I was told specifically by Midnite Tech support that the AIO was
designed for parallel conductors. There isn't anything in the manual
that contradicts that, that I'm aware of.
I have never considered 2 lugs on a single bolt a violation. Its when
two conductors go into a single lug that is not designed for 2
conductors, that it's considered double lugging. If 2 lugs on one bolt
were not legal, how in the world would you ever wire L16s, golf cart
batteries, etc. in parallel?
Ray Walters
Remote Solar
On 7/17/2025 3:50 PM, Jason Szumlanski via RE-wrenches wrote:
This is an interesting option. I think it goes against the manual,
however, which could be flagged as a code violation.
I also considered Polaris taps that are rated for fine-stranded wire.
Jason Szumlanski
Principal Solar Designer | Florida Solar Design Group
NABCEP Certified Solar Professional (PVIP)
Florida State Certified Solar Contractor CVC56956
Florida Certified Electrical Contractor EC13013208
On Thu, Jul 17, 2025 at 11:41 AM Zeke Yewdall via RE-wrenches
<[email protected]
<mailto:[email protected]>> wrote:
I have done several systems where we just paralleled two
batteries on the battery terminals, just like we'd do with lead
acid batteries, with a reverse return for the home runs. With the
active balancing, the reverse return is apparently not as
important, but I still think it's best practice.
MidNite Power is working on a custom gutter/wiring box for
coupling the PF16's directly to the AIO, but not sure on timeline
for it. I've seen a few really nice installs where someone used a
standard 10" gutter with cutouts in it directly on top of the
PF16's, then set the AIO's on top of that. No exposed wiring or
even conduit showing.
Zeke
--
Zeke Yewdall
PV Engineer
NABCEP #031508-89
[email protected]
303-523-3592
_______________________________________________
List sponsored by Redwood Alliance
Pay optional member dues here: http://re-wrenches.org
List Address: [email protected]
<mailto:[email protected]>
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
<http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>
There are two list archives for searching. When one doesn't work,
try the other:
https://www.mail-archive.com/[email protected]/
<https://www.mail-archive.com/[email protected]/>
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
<http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org>
List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm
<http://www.re-wrenches.org/etiquette.htm>
Check out or update participant bios:
http://www.members.re-wrenches.org
<http://www.members.re-wrenches.org>
_______________________________________________
List sponsored by Redwood Alliance
Pay optional member dues here:http://re-wrenches.org
List Address:[email protected]
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
http://www.members.re-wrenches.org
_______________________________________________
List sponsored by Redwood Alliance
Pay optional member dues here: http://re-wrenches.org
List Address: [email protected]
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
http://www.members.re-wrenches.org