A word of caution – the XW Pro is, IMO a major downgrade from any previous 
XW’s. The newest firmware causes all sorts of power quality issues if you are 
running a generator. Like it literally smoked electronics for some clients. 
Schneider knows, they just don’t care. There’s good reason these units are 
going cheap now to dump obsolete inventory.

XW Lithium integration is through the Insight Home or Gateway monitoring 
devices. It can be done, but in my experience it’s constantly glitching out and 
not delivering reliable power solutions to clients.

I generally recommend to clients if they want newest battery tech, let’s 
upgrade the inverter as well. Less call backs.

Kevin

From: RE-wrenches <[email protected]> On Behalf Of Jay 
via RE-wrenches
Sent: Monday, October 27, 2025 5:23 AM
To: RE-wrenches <[email protected]>
Cc: Jay <[email protected]>
Subject: Re: [RE-wrenches] Schneider XW+ and Midnite batteries

I just had a conversation with someone about this the other day and he 
recommended buying an xw pro which he said has the latest firmware and can do 
lithium communication much easier than the older xw.

I haven’t researched it but if true you can buy a new xw pro from NWS for under 
$900.

Jay


On Oct 26, 2025, at 9:42 PM, Howie Michaelson via RE-wrenches 
<[email protected]<mailto:[email protected]>> 
wrote:

Has anyone successfully close-looped a Schneider XW+ with Midnite PF16 
batteries, or any other battery BMS that uses Pylon? I have a client that 
currently has an XW= running on a set of 2 volt Surrettes that are failing.  
I'd like to switch him out to an AIO/PF16 system, but want to give him the 
option of keeping the XW+ (which is paired with 2 Outback150vDC Charge 
Controllers). The mixed brand Inverter-Charge Controller setup gives me some 
pause if keeping that, but if necessary, I just want to hear success stories if 
they are out there.
Thanks,
Howie Michaelson
Sun Catcher

_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: 
[email protected]<mailto:[email protected]>

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org
_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to