I seem to remember this was an issue a long time ago. The GTI was some sort of 
fix. 

I’d install a manual transfer switch as I presume the inverter/solar  is now 
battery backup?

Or you could use a breaker box with an interlock kit. 

Good luck

Jay

> On Jan 10, 2026, at 2:13 PM, David Palumbo via RE-wrenches 
> <[email protected]> wrote:
> 
> 
> Wrench,
> 
> An off-grid installation of mine from many years ago has is now using grid 
> power instead of a generator. The utility is telling the homeowner that they 
> are going to disconnect him because his house is back feeding 1 amp into 
> their grid power.
> 
> I've been retired for many years now and did not do any of the work to 
> connect the utility power to his Trace SW4024 inverter/charger. The utility 
> power became available when his son brought in utility power for his maple 
> sugaring operation in the neighborhood, and the father connected power to his 
> house to replace his fossil fueled generator for additional charging into his 
> battery bank. They do not have a grid interconnect sellback agreement with 
> the utility.
> 
> I have no experience with this, but I'm assuming that the utility grid is 
> seeing power from its input connection to his Trace SW4024. Does that sound 
> right? If so, is there a simple solution to fix this problem while continuing 
> to use the grid power through his SW inverter? 
> 
> Thanks for any advice that may help.
> 
> David Palumbo
> Hyde Park, VT
> 
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> Pay optional member dues here: http://re-wrenches.org
> 
> List Address: [email protected]
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> There are two list archives for searching. When one doesn't work, try the 
> other:
> https://www.mail-archive.com/[email protected]/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> http://www.members.re-wrenches.org
> 
_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org