, CA 93422

                        805-438-5600

                        www.millersolar.com <http://www.millersolar.com/>

                        CA Lic. 773985

                        *From:*RE-wrenches
                        [mailto:[email protected]]
                        *On Behalf Of *david quattro via RE-wrenches
                        *Sent:* Saturday, February 15, 2025 6:05 AM
                        *To:* RE-wrenches
                        *Cc:* david quattro
                        *Subject:* Re: [RE-wrenches] Tigo inverter
                        experience

                        RSD is the worst thing to happen to solar.
                        Has anyone considered civil disobedience?

                            I wonder what would happen if all the
                        installers banded together and refused, as a
                        united industry ‘brotherhood.’ WE are the
                        ones stuck with the bullshit in the aftermath.

                             I’m not being snarky here , this a
                        genuine question to the group: Does anyone
                        have _good_ experience with RSD? i.e. you’re
                        really glad RSD was there, and you genuinely
                        feel safer?  you’re glad and happy to comply
                        with this code and you look forward to
                        continuing to use RSD for the rest of your
                        career?

                        On Fri, Feb 14, 2025 at 3:40 PM Ray Walters
                        via RE-wrenches
                        <[email protected]> wrote:

                            it seems silly that we are required to
                            install these extra pieces of equipment
                            for added "safety", that are actually a
                            fire hazard on the roof. Just to survey
                            again: how many homes have been saved by
                            RSD? How many fire fighters have actually
                            actuated the RSD system, so that they
                            could hack through the array to vent the
                            roof?

                            I think it should only be required if you
                            have covered so much of the roof with PV,
                            that the fire dept can't access uncovered
                            roof to do their venting.  The whole
                            premise of RSD is flawed.  IMHO, its just
                            another effort to block the wider
                            adoption of solar.

                            When it comes to off grid, RSD causes
                            such a decrease in reliability to amount
                            to a decrease in safety, due to possible
                            loss of communications, water, and heat. 
                            Add the fire hazard and RSD is really not
                            making our customers' lives better.

                            Ray Walters
                            Remote Solar

                    _______________________________________________
                    List sponsored by Redwood Alliance

                    Pay optional member dues here: http://re-wrenches.org

                    List Address: [email protected]

                    Change listserver email address & settings:
                    
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

                    There are two list archives for searching. When
                    one doesn't work, try the other:
                    
https://www.mail-archive.com/[email protected]/
                    
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

                    List rules & etiquette:
                    http://www.re-wrenches.org/etiquette.htm

                    Check out or update participant bios:
                    http://www.members.re-wrenches.org

                    _______________________________________________
                    List sponsored by Redwood Alliance

                    Pay optional member dues here: http://re-wrenches.org

                    List Address: [email protected]

                    Change listserver email address & settings:
                    
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

                    There are two list archives for searching. When
                    one doesn't work, try the other:
                    
https://www.mail-archive.com/[email protected]/
                    
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

                    List rules & etiquette:
                    http://www.re-wrenches.org/etiquette.htm

                    Check out or update participant bios:
                    http://www.members.re-wrenches.org

                _______________________________________________
                List sponsored by Redwood Alliance

                Pay optional member dues here: http://re-wrenches.org

                List Address: [email protected]

                Change listserver email address & settings:
                
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

                There are two list archives for searching. When one
                doesn't work, try the other:
                https://www.mail-archive.com/[email protected]/
                
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

                List rules & etiquette:
                http://www.re-wrenches.org/etiquette.htm

                Check out or update participant bios:
                http://www.members.re-wrenches.org


            _______________________________________________
            List sponsored by Redwood Alliance

            Pay optional member dues here:http://re-wrenches.org

            List Address:[email protected]

            Change listserver email address & settings:
            http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

            There are two list archives for searching. When one doesn't work, 
try the other:
            https://www.mail-archive.com/[email protected]/
            http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

            List rules & etiquette:
            http://www.re-wrenches.org/etiquette.htm

            Check out or update participant bios:
            http://www.members.re-wrenches.org

-- Christopher Warfel, PE
        ENTECH Engineering, Inc.
        PO Box 871, Block Island, RI 02807
        (401) 447-5773


-- Christopher Warfel, PE
    ENTECH Engineering, Inc.
    PO Box 871, Block Island, RI 02807
    (401) 447-5773

    _______________________________________________
    List sponsored by Redwood Alliance

    Pay optional member dues here: http://re-wrenches.org

    List Address: [email protected]

    Change listserver email address & settings:
    http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

    There are two list archives for searching. When one doesn't work,
    try the other:
    https://www.mail-archive.com/[email protected]/
    http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

    List rules & etiquette:
    http://www.re-wrenches.org/etiquette.htm

    Check out or update participant bios:
    http://www.members.re-wrenches.org

--
Christopher Warfel, PE
ENTECH Engineering, Inc.
PO Box 871, Block Island, RI 02807
(401) 447-5773
_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to