Normally when grounding electrical and stakes  we drive the rrod , connect the 
ground strap having sanded the connection and clamp securely then spray with a 
special metalic paint , been doing this a long time with good success. 

________________________________
> To: Repeater-Builder@yahoogroups.com
> From: gascha...@comcast.net
> Date: Tue, 30 Jun 2009 23:23:43 -0500
> Subject: RE: [Repeater-Builder] Re: DC Ground Lightning Protection / Concrete 
> Electrode
>
>
>
>
>
>
>
>
>
>
>
>
>
>
>
>
>
>
>
>
>
>
>
>
>
>
>
>
>
>
>
>
>
>
>
> Actually galvanized and copper plated
> ground rods should not be mixed in any ground system. Electrolysis will 
> deplete
> the plating. All ground rods in any ground system are electrically connected 
> to
> one another.
>
>
>
>
>
>
>
> 73
>
>
>
> Gary k4FMX
>
>
>
>
>
>
>
>
>
>
>
>
> ________________________________
>
>
>
>
>
> From: Repeater-Builder@yahoogroups.com 
> [mailto:repeater-buil...@yahoogroups.com] On Behalf Of Glenn Little WB4UIV
>
> Sent: Tuesday, June 30, 2009 7:53
> PM
>
> To: Repeater-Builder@yahoogroups.com
>
> Subject: Re: [Repeater-Builder]
> Re: DC Ground Lightning Protection / Concrete Electrode
>
>
>
>
>
>
>
>
>
>
>
>
> Another way to pass a ground cable through
> concrete is via a PVC pipe. The last thing that you want to do is run a ground
> cable that can carry lightning fault current through concrete without 
> isolating
> the cable from the concrete.
>
> The fault current will rapidly heat the ground cable, causing it to expand, at
> the same time vaporizing the water trapped in the concrete. The result is a
> violent steam explosion. The results could be the total fragmentation of the
> concrete.
>
>
>
> MIL HDBK 419 is available for download. This is a military manual that
> addresses grounding.
>
> Another very respected guide is Motorola R-56.
>
>
>
> Galvanized ground rods should only be used at the guy anchor points.
>
> Copper plated ground rods should be used around the tower base and the 
> building
> with all bonded together by exothermic welds 18 inches below grade.
>
> Ground rods are to be placed no closer than twice the length of the rod.
>
> Any closer and you are wasting your funds.
>
>
>
> YMMV.
>
>
>
> 73
>
> Glenn
>
> WB4UIV
>
>
>
> At 10:07 AM 6/30/2009, you wrote:
>
>
>
>
>
>
>
>
>
>
>
>
> I'm going to disagree with the
> following posting:
>
>
>
> If the tower is bolted to galvanized pipe that is embedded in concrete of
>
> which a significant amount is in contact with soil, you have a
>
> "concrete-encased grounding electrode" which is hard to improve upon.
> It is
>
> not likely that a ground rod would be worthwhile, since damp concrete
>
> (concrete in intimate contact with soil at grade level) is a fairly good
>
> conductor, and such a footing or foundation has hundreds of times the
>
> surface area of a ground rod.
>
>
>
> I have
> read Ericsson specs for cellular tower installation in that disagrees with the
> previous statement.
>
>
>
> Standard
> concrete without conductive enhancing materials can crack, pop or crumble if
> subjected to a direct lightning strike if ground rods are not properly
> installed. The water contained within the concrete will vaporize
> instantly causing the concrete to fail.
>
>
>
> There
> are types of conductive concrete mixes or additives that can be used, but the
> most common practice is to use a ground rod from each leg with a copper wire
> bonded to each tower leg.
>
>
>
> Our
> mfg building at work is made from steel I-Beams into concrete. I have
> noticed each I-Beam has its own ground connection. The strap is bolted to
> the beam about 1" above the concrete, then disappears into the concrete,
> and suspect there is a ground rod going into the soil beneath the concrete
> piling, but thats just a theory, as I dident see it before the mud was
> poured.
>
>
>