Kirk,    it sounds like phase imbalance is not a problem

On Fri, Dec 19, 2025 at 2:42 PM Kirk Herander <[email protected]> wrote:

> Hi,
> I’ve done one large off grid system with 480 -3 - phase inverters and 1
> mwh, 850 vdc LFP storage.
>
> We created 240vac  by stepping each 480v L-L phase down to 240 through its
> own transformer of proper size.
> So we have three 240/120 VAC panels for typical household loads.
>
>
> *Kirk Herander / **[email protected] <[email protected]>*
>
> *Owner|Principal, VT Solar, LLC*
>
> *Celebrating our 34st Anniversary 1991-2025!!*
>
> dba Vermont Solar Engineering
>
> 802.559.1225
>
>
> On Fri, Dec 19, 2025 at 5:25 PM david quattro via RE-wrenches <
> [email protected]> wrote:
>
>> I’ve thought about HV and 60K model, but my loads are 240 Single phase,
>> across 5 separate contiguous parcels.  all these homes already have their
>> own utility meters.  There is one owner.  The plan is to have an ATS at
>> each meter.
>>    Regarding 3 phase offgrid, I’ve been concerned about phase imbalance.
>> Maybe I don’t need to worry about that.
>>
>>
>>
>> On Fri, Dec 19, 2025 at 1:51 PM Michael Morningstar via RE-wrenches <
>> [email protected]> wrote:
>>
>>> A couple or three Discover HVs and Sol-Ark 60ks. Done quickly
>>>
>>> On Fri, Dec 19, 2025 at 1:00 PM Kirk Herander via RE-wrenches <
>>> [email protected]> wrote:
>>>
>>>> Why 48v, why not commercial DC, like 850? What are you looking at for
>>>> kwh storage? A1000vdc buss, homemade or otherwise, would drop the buss
>>>> rating down to about 300 A. Commercial grade  inverters, such as 3-phase
>>>> Delta PCS inverters are spec'ed for these situations.
>>>>
>>>> On Fri, Dec 19, 2025 at 1:13 PM david quattro via RE-wrenches <
>>>> [email protected]> wrote:
>>>>
>>>>> Hi everyone,
>>>>>    I am still helping an uber wealthy owner determine if he really
>>>>> wants this much power. If he does, do any of you have experience sourcing 
>>>>> a
>>>>> 48v battery-combiner on the order of 4500 to 5000 amps?
>>>>>   I also want to get clear on how to best wire from batteries to
>>>>> combiner, and from combiner to inverters. I read here on the Wrenches list
>>>>> about some electricians who strategically sized conductor AWG so that
>>>>> resistance matches, which seems straightforward once we get our components
>>>>> mounted and accurate distances can be determined. Can anyone on list
>>>>> provide feedback about that, I really appreciate it!
>>>>> Thank you
>>>>> _______________________________________________
>>>>> List sponsored by Redwood Alliance
>>>>>
>>>>> Pay optional member dues here: http://re-wrenches.org
>>>>>
>>>>> List Address: [email protected]
>>>>>
>>>>> Change listserver email address & settings:
>>>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>>>
>>>>> There are two list archives for searching. When one doesn't work, try
>>>>> the other:
>>>>> https://www.mail-archive.com/[email protected]/
>>>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>>>
>>>>> List rules & etiquette:
>>>>> http://www.re-wrenches.org/etiquette.htm
>>>>>
>>>>> Check out or update participant bios:
>>>>> http://www.members.re-wrenches.org
>>>>>
>>>>>
>>>>
>>>> --
>>>>
>>>>
>>>> *Kirk Herander / **[email protected] <[email protected]>*
>>>>
>>>> *Owner|Principal, VT Solar, LLC*
>>>>
>>>> *Celebrating our 34st Anniversary 1991-2025!!*
>>>>
>>>> dba Vermont Solar Engineering
>>>>
>>>> 802.559.1225
>>>> _______________________________________________
>>>> List sponsored by Redwood Alliance
>>>>
>>>> Pay optional member dues here: http://re-wrenches.org
>>>>
>>>> List Address: [email protected]
>>>>
>>>> Change listserver email address & settings:
>>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>>
>>>> There are two list archives for searching. When one doesn't work, try
>>>> the other:
>>>> https://www.mail-archive.com/[email protected]/
>>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>>
>>>> List rules & etiquette:
>>>> http://www.re-wrenches.org/etiquette.htm
>>>>
>>>> Check out or update participant bios:
>>>> http://www.members.re-wrenches.org
>>>>
>>>>
>>>
>>> --
>>>
>>> Michael Morningstar
>>>
>>>
>>> Morningstar Electric Inc
>>>
>>> PO Box 1494
>>>
>>> Mount Shasta, CA 96067
>>>
>>> 530-921-0560
>>>
>>> CSLB 1116835
>>>
>>> [email protected]
>>>
>>>
>>> _______________________________________________
>>> List sponsored by Redwood Alliance
>>>
>>> Pay optional member dues here: http://re-wrenches.org
>>>
>>> List Address: [email protected]
>>>
>>> Change listserver email address & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>
>>> There are two list archives for searching. When one doesn't work, try
>>> the other:
>>> https://www.mail-archive.com/[email protected]/
>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>
>>> List rules & etiquette:
>>> http://www.re-wrenches.org/etiquette.htm
>>>
>>> Check out or update participant bios:
>>> http://www.members.re-wrenches.org
>>>
>>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> Pay optional member dues here: http://re-wrenches.org
>>
>> List Address: [email protected]
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> There are two list archives for searching. When one doesn't work, try the
>> other:
>> https://www.mail-archive.com/[email protected]/
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org
>>
>>
_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to