It’ll work fine no problems. 

Open loop of course. 

Jay

> On Dec 22, 2025, at 12:50 PM, Chris Daum via RE-wrenches 
> <[email protected]> wrote:
> 
> 
> RE:  Closed loop communications…  I have a customer who needs to replace his 
> old AGMs; he’s looking at getting something like 2500ah @ 24V and wants LFPs. 
>  This is a battery based, grid tie system.  His equipment is a pair of 
> XW4024s (Schneider – and he has NO interest in replacing his inverters) and 
> three Classic (Midnite) charge controllers.  I’m concerned with integrating 
> the LFPs with his old inverter, but his Classics, I believe, can be 
> reprogrammed to accommodate the LFPs.  This system was installed around 2015 
> so the equipment is not new – but it’s basically been humming along until a 
> couple of weeks ago, when there was a week of 60 to 90 MPH winds that killed 
> the power for a while.  This is near Boulder, CO (at 9000 ft elevation).  His 
> system worked fine til his old AGMs gave out.  Their power was out for ~3 
> days, then came on for 2 days, then went out again for a couple of days.  So 
> he realized how undersized and old his batteries were.
>  
> If he gets some new LFPs, do you think they’ll work with this vintage 
> equipment?  Any of your wonderful advice to pass along!?   I’m thinking the 
> Classics can dial in the settings he needs.
>  
> Thanks, y’all!
>  
> Chris Daum
> Oasis Montana Inc.
> 406-777-4309 or 4321
> 406-777-4309 fax
>  
>  
>  
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> Pay optional member dues here: http://re-wrenches.org
> 
> List Address: [email protected]
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> There are two list archives for searching. When one doesn't work, try the 
> other:
> https://www.mail-archive.com/[email protected]/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> http://www.members.re-wrenches.org
> 
_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to