Re: ISO TR 10605 test setup (ESD)
<83d652574e7af740873674f9fc12dbaa675...@utexh1w2.gnnettest.com>, Chris Maxwell inimitably wrote: >The GRP's connection to Earth ground serves two purposes. It is a low >frequency ground connection to ensure that, over time, the GRP's DC >potential won't change with respect to Earth ground. The GRP's Earth ground >connection also ensures that the GRP has a low frequency common with any >Earth grounds that the device under test may have. > >It is my belief that you don't need a dedicated ground rod for your ESD >setup to satisfy this requirement. Is right what he say. Refer everything in the test set-up to the GRP and just run a drain wire to the mains earth. -- Regards, John Woodgate, OOO - Own Opinions Only. Phone +44 (0)1268 747839 Fax +44 (0)1268 777124. http://www.jmwa.demon.co.uk Why not call a vertically- applied manulo-pedally-operated quasi-planar chernozem-penetrating and excavating implement a SPADE? --- This message is from the IEEE EMC Society Product Safety Technical Committee emc-pstc discussion list. Visit our web site at: http://www.ewh.ieee.org/soc/emcs/pstc/ To cancel your subscription, send mail to: majord...@ieee.org with the single line: unsubscribe emc-pstc For help, send mail to the list administrators: Michael Garretson:pstc_ad...@garretson.org Dave Healddavehe...@mediaone.net For policy questions, send mail to: Richard Nute: ri...@ieee.org Jim Bacher: j.bac...@ieee.org All emc-pstc postings are archived and searchable on the web at: http://www.rcic.com/ click on "Virtual Conference Hall,"
RE: ISO TR 10605 test setup (ESD)
Just one more comment: You never want a separate ground to a GRP that is different from other grounds in the building and more importantly, in the test area. There is a real risk of the GRP being at a different potential than other grounds, even if it is connected to a ground rod. Others have measured significant potentials between separate grounds in the same building.. Mike Hopkins KeyTek -Original Message- From: Chris Maxwell [mailto:chris.maxw...@nettest.com] Sent: Tuesday, June 19, 2001 8:46 AM To: 'Chris Chileshe'; emc-p...@majordomo.ieee.org Subject: RE: ISO TR 10605 test setup (ESD) Hi from one Chris to another, I'm going to address your "ground rod" concerns (Question 3). In our lab here, we have a new building with new wiring and a reliable third wire Earth ground, so I simply tie my Ground Reference Plane ("GRP") to the third wire of one of the AC outlets in the room. I have a cable from the GRP to the outlet with a ring lug. The ring lug is screwed to the ground connection with a lock washer and screw. I occassionally verify this ground connection with a ohmmeter. All devices under test are plugged into these same AC outlets (unless they're battery powered), so my GRP is "common" with all of my device under test Earth ground connections. If you used a doctored plug, the only concern that I would have would be with regard to the connection coming loose. However, I noticed that you're in the UK where they use that three pound broad sword for the AC ground terminal. It would probably take an earthquake to loosen that thing. But, I would still verify the connection with an ohmmeter. I have talked to many people about this; and this is the "collective rationale" that I have gathered. An ESD test setup needs to have a stable reference potential set by the GRP. The ESD gun's ground strap is tied to the GRP and all discharge potentials are then referenced to the GRP. Since the GRP is large and wide; it has low inductance along with a large amount of free space capacitance. The GRP is a very good high frequency ground potential. This means that the GRP's potential won't change much when the ESD current is bled into it. This keeps results repeatable. Just by having a GRP, you have satisfied 99% of the grounding requirements for a good ESD test . Now, why tie the GRP to Earth? The GRP's connection to Earth ground serves two purposes. It is a low frequency ground connection to ensure that, over time, the GRP's DC potential won't change with respect to Earth ground. The GRP's Earth ground connection also ensures that the GRP has a low frequency common with any Earth grounds that the device under test may have. It is my belief that you don't need a dedicated ground rod for your ESD setup to satisfy this requirement. My opinions only; not to be confused with fact, company policy or gospel under any circumstance :-) Chris Maxwell Design Engineer - NetTest Optical Division email chris.maxw...@nettest.com phone +1 315 266 5128 fax +1 315 797 8024 NetTest 6 Rhoads Drive, Utica, NY 13502 USA web www.nettest.com > -Original Message- > From: Chris Chileshe [SMTP:chris.chile...@ultronics.co.uk] > Sent: Tuesday, June 19, 2001 5:22 AM > To: emc-p...@majordomo.ieee.org > Subject: ISO TR 10605 test setup (ESD) > > > Hi group > > For those of you unfamiliar with ISO TR 10605, it is the ESD > test standard for automotive electronics (8kV contact, 25kV > air). > > I am trying to perform quick ESD tests on a product which has > bottom entry proprietary cable. Picture if you an upside-down > bottle of coke with push buttons at the top and cable entry at > the bottom end. > > The cable itself is screened multicore with a molded end connector > so there is a minimum length it must protrude from the product before > it even thinks about bending. This is about an inch and a half > (about 40mm). > > According to ISO TR 10605, if insulation is required under the > EUT, the insulation must support the EUT some 25mm above > the ground plane. > > Question 1: Does this insulation have to be 25mm thick or can > I make a table like structure with thinner insulating sheet and > supporting pillars at the corners? > > Question 2: Would a more 'compliant' test set-up have the bottle > of coke lying on its side rather than standing vertically as it would > in practice? > > The setup for the ESD test shows a ground strap connect the plane > to a grounding rod. We had a specialised ESD test area where I worked > before but we took everything for granted and didn't really bother finding > out where or how the ground connection was made! > > Question 3: Can I connect the ground strap via say a UK 3-pin plug > (with
RE: ISO TR 10605 test setup (ESD)
A third reason to tie the GRP to earth is safety. An ungrounded GRP could be very hazardous around AC mains voltages. Chris Maxwell @majordomo.ieee.org on 06/19/2001 08:46:30 AM Please respond to Chris Maxwell Sent by: owner-emc-p...@majordomo.ieee.org To: "'Chris Chileshe'" , emc-p...@majordomo.ieee.org cc: Subject: RE: ISO TR 10605 test setup (ESD) Hi from one Chris to another, I'm going to address your "ground rod" concerns (Question 3). In our lab here, we have a new building with new wiring and a reliable third wire Earth ground, so I simply tie my Ground Reference Plane ("GRP") to the third wire of one of the AC outlets in the room. I have a cable from the GRP to the outlet with a ring lug. The ring lug is screwed to the ground connection with a lock washer and screw. I occassionally verify this ground connection with a ohmmeter. All devices under test are plugged into these same AC outlets (unless they're battery powered), so my GRP is "common" with all of my device under test Earth ground connections. If you used a doctored plug, the only concern that I would have would be with regard to the connection coming loose. However, I noticed that you're in the UK where they use that three pound broad sword for the AC ground terminal. It would probably take an earthquake to loosen that thing. But, I would still verify the connection with an ohmmeter. I have talked to many people about this; and this is the "collective rationale" that I have gathered. An ESD test setup needs to have a stable reference potential set by the GRP. The ESD gun's ground strap is tied to the GRP and all discharge potentials are then referenced to the GRP. Since the GRP is large and wide; it has low inductance along with a large amount of free space capacitance. The GRP is a very good high frequency ground potential. This means that the GRP's potential won't change much when the ESD current is bled into it. This keeps results repeatable. Just by having a GRP, you have satisfied 99% of the grounding requirements for a good ESD test . Now, why tie the GRP to Earth? The GRP's connection to Earth ground serves two purposes. It is a low frequency ground connection to ensure that, over time, the GRP's DC potential won't change with respect to Earth ground. The GRP's Earth ground connection also ensures that the GRP has a low frequency common with any Earth grounds that the device under test may have. It is my belief that you don't need a dedicated ground rod for your ESD setup to satisfy this requirement. My opinions only; not to be confused with fact, company policy or gospel under any circumstance :-) Chris Maxwell Design Engineer - NetTest Optical Division email chris.maxw...@nettest.com phone +1 315 266 5128 fax +1 315 797 8024 NetTest 6 Rhoads Drive, Utica, NY 13502 USA web www.nettest.com > -Original Message- > From: Chris Chileshe [SMTP:chris.chile...@ultronics.co.uk] > Sent: Tuesday, June 19, 2001 5:22 AM > To: emc-p...@majordomo.ieee.org > Subject: ISO TR 10605 test setup (ESD) > > > Hi group > > For those of you unfamiliar with ISO TR 10605, it is the ESD > test standard for automotive electronics (8kV contact, 25kV > air). > > I am trying to perform quick ESD tests on a product which has > bottom entry proprietary cable. Picture if you an upside-down > bottle of coke with push buttons at the top and cable entry at > the bottom end. > > The cable itself is screened multicore with a molded end connector > so there is a minimum length it must protrude from the product before > it even thinks about bending. This is about an inch and a half > (about 40mm). > > According to ISO TR 10605, if insulation is required under the > EUT, the insulation must support the EUT some 25mm above > the ground plane. > > Question 1: Does this insulation have to be 25mm thick or can > I make a table like structure with thinner insulating sheet and > supporting pillars at the corners? > > Question 2: Would a more 'compliant' test set-up have the bottle > of coke lying on its side rather than standing vertically as it would > in practice? > > The setup for the ESD test shows a ground strap connect the plane > to a grounding rod. We had a specialised ESD test area where I worked > before but we took everything for granted and didn't really bother finding > out where or how the ground connection was made! > > Question 3: Can I connect the ground strap via say a UK 3-pin plug > (with live and neutral prongs removed) into a mains socket or is this > asking for trouble (RCD's etc). > > Grateful for any advice > > Regards > > - Chris Chileshe > > > ___
RE: ISO TR 10605 test setup (ESD)
Hi from one Chris to another, I'm going to address your "ground rod" concerns (Question 3). In our lab here, we have a new building with new wiring and a reliable third wire Earth ground, so I simply tie my Ground Reference Plane ("GRP") to the third wire of one of the AC outlets in the room. I have a cable from the GRP to the outlet with a ring lug. The ring lug is screwed to the ground connection with a lock washer and screw. I occassionally verify this ground connection with a ohmmeter. All devices under test are plugged into these same AC outlets (unless they're battery powered), so my GRP is "common" with all of my device under test Earth ground connections. If you used a doctored plug, the only concern that I would have would be with regard to the connection coming loose. However, I noticed that you're in the UK where they use that three pound broad sword for the AC ground terminal. It would probably take an earthquake to loosen that thing. But, I would still verify the connection with an ohmmeter. I have talked to many people about this; and this is the "collective rationale" that I have gathered. An ESD test setup needs to have a stable reference potential set by the GRP. The ESD gun's ground strap is tied to the GRP and all discharge potentials are then referenced to the GRP. Since the GRP is large and wide; it has low inductance along with a large amount of free space capacitance. The GRP is a very good high frequency ground potential. This means that the GRP's potential won't change much when the ESD current is bled into it. This keeps results repeatable. Just by having a GRP, you have satisfied 99% of the grounding requirements for a good ESD test . Now, why tie the GRP to Earth? The GRP's connection to Earth ground serves two purposes. It is a low frequency ground connection to ensure that, over time, the GRP's DC potential won't change with respect to Earth ground. The GRP's Earth ground connection also ensures that the GRP has a low frequency common with any Earth grounds that the device under test may have. It is my belief that you don't need a dedicated ground rod for your ESD setup to satisfy this requirement. My opinions only; not to be confused with fact, company policy or gospel under any circumstance :-) Chris Maxwell Design Engineer - NetTest Optical Division email chris.maxw...@nettest.com phone +1 315 266 5128 fax +1 315 797 8024 NetTest 6 Rhoads Drive, Utica, NY 13502 USA web www.nettest.com > -Original Message- > From: Chris Chileshe [SMTP:chris.chile...@ultronics.co.uk] > Sent: Tuesday, June 19, 2001 5:22 AM > To: emc-p...@majordomo.ieee.org > Subject: ISO TR 10605 test setup (ESD) > > > Hi group > > For those of you unfamiliar with ISO TR 10605, it is the ESD > test standard for automotive electronics (8kV contact, 25kV > air). > > I am trying to perform quick ESD tests on a product which has > bottom entry proprietary cable. Picture if you an upside-down > bottle of coke with push buttons at the top and cable entry at > the bottom end. > > The cable itself is screened multicore with a molded end connector > so there is a minimum length it must protrude from the product before > it even thinks about bending. This is about an inch and a half > (about 40mm). > > According to ISO TR 10605, if insulation is required under the > EUT, the insulation must support the EUT some 25mm above > the ground plane. > > Question 1: Does this insulation have to be 25mm thick or can > I make a table like structure with thinner insulating sheet and > supporting pillars at the corners? > > Question 2: Would a more 'compliant' test set-up have the bottle > of coke lying on its side rather than standing vertically as it would > in practice? > > The setup for the ESD test shows a ground strap connect the plane > to a grounding rod. We had a specialised ESD test area where I worked > before but we took everything for granted and didn't really bother finding > out where or how the ground connection was made! > > Question 3: Can I connect the ground strap via say a UK 3-pin plug > (with live and neutral prongs removed) into a mains socket or is this > asking for trouble (RCD's etc). > > Grateful for any advice > > Regards > > - Chris Chileshe > > > _ > This message has been checked for all known viruses by Star Internet > delivered through the MessageLabs Virus Scanning Service. For further > information visit http://www.star.net.uk/stats.asp or alternatively call > 01285 884400. > > --- > This message is from the IEEE EMC Society Product Safety > Technical Committee emc-pstc discussion list. > > Visit our web site at: http://www.ewh.ieee.org/soc/emcs/pstc/ > > To cancel your subscription, send mail to: > majord...@ieee.org > with the single line: > unsubscribe emc-pstc > > For help, send mail to the list ad