For you Wrenches using EG4: I'm contemplating a system design that would benefit tremendously if I could AC Couple PV to the GridBOSS on the backed up load port, but I don't see that documented as a method of AC Coupling. I know you can AC Couple up to 125A OCPD through a Smart Load port in the GridBOSS, but the AC Coupled PV in this scenario would be 400 feet away, and it could be connected to the backed up load center at that location (presumably via a feeder tap just on the line side of the load center with main breaker installed). I'm trying to avoid running a 125A circuit 400 feet back to the GridBOSS, and there are some code issues with doing that (multiple feeders between buildings being the biggest problem).
I did find a document that allows AC Coupled PV on the load port of the FlexBOSS in this scenario, but that does not help me. The FlexBoss connects to the GridBOSS through its Grid port, so it's a different scenario. I reached out to EG4 about this, but I was wondering if anyone here has some insight. Jason Szumlanski Florida Solar Design Group
_______________________________________________ List sponsored by Redwood Alliance Pay optional member dues here: http://re-wrenches.org List Address: [email protected] Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org There are two list archives for searching. When one doesn't work, try the other: https://www.mail-archive.com/[email protected]/ http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: http://www.re-wrenches.org/etiquette.htm Check out or update participant bios: http://www.members.re-wrenches.org