Re: [RE-wrenches] Cable tray

2013-03-26 Thread Bill Brooks
William,

 

I have all the respect in the world for you, but I'm not referring to
"basket tray", which is only appropriate for small conductors. I'm talking
about legitimate cable tray that can be up to 12" wide and that has a top
and rungs every 12". The main facilities that use it in the United States
are large industrial facilities. Most electricians don't get to work with
it. It is clearly superior to EMT and is at least as good as IMC without all
the hassle of threaded fittings and setting up expansion joints and worrying
about 20 years of conductors thermal cycling. Even the best electricians
have problems with this stuff.

 

I am talking about projects with 800 foot long feeder runs. We can bring
them in the building and build a rack for the conduit or run covered tray
outside. As the 2014 NEC will require, you will have to use contactor
combiners or some other means to shut down the conductors inside a building.
It's all doable. My recommendation after seeing the aftermath of rooftop
conduit by good electricians is to put cable tray on roofs and use conduit
if you bring the feeders indoors. It will become common practice soon.
Hopefully sooner than later.

 

Bill.

 

From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of William
Miller
Sent: Tuesday, March 26, 2013 9:49 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] Cable tray

 

Bill:

I have to disagree with you on this one.  We can not abandoned a tried and
true practice just because some practitioners don't do it right.  I don't
know how one can justify saying that encapsulating high voltage conductors
in a conduit is less safe than exposed in a flimsy basket.  Consider snow
and ice and falling objects.

Too many installers entered the PV field without first acquiring the
necessary skills as journeymen or women electricians.  I don't see the
benefit of rewriting the code to accommodate a lack of skills in the
industry.

Respectfully,

William Miller

PS:  The temperature adders always encourage us to enter the building
envelope at the first appropriate location to avoid adding them.  Thoughtful
installers will do the same.

Wm


At 10:15 PM 3/25/2013, you wrote:



Content-Type: multipart/alternative;
boundary="=_NextPart_000_00E3_01CE29A6.37CC5110"
Content-Language: en-us

William,
 
I would strongly disagree that conduit is tried and true on rooftops. I have
rarely seen good conduit runs on rooftops. Most electricians have no clue
how to work with expansion joints. Conduit on rooftops is a bad idea in
general. Most conduit runs in big buildings are all done indoors for good
reason. We are the crazy people doing things on the roof. 
 
The sooner we get away from conduit-particularly for long feeder runs-the
better.
 
In Europe they don't have problems with their rooftop wiring systems because
everything is in tray.
 
For those that don't allow cable tray for anything less than 1/0, just
remember that if it isn't called cable tray, then 392 doesn't apply. The NEC
would allow us to use treated lumber in place of cable tray. This makes no
sense.
 
We did some research on the origin of the 1/0 requirement, and it is ancient
and no longer relevant. Just because it is in the code, does not mean it is
correct. That's why we try to fix it every three years.
 
Bill.
 

 

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Cable tray

2013-03-26 Thread William Miller

Bill:

I have to disagree with you on this one.  We can not abandoned a tried and 
true practice just because some practitioners don't do it right.  I don't 
know how one can justify saying that encapsulating high voltage conductors 
in a conduit is less safe than exposed in a flimsy basket.  Consider snow 
and ice and falling objects.


Too many installers entered the PV field without first acquiring the 
necessary skills as journeymen or women electricians.  I don't see the 
benefit of rewriting the code to accommodate a lack of skills in the industry.


Respectfully,

William Miller

PS:  The temperature adders always encourage us to enter the building 
envelope at the first appropriate location to avoid adding 
them.  Thoughtful installers will do the same.


Wm


At 10:15 PM 3/25/2013, you wrote:

Content-Type: multipart/alternative;
boundary="=_NextPart_000_00E3_01CE29A6.37CC5110"
Content-Language: en-us

William,

I would strongly disagree that conduit is tried and true on rooftops. I 
have rarely seen good conduit runs on rooftops. Most electricians have no 
clue how to work with expansion joints. Conduit on rooftops is a bad idea 
in general. Most conduit runs in big buildings are all done indoors for 
good reason. We are the crazy people doing things on the roof.


The sooner we get away from conduit­particularly for long feeder runs­the 
better.


In Europe they don’t have problems with their rooftop wiring systems 
because everything is in tray.


For those that don’t allow cable tray for anything less than 1/0, just 
remember that if it isn’t called cable tray, then 392 doesn’t apply. The 
NEC would allow us to use treated lumber in place of cable tray. This 
makes no sense.


We did some research on the origin of the 1/0 requirement, and it is 
ancient and no longer relevant. Just because it is in the code, does not 
mean it is correct. That’s why we try to fix it every three years.


Bill.


From: re-wrenches-boun...@lists.re-wrenches.org 
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of William Miller

Sent: Monday, March 25, 2013 9:30 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] Cable tray

David:

Of course, I understand that you are not saying we can willfully disregard 
the Code in anticipation of future clarification.  I was just 
extrapolating on your idea.


If we want an exception based on a predicted update in the code, we are at 
the mercy of the AHJ who may or may not be convinced.  I think most AHJs 
are willing to diverge from the Code in a more strict interpretation, but 
not the reverse. Right now, as I read it, unless the leads are 1/0 or 
larger, we are forbade.


I treat PV systems like rooftop AC units.  The voltages and currents are 
similar, if not more severe.  I don't believe you could or should run 
power to a rooftop AC unit in cable tray.  Conduit is a tried and true 
practice and I recommend it.


William Miller


At 06:01 PM 3/25/2013, you wrote:

Ouch. I promise I'm not advocating for anything like that. What I may be 
missing is the Code reference that says "no cable tray on roofs" or similar.


There is so much room for improvement in wire management practices, that 
being able to use cable tray seems like a step forward. I understand some 
jurisdictions do not allow it, but it appears as though Code changes were 
made specifically to address this. It's boring stuff, but you can read the 
explanation of the Code changes in the ROP and ROC documents.


The Code changes a lot with regards to PV system, and Article 690 is more 
fluid than other articles. Some of this is the Code trying to keep up with 
technology. In other cases the Code evolves based on new applications for 
existing products. Often it changes because some areas of the Code are 
confusing for electricians and inspectors alike. If the new Code language 
is more clear in its intent than previous versions, some inspectors are 
willing to let installers build to the most current standard.


That's all I'm advocating for: Trying to understand how the minimum 
requirements outlined in Code evolve over time so that you can have a 
friendly and informed conversation with your AHJ over a donut.





On Mar 25, 2013, at 6:26 PM, William Miller wrote:


David:

This is great news.  Now, whenever I want to do something that is 
prohibited by code, I can just say that the Code Making Panel is gonna 
correct that pesky code section (insert your problem citation here) any 
day now, so I might as well be allowed to do whatever it was I was fixin' 
to do anyway.  Unless I am missing something...


Thanks!

William Miller

PS:  Just kidding.  Hope no offense is taken.

wm


At 03:46 PM 3/25/2013, you wrote:


So if you ever get called on 392.10(B)(2), I think you can point out that 
the Code Making Panels have been busy clarifying that cable tray is okay 
for source circuit conductors. Unless I'm missing something

___
List sponsored by 

[RE-wrenches] Sparq Micro-Inverters

2013-03-26 Thread Benn Kilburn - DayStar Renewable Energy
Hey Wrenches,
Do any of you have any experience with Sparq micro-inverters?  SPARQ Systems
Inc. 
Any feedback?

I have installed one system so far using them, but the (new construction)
home will not have internet access for several months, so remote monitoring
is not possible yet. I know of at least one other in the area.
They are very much like the M190 in appearance and interconnection method
(daisy-chain) but I'm told that the next generation will likely be much
smaller in size.

The technology they are using is resonant conversion (I hope I got that
right), which as I understand makes the units themselves more "software"
rather than "hardware" This also eliminates some of the failure prone
components of a typical inverter, so they are confidant coming out of the
gate with a 25yr warranty.  Pretty bold for a newer company/product, but
they are pretty confidant with their technology and everyone has to start
somewhereŠ

Benn

DayStar Renewable Energy Inc.
www.daystarsolar.ca
780-906-7807 
Construction Electrician Solar PV Systems Certified
Certificate # 0007S
HAVE A SUNNY DAY


___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] P1 micro performance

2013-03-26 Thread Carl Emerson
Friends,

 

Keeping the record straight.

 

I need to say that I have had correspondence 'off list' from a development
engineer from a prominent manufacturer who assures me that his product is
designed to run 'flat out' 24/7. 

 

The unit in fact is just coasting at it's maximum power rating. 

 

This allows for a projected life matching that of the PV.

 

In this case power clipping will not shorten the products life.

 

I am unable to confirm if all manufacturers are taking this approach, buyer
beware.

 

Regards
Carl Emerson

 

Nick,

 

Is Enphase going to be introducing to market any time in the near-term a new
micro with a higher output?  It seems very likely that the trend toward
higher output mods will continue.  The M215 will surely be left behind to a
greater degree as this trend continues if there are higher and reliable and
comparably priced, on a dollar/watt basis, micros available.

 

Thanks,

marco

 

Hi Carl, Marco, and Wrenches,

As a longtime installer, I understand your point of view.  Historically, I
designed my string and microinverter systems with the same consideration for
maintaining conservative DC to AC ratios.  That being said, the costs of
modules have decreased significantly and the dynamics have changed.  Solar
companies should be focused on selling systems that offers a great rate of
return.  Maximizing the customer's investment is most important.  Isn't that
what your customer wants?

What Enphase is encouraging is the development of cost effective PV systems
that will generate a healthy return.  Considering that the modules are only
20% of the total system costs today, it is smart to give up 0.2% or more of
the module production to lower the overall system costs by 5-10%.  The NEC
requires that the AC panel boards, conductors, and circuit breakers are
sized to the inverter continuous output current rating.  We should be
maximizing this infrastructure.

 

The data available indicates that when a system is installed with a 1.2 to
1.25 DC to AC ratio, it will rarely operate at peak output.  Installing a PV
system with a 1.25 DC to AC ratio is not driving the equipment to the
maximum.  In the case of the Enphase M215s; they are designed to operate
continuously at peak output, so reaching that level a few hours in the first
years is not problematic.  To be clear, this limiting will occur the most
during the spring months, because you have a combination of both cool
weather and high irradiance levels.

As Dan mentioned, this applies to string inverters as well as
microinverters.  One of the most common system designs of the early US
grid-tied market was installing 18- 165 watt modules on an SWR-2500.  I
designed hundreds of projects like that.  That was a ~1.2 multiplier, and
was at a time when the modules cost $5 per watt; not $1 per watt.  Why be
more conservative now?

  

 
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Cable tray

2013-03-26 Thread Glenn Burt
In a world where PV wire may be substituted for USE-2, but USE-2 cannot be
substituted for PV wire, and (future) 690 wording that only refers to PV
wire, there is still question in my mind about proper (future) use in cable
trays when 690 over rules 392, as it does in so many other matters.

 

The devil is in the details. 

 

 

From: David Brearley [mailto:david.brear...@solarprofessional.com] 
Sent: Tuesday, March 26, 2013 12:51 PM
To: glenn.b...@glbcc.com; RE-wrenches
Subject: Re: [RE-wrenches] Cable tray

 

Not at all. Type USE cable was added to the Permitted Uses of Cable Tray, as
outlined in Section 392.10(A) and the the companion Table 392.10(A).

 

On Mar 26, 2013, at 10:02 AM, Glenn Burt wrote:





Bill,

 

Does this mean that USE-2 is not acceptable for use in this manner?

Also, what is your confidence level that this will make it to the printer? I
recall a few other instances of proposed amendments that at the last minute
were not included in the past few code cycles (pertaining to PV).

 

Too bad we are still on the 2008 code cycle here.

 

Thanks

Glenn Burt

 

From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Bill Brooks
Sent: Monday, March 25, 2013 10:54 PM
To: 'RE-wrenches'
Subject: Re: [RE-wrenches] Cable tray

 

All,

 

Here is the language that has been accepted into the 2014 NEC:

 

690.31(C)(2)

 

(2) Cable Trays. PV source circuits and PV output circuits using
single-conductor cable listed and labeled as Photovoltaic (PV) wire of all
sizes with or without a Cable Tray marking/rating shall be permitted in
cable trays installed in outdoor locations provided the cables are supported
at intervals not to exceed 30cm (12 in.) and secured at intervals not to
exceed 1.4m (4.5').

 

I hope this helps. It is a very big deal.

 

Bill.

 

 

 

From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of David
Brearley
Sent: Monday, March 25, 2013 6:01 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] Cable tray

 

Ouch. I promise I'm not advocating for anything like that. What I may be
missing is the Code reference that says "no cable tray on roofs" or similar.


 

There is so much room for improvement in wire management practices, that
being able to use cable tray seems like a step forward. I understand some
jurisdictions do not allow it, but it appears as though Code changes were
made specifically to address this. It's boring stuff, but you can read the
explanation of the Code changes in the ROP and ROC documents. 

 

The Code changes a lot with regards to PV system, and Article 690 is more
fluid than other articles. Some of this is the Code trying to keep up with
technology. In other cases the Code evolves based on new applications for
existing products. Often it changes because some areas of the Code are
confusing for electricians and inspectors alike. If the new Code language is
more clear in its intent than previous versions, some inspectors are willing
to let installers build to the most current standard.

 

That's all I'm advocating for: Trying to understand how the minimum
requirements outlined in Code evolve over time so that you can have a
friendly and informed conversation with your AHJ over a donut. 

 

 

 

 

On Mar 25, 2013, at 6:26 PM, William Miller wrote:

 

David:

This is great news.  Now, whenever I want to do something that is prohibited
by code, I can just say that the Code Making Panel is gonna correct that
pesky code section (insert your problem citation here) any day now, so I
might as well be allowed to do whatever it was I was fixin' to do anyway.
Unless I am missing something...

Thanks!

William Miller

PS:  Just kidding.  Hope no offense is taken.

wm


At 03:46 PM 3/25/2013, you wrote:




So if you ever get called on 392.10(B)(2), I think you can point out that
the Code Making Panels have been busy clarifying that cable tray is okay for
source circuit conductors. Unless I'm missing something

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

 

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

 

___
List sponsored by Home P

Re: [RE-wrenches] Cable tray

2013-03-26 Thread Chris Mason
I don't understand how it can be permissible to string the PV wire over the
rails, under the modules, and in the rail channels, but not permissible to
put it in purpose made cable trays. Makes no sense.
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



[RE-wrenches] P1 micro performance

2013-03-26 Thread Marco Mangelsdorf
Nick,

 

Is Enphase going to be introducing to market any time in the near-term a new
micro with a higher output?  It seems very likely that the trend toward
higher output mods will continue.  The M215 will surely be left behind to a
greater degree as this trend continues if there are higher and reliable and
comparably priced, on a dollar/watt basis, micros available.

 

Thanks,

marco

 

Hi Carl, Marco, and Wrenches,

As a longtime installer, I understand your point of view.  Historically, I
designed my string and microinverter systems with the same consideration for
maintaining conservative DC to AC ratios.  That being said, the costs of
modules have decreased significantly and the dynamics have changed.  Solar
companies should be focused on selling systems that offers a great rate of
return.  Maximizing the customer's investment is most important.  Isn't that
what your customer wants?

What Enphase is encouraging is the development of cost effective PV systems
that will generate a healthy return.  Considering that the modules are only
20% of the total system costs today, it is smart to give up 0.2% or more of
the module production to lower the overall system costs by 5-10%.  The NEC
requires that the AC panel boards, conductors, and circuit breakers are
sized to the inverter continuous output current rating.  We should be
maximizing this infrastructure.

 

The data available indicates that when a system is installed with a 1.2 to
1.25 DC to AC ratio, it will rarely operate at peak output.  Installing a PV
system with a 1.25 DC to AC ratio is not driving the equipment to the
maximum.  In the case of the Enphase M215s; they are designed to operate
continuously at peak output, so reaching that level a few hours in the first
years is not problematic.  To be clear, this limiting will occur the most
during the spring months, because you have a combination of both cool
weather and high irradiance levels.

As Dan mentioned, this applies to string inverters as well as
microinverters.  One of the most common system designs of the early US
grid-tied market was installing 18- 165 watt modules on an SWR-2500.  I
designed hundreds of projects like that.  That was a ~1.2 multiplier, and
was at a time when the modules cost $5 per watt; not $1 per watt.  Why be
more conservative now?

  

 
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Cable tray

2013-03-26 Thread David Brearley
Not at all. Type USE cable was added to the Permitted Uses of Cable Tray, as 
outlined in Section 392.10(A) and the the companion Table 392.10(A).

On Mar 26, 2013, at 10:02 AM, Glenn Burt wrote:

> Bill,
>  
> Does this mean that USE-2 is not acceptable for use in this manner?
> Also, what is your confidence level that this will make it to the printer? I 
> recall a few other instances of proposed amendments that at the last minute 
> were not included in the past few code cycles (pertaining to PV).
>  
> Too bad we are still on the 2008 code cycle here…
>  
> Thanks
> Glenn Burt
>  
> From: re-wrenches-boun...@lists.re-wrenches.org 
> [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Bill Brooks
> Sent: Monday, March 25, 2013 10:54 PM
> To: 'RE-wrenches'
> Subject: Re: [RE-wrenches] Cable tray
>  
> All,
>  
> Here is the language that has been accepted into the 2014 NEC:
>  
> 690.31(C)(2)
>  
> (2) Cable Trays. PV source circuits and PV output circuits using 
> single-conductor cable listed and labeled as Photovoltaic (PV) wire of all 
> sizes with or without a Cable Tray marking/rating shall be permitted in cable 
> trays installed in outdoor locations provided the cables are supported at 
> intervals not to exceed 30cm (12 in.) and secured at intervals not to exceed 
> 1.4m (4.5’).
>  
> I hope this helps. It is a very big deal.
>  
> Bill.
>  
>  
>  
> From: re-wrenches-boun...@lists.re-wrenches.org 
> [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of David Brearley
> Sent: Monday, March 25, 2013 6:01 PM
> To: RE-wrenches
> Subject: Re: [RE-wrenches] Cable tray
>  
> Ouch. I promise I'm not advocating for anything like that. What I may be 
> missing is the Code reference that says "no cable tray on roofs" or similar. 
>  
> There is so much room for improvement in wire management practices, that 
> being able to use cable tray seems like a step forward. I understand some 
> jurisdictions do not allow it, but it appears as though Code changes were 
> made specifically to address this. It's boring stuff, but you can read the 
> explanation of the Code changes in the ROP and ROC documents. 
>  
> The Code changes a lot with regards to PV system, and Article 690 is more 
> fluid than other articles. Some of this is the Code trying to keep up with 
> technology. In other cases the Code evolves based on new applications for 
> existing products. Often it changes because some areas of the Code are 
> confusing for electricians and inspectors alike. If the new Code language is 
> more clear in its intent than previous versions, some inspectors are willing 
> to let installers build to the most current standard.
>  
> That's all I'm advocating for: Trying to understand how the minimum 
> requirements outlined in Code evolve over time so that you can have a 
> friendly and informed conversation with your AHJ over a donut. 
>  
>  
>  
>  
> On Mar 25, 2013, at 6:26 PM, William Miller wrote:
>  
> 
> David:
> 
> This is great news.  Now, whenever I want to do something that is prohibited 
> by code, I can just say that the Code Making Panel is gonna correct that 
> pesky code section (insert your problem citation here) any day now, so I 
> might as well be allowed to do whatever it was I was fixin' to do anyway.  
> Unless I am missing something...
> 
> Thanks!
> 
> William Miller
> 
> PS:  Just kidding.  Hope no offense is taken.
> 
> wm
> 
> 
> At 03:46 PM 3/25/2013, you wrote:
> 
> 
> So if you ever get called on 392.10(B)(2), I think you can point out that the 
> Code Making Panels have been busy clarifying that cable tray is okay for 
> source circuit conductors. Unless I'm missing something
> ___
> List sponsored by Home Power magazine
> 
> List Address: RE-wrenches@lists.re-wrenches.org
> 
> Change email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: 
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out participant bios:
> www.members.re-wrenches.org
> 
>  
> ___
> List sponsored by Home Power magazine
> 
> List Address: RE-wrenches@lists.re-wrenches.org
> 
> Change email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: 
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out participant bios:
> www.members.re-wrenches.org
> 

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenc

Re: [RE-wrenches] AFCI

2013-03-26 Thread Bill Brooks
Wrenches,


Fronius is releasing their AFCI inverters this month. They sent them to me
for CEC approval.

 

Bill.

 

From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Nathan
Stumpff
Sent: Tuesday, March 26, 2013 9:09 AM
To: re-wrenches@lists.re-wrenches.org
Subject: [RE-wrenches] AFCI

 

Wrenches,

 

Are there other string inverters currently in production and available with
working AFCI besides SMA? It seems like I would have gotten a hundred emails
if there was, but maybe some company with a little smaller profile?

 

Nothing against SMA of course, but their relatively narrow operating voltage
window makes design tough in many cases in my climate.

 

Many thanks,

-Nathan

 

--

Nathan J. Stumpff

NABCEP Certified PV Installer #091209-175

NABCEP Certified Solar Heating Installer #032412-14

Project Manager | Arctic Sun, LLC

nat...@arcticsun-llc.com    | (907)
457-1297

www.reina-llc.com | www.arcticsun-llc.com  

  Description: ZA102637861

 

<>___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



[RE-wrenches] AFCI

2013-03-26 Thread Nathan Stumpff
Wrenches,

Are there other string inverters currently in production and available with 
working AFCI besides SMA? It seems like I would have gotten a hundred emails if 
there was, but maybe some company with a little smaller profile?

Nothing against SMA of course, but their relatively narrow operating voltage 
window makes design tough in many cases in my climate...

Many thanks,
-Nathan

--
Nathan J. Stumpff
NABCEP Certified PV Installer #091209-175
NABCEP Certified Solar Heating Installer #032412-14
Project Manager | Arctic Sun, LLC
nat...@arcticsun-llc.com   | (907) 457-1297
www.reina-llc.com | 
www.arcticsun-llc.com
[cid:image001.png@01CE29F8.57138B90]

<>___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] GSCM-mini with Honda EM5000SX

2013-03-26 Thread SunHarvest
Thanks all for the comments. I did not install the batteries, genny, Outback 
inverter, or Mate, just the GSCM and an RTS. I've given the homeowner a lot of 
advice along the way but did not touch the other installer's work. It was clear 
from the beginning that the homeowner knows nothing about off-grid power 
generation or battery maintenance and that the previous installer didn't bother 
with code compliance or educating the homeowner on how to operate his own 
system. Yes, it's one of those. I'm trying to keep my distance while still 
being available to answer questions. Thanks again guys!

Eric Stikes
SunHarvest

- Original Message - 
  From: William Miller 
  To: RE-wrenches 
  Sent: Monday, March 25, 2013 12:41 PM
  Subject: Re: [RE-wrenches] GSCM-mini with Honda EM5000SX


  Eric:

  The generator-based charging may impose higher currents into the batteries 
than either PV charging or inverter consumption, triggering the problem.  

  Melted battery terminals are not uncommon.  You must have washers under your 
bolt heads with lead flanges.  Otherwise the bolt heads sink into the lead, 
loosening connections.  All mating surfaces need to be newly wired brushed just 
before assembly.  Battery connections need to be re-torqued annually.

  William Miller

  At 09:40 AM 3/25/2013, you wrote:

Larry,
 
Thanks for your reply. For some reason the schematic I received from the 
tech at Atkinson did not show any wires being connected to pins 9 & 10 and as 
I'm a literalist I did not make those connections. After I received your (and 
other) feedback I connected gen power to those pins and the AGS seemed to 
function fine. Within 2 days the customer called me back saying his genny was 
shutting off after 20 mins of runtime. I told him to disconnect or reprogram 
one system component at a time to find the fault source. Before a fault source 
was determined, he observed that two batteries in his bank were experiencing 
the "battery terminals melting into the battery casing" (as was texted to me by 
the customer). I have no idea how a GSCM interface would cause or allow an 
overcurrent fault at the batteries but the timing of the installation seems to 
indicate that the AGS is at fault. Ever heard of this before?
 
Eric Stikes
SunHarvest Solar
 

We install solar pool pumps quite frequently here in the Caribbean. We 
use Sunpumps - excellent company, great support. Email Joe Lines 
j...@sunpumps.com for design assistance, he is very helpful.


On Wed, Feb 20, 2013 at 1:02 PM, William Korthof  
wrote:

  A few questions. 

  I have a customer who really wants a solar-direct pool pump for his 
home. Medium size in-ground pool and I'd like the pump to be strong enough to 
lift to the solar pool panels (12 ft lift above pool level). I'd like to offer 
him hardware that is at least one notch above experimental beta-test. I 
remember the SunCentric from several years ago, but not sure how durable that 
turned out, and I was having trouble a vendor for it now. Any suggestions for 
today with some favorable track record? Or suggestions on what to avoid? 

  William Korthof
  Sustainable Solutions Partners


  ___
  List sponsored by Home Power magazine

  List Address: RE-wrenches@lists.re-wrenches.org

  Options & settings:
  http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

  List-Archive: 
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

  List rules & etiquette:
  www.re-wrenches.org/etiquette.htm

  Check out participant bios:
  www.members.re-wrenches.org





-- 
Chris Mason 
President, Comet Systems Ltd
www.cometenergysystems.com
Cell: 264.235.5670
Skype: netconcepts




___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

  ___
  List sponsored by Home Power magazine

  List Address: RE-wrenches@lists.re-wrenches.org

  Change email address & settings:
  http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

  List-Archive: 
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

  List rules & etiquette:
  www.re-wrenches.org/etiquette.htm

  Check out participant bios:
  www.members.re-wrenches.

Re: [RE-wrenches] Cable tray

2013-03-26 Thread Glenn Burt
Bill,

 

Does this mean that USE-2 is not acceptable for use in this manner?

Also, what is your confidence level that this will make it to the printer? I
recall a few other instances of proposed amendments that at the last minute
were not included in the past few code cycles (pertaining to PV).

 

Too bad we are still on the 2008 code cycle here.

 

Thanks

Glenn Burt

 

From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Bill Brooks
Sent: Monday, March 25, 2013 10:54 PM
To: 'RE-wrenches'
Subject: Re: [RE-wrenches] Cable tray

 

All,

 

Here is the language that has been accepted into the 2014 NEC:

 

690.31(C)(2)

 

(2) Cable Trays. PV source circuits and PV output circuits using
single-conductor cable listed and labeled as Photovoltaic (PV) wire of all
sizes with or without a Cable Tray marking/rating shall be permitted in
cable trays installed in outdoor locations provided the cables are supported
at intervals not to exceed 30cm (12 in.) and secured at intervals not to
exceed 1.4m (4.5').

 

I hope this helps. It is a very big deal.

 

Bill.

 

 

 

From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of David
Brearley
Sent: Monday, March 25, 2013 6:01 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] Cable tray

 

Ouch. I promise I'm not advocating for anything like that. What I may be
missing is the Code reference that says "no cable tray on roofs" or similar.


 

There is so much room for improvement in wire management practices, that
being able to use cable tray seems like a step forward. I understand some
jurisdictions do not allow it, but it appears as though Code changes were
made specifically to address this. It's boring stuff, but you can read the
explanation of the Code changes in the ROP and ROC documents. 

 

The Code changes a lot with regards to PV system, and Article 690 is more
fluid than other articles. Some of this is the Code trying to keep up with
technology. In other cases the Code evolves based on new applications for
existing products. Often it changes because some areas of the Code are
confusing for electricians and inspectors alike. If the new Code language is
more clear in its intent than previous versions, some inspectors are willing
to let installers build to the most current standard.

 

That's all I'm advocating for: Trying to understand how the minimum
requirements outlined in Code evolve over time so that you can have a
friendly and informed conversation with your AHJ over a donut. 

 

 

 

 

On Mar 25, 2013, at 6:26 PM, William Miller wrote:

 

David:

This is great news.  Now, whenever I want to do something that is prohibited
by code, I can just say that the Code Making Panel is gonna correct that
pesky code section (insert your problem citation here) any day now, so I
might as well be allowed to do whatever it was I was fixin' to do anyway.
Unless I am missing something...

Thanks!

William Miller

PS:  Just kidding.  Hope no offense is taken.

wm


At 03:46 PM 3/25/2013, you wrote:



So if you ever get called on 392.10(B)(2), I think you can point out that
the Code Making Panels have been busy clarifying that cable tray is okay for
source circuit conductors. Unless I'm missing something

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

 

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



[RE-wrenches] Remote SW control

2013-03-26 Thread Hilton Dier III
A friend of mine has an old Xantrex SW 4024 installed in a 
less-than-accessible location. He's looking for one of their remote 
control and monitoring panels. If you have one of these kicking around, 
or know of one, please contact me off line.


Many thanks,

Hilton

--
Hilton Dier III
Renewable Energy Design
Partner, Solar Gain LLC
453 East Hill Rd.
Middlesex, VT 05602

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Cable tray

2013-03-26 Thread Mark Richardson
Bill,
Thank you for continuing to help adopt more practical and 'user friendly' code1 
requirements.
As Glen pointed out, [NEC 2011] 392.10(B)(1)(a) could pose a problem for some 
AHJ's - even though 690.31(B) allows PV wire in exposed outdoor locations 
(presumably not in "cable tray").
It is truly counter-intuitive that by efforting responsible wire-management and 
installing PV wire in "cable tray" it would somehow create a code violation 
unless it was at least 1/0, and that it would somehow be allowed in a 
residential application under the same 392.10? It is also interesting to note 
the definition of Supervised Industrial Installation2  in 240.2 and that all of 
those conditions are not met in most cases
Just wanted to say again: Thanks for the forward progress!
Mark

1 - I know, I know: "user-friendly code" is an oxymoron J
2 - I could not find a referenced definition of Industrial Establishments

[NYLE LOGO SMALL]
Mark Richardson
mrichard...@newyorklightenergy.com

From: re-wrenches-boun...@lists.re-wrenches.org 
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Bill Brooks
Sent: Monday, March 25, 2013 10:54 PM
To: 'RE-wrenches'
Subject: Re: [RE-wrenches] Cable tray

All,

Here is the language that has been accepted into the 2014 NEC:

690.31(C)(2)

(2) Cable Trays. PV source circuits and PV output circuits using 
single-conductor cable listed and labeled as Photovoltaic (PV) wire of all 
sizes with or without a Cable Tray marking/rating shall be permitted in cable 
trays installed in outdoor locations provided the cables are supported at 
intervals not to exceed 30cm (12 in.) and secured at intervals not to exceed 
1.4m (4.5').

I hope this helps. It is a very big deal.

Bill.



From: 
re-wrenches-boun...@lists.re-wrenches.org
 [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of David Brearley
Sent: Monday, March 25, 2013 6:01 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] Cable tray

Ouch. I promise I'm not advocating for anything like that. What I may be 
missing is the Code reference that says "no cable tray on roofs" or similar.

There is so much room for improvement in wire management practices, that being 
able to use cable tray seems like a step forward. I understand some 
jurisdictions do not allow it, but it appears as though Code changes were made 
specifically to address this. It's boring stuff, but you can read the 
explanation of the Code changes in the ROP and ROC documents.

The Code changes a lot with regards to PV system, and Article 690 is more fluid 
than other articles. Some of this is the Code trying to keep up with 
technology. In other cases the Code evolves based on new applications for 
existing products. Often it changes because some areas of the Code are 
confusing for electricians and inspectors alike. If the new Code language is 
more clear in its intent than previous versions, some inspectors are willing to 
let installers build to the most current standard.

That's all I'm advocating for: Trying to understand how the minimum 
requirements outlined in Code evolve over time so that you can have a friendly 
and informed conversation with your AHJ over a donut.




On Mar 25, 2013, at 6:26 PM, William Miller wrote:

David:

This is great news.  Now, whenever I want to do something that is prohibited by 
code, I can just say that the Code Making Panel is gonna correct that pesky 
code section (insert your problem citation here) any day now, so I might as 
well be allowed to do whatever it was I was fixin' to do anyway.  Unless I am 
missing something...

Thanks!

William Miller

PS:  Just kidding.  Hope no offense is taken.

wm


At 03:46 PM 3/25/2013, you wrote:

So if you ever get called on 392.10(B)(2), I think you can point out that the 
Code Making Panels have been busy clarifying that cable tray is okay for source 
circuit conductors. Unless I'm missing something
___
List sponsored by Home Power magazine

List Address: 
RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

<>___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org