1) that a mib browser, that something we're working on...could be in v5 or
v5.1 
 
 
3) so you would want not only the name of the OID but also the description?
For the received traps only or also for the checks that you defined?
If for the check I would guess that we could have a parameter that if used
with the REMARK field would give you the full description as remark for that
entry.
 

Dirk.


 

  _____  

From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf
Of Michael D. Shook
Sent: Thursday, December 02, 2004 4:13 PM
To: [EMAIL PROTECTED]
Subject: RE: [SA-list] SNMP OID -> text



1)       IF you (SA) have the complete MIB files for my device, then I would
think it would be easiest if I could browse via a GUI interface out the text
OID tree to find the OID I want. Then if it's kept as a number internally to
SA, it wouldn't matter; you'd only have to deal with the full text during a
browsing situation. That way I wouldn't have to use a separate tool like
GetIF to figure out what I wanted to do. If this little GUI also had the
ability to run an instant check (Get Now), then it's even easier. Especially
for those who have never dealt with SNMP before. (kinda build in the
MBrowser portion of GetIF)

2)       I think for my end users, I'd need an alert like "ImportantDevice
is DOWN (check returned: CreateAndGo)", because only I or the setter-upper
would really remember what all of the status's mean. 

3)       Finally (?) I'd like the option to somehow return the description
or lookup the description for each check because as you can see from the
example below, the status text is necessarily short, but doesn't quite have
good enough information for someone who isn't intimately familiar with the
device or check.

 

 

Sample MIB OID entry (from an APC UPS):

upsAdvInputLineFailCause OBJECT-TYPE

   SYNTAX INTEGER  {

      noTransfer(1),

      highLineVoltage(2),

      brownout(3),

      blackout(4),

      smallMomentarySag(5),

      deepMomentarySag(6),

      smallMomentarySpike(7),

      largeMomentarySpike(8),

      selfTest(9),

      rateOfVoltageChnage(10)

   }

   ACCESS read-only

   STATUS mandatory

   DESCRIPTION

      "The reason for the occurrence of the last transfer to UPS

       battery power.  The variable is set to:

       - noTransfer(1) -- if there is no transfer yet.

       - highLineVoltage(2) -- if the transfer to battery is caused

       by an over voltage greater than the high transfer vloltage.

       - brownout(3) -- if the duration of the outage is greater than

       five seconds and the line voltage is between 40% of the

       rated output voltage and the low transfer voltage.

       - blackout(4) -- if the duration of the outage is greater than five

       seconds and the line voltage is between 40% of the rated 

       output voltage and ground.

       - smallMomentarySag(5) -- if the duration of the outage is less

       than five seconds and the line voltage is between 40% of the

       rated output voltage and the low transfer voltage.

       - deepMomentarySag(6) -- if the duration of the outage is less 

       than five seconds and the line voltage is between 40% of the 

       rated output voltage and ground.  The variable is set to 

       - smallMomentarySpike(7) -- if the line failure is caused by a

       rate of change of input voltage less than ten volts per cycle.

       - largeMomentarySpike(8) -- if the line failure is caused by 

       a rate of change of input voltage greater than ten volts per cycle.

       - selfTest(9) -- if the UPS was commanded to do a self test.

       - rateOfVoltageChange(10) -- if the failure is due to the rate of
change of

       the line voltage."

   ::= { upsAdvInput 5 }