I live in a TVA area where there is a Feed In Tariff.  Everything that is
generated by the PV array feeds into the grid through a Generation Meter
that ties-in ahead of the house meter.  I have started getting calls from
customers who hate having a solar array that does not generate when the
grid is down but the sun is shining, but who also want to get the $.12
premium when the grid is connected.  We have lots of systems with SMA
Sunnyboy inverters, but more with Enphase micro-inverters.  Rather than
trying to reinvent the wheel, what you found to be the best solution for
this type of installation?



W.C. (Bill) Turberville P.E.

President



ECE Solar

Electrical Contracting Enterprises LLC

3080 Stage Post Road Suite 107

Bartlett, TN 38133



901-348-9230 ext 101 phone

901-348-2192 fax

901-289-6346 cell

billt...@ece-llc.com



NABCEP Certified PV Installation Professional 032611-320
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Battery Back-up and Grid Tie

2013-04-26 Thread Jay Peltz
Hi bill

Just how often is your grid down?

Jay
Peltz power

Sent from my iPhone

On Apr 26, 2013, at 10:01 AM, Bill Turberville billt...@ece-llc.com wrote:

 I live in a TVA area where there is a Feed In Tariff.  Everything that is 
 generated by the PV array feeds into the grid through a Generation Meter that 
 ties-in ahead of the house meter.  I have started getting calls from 
 customers who hate having a solar array that does not generate when the grid 
 is down but the sun is shining, but who also want to get the $.12 premium 
 when the grid is connected.  We have lots of systems with SMA Sunnyboy 
 inverters, but more with Enphase micro-inverters.  Rather than trying to 
 reinvent the wheel, what you found to be the best solution for this type of 
 installation?
  
 W.C. (Bill) Turberville P.E.
 President
  
 ECE Solar
 Electrical Contracting Enterprises LLC
 3080 Stage Post Road Suite 107
 Bartlett, TN 38133
  
 901-348-9230 ext 101 phone
 901-348-2192 fax
 901-289-6346 cell
 billt...@ece-llc.com
  
 NABCEP Certified PV Installation Professional 032611-320
  
  
 ___
 List sponsored by Home Power magazine
 
 List Address: RE-wrenches@lists.re-wrenches.org
 
 Change email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
 List-Archive: 
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
 
 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm
 
 Check out participant bios:
 www.members.re-wrenches.org
 
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Battery Back-up and Grid Tie

2013-04-26 Thread Bill Turberville
Not very often, and usually for no more than an hour or two, although it
has been down as long as 5 days, either during tornado season, or ice
taking down power lines.  What these people are looking for is Just In Case
a big event happens.  They do not want to have all those panels just
sitting there.



*From:* re-wrenches-boun...@lists.re-wrenches.org [mailto:
re-wrenches-boun...@lists.re-wrenches.org] *On Behalf Of *Jay Peltz
*Sent:* Friday, April 26, 2013 12:25 PM
*To:* RE-wrenches
*Subject:* Re: [RE-wrenches] Battery Back-up and Grid Tie



Hi bill



Just how often is your grid down?



Jay

Peltz power

Sent from my iPhone


On Apr 26, 2013, at 10:01 AM, Bill Turberville billt...@ece-llc.com wrote:

I live in a TVA area where there is a Feed In Tariff.  Everything that is
generated by the PV array feeds into the grid through a Generation Meter
that ties-in ahead of the house meter.  I have started getting calls from
customers who hate having a solar array that does not generate when the
grid is down but the sun is shining, but who also want to get the $.12
premium when the grid is connected.  We have lots of systems with SMA
Sunnyboy inverters, but more with Enphase micro-inverters.  Rather than
trying to reinvent the wheel, what you found to be the best solution for
this type of installation?



W.C. (Bill) Turberville P.E.

President



ECE Solar

Electrical Contracting Enterprises LLC

3080 Stage Post Road Suite 107

Bartlett, TN 38133



901-348-9230 ext 101 phone

901-348-2192 fax

901-289-6346 cell

billt...@ece-llc.com



NABCEP Certified PV Installation Professional 032611-320





___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Battery Back-up and Grid Tie

2013-04-26 Thread Chris Mason
For the price that you would spend on batteries and a Sunny Island system,
you could buy and install a generator. I would go that route.


On Fri, Apr 26, 2013 at 1:33 PM, Bill Turberville billt...@ece-llc.comwrote:

 Not very often, and usually for no more than an hour or two, although it
 has been down as long as 5 days, either during tornado season, or ice
 taking down power lines.  What these people are looking for is Just In Case
 a big event happens.  They do not want to have all those panels just
 sitting there.



 *From:* re-wrenches-boun...@lists.re-wrenches.org [mailto:
 re-wrenches-boun...@lists.re-wrenches.org] *On Behalf Of *Jay Peltz
 *Sent:* Friday, April 26, 2013 12:25 PM
 *To:* RE-wrenches
 *Subject:* Re: [RE-wrenches] Battery Back-up and Grid Tie



 Hi bill



 Just how often is your grid down?



 Jay

 Peltz power

 Sent from my iPhone


 On Apr 26, 2013, at 10:01 AM, Bill Turberville billt...@ece-llc.com
 wrote:

 I live in a TVA area where there is a Feed In Tariff.  Everything that is
 generated by the PV array feeds into the grid through a Generation Meter
 that ties-in ahead of the house meter.  I have started getting calls from
 customers who hate having a solar array that does not generate when the
 grid is down but the sun is shining, but who also want to get the $.12
 premium when the grid is connected.  We have lots of systems with SMA
 Sunnyboy inverters, but more with Enphase micro-inverters.  Rather than
 trying to reinvent the wheel, what you found to be the best solution for
 this type of installation?



 W.C. (Bill) Turberville P.E.

 President



 ECE Solar

 Electrical Contracting Enterprises LLC

 3080 Stage Post Road Suite 107

 Bartlett, TN 38133



 901-348-9230 ext 101 phone

 901-348-2192 fax

 901-289-6346 cell

 billt...@ece-llc.com



 NABCEP Certified PV Installation Professional 032611-320





 ___
 List sponsored by Home Power magazine

 List Address: RE-wrenches@lists.re-wrenches.org

 Change email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

 List-Archive:
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm

 Check out participant bios:
 www.members.re-wrenches.org


 ___
 List sponsored by Home Power magazine

 List Address: RE-wrenches@lists.re-wrenches.org

 Change email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

 List-Archive:
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm

 Check out participant bios:
 www.members.re-wrenches.org





-- 
Chris Mason
President, Comet Systems Ltd
www.cometenergysystems.com
Cell: 264.235.5670
Skype: netconcepts
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Battery Back-up and Grid Tie

2013-04-26 Thread Bill Turberville
I have done that with several customers, but those generators were natural
gas, and their concern is if we have an earth quake and lose natural gas,
since we are on the New Madrid fault.



*From:* re-wrenches-boun...@lists.re-wrenches.org [mailto:
re-wrenches-boun...@lists.re-wrenches.org] *On Behalf Of *Chris Mason
*Sent:* Friday, April 26, 2013 1:36 PM
*To:* RE-wrenches
*Subject:* Re: [RE-wrenches] Battery Back-up and Grid Tie



For the price that you would spend on batteries and a Sunny Island system,
you could buy and install a generator. I would go that route.



On Fri, Apr 26, 2013 at 1:33 PM, Bill Turberville billt...@ece-llc.com
wrote:

Not very often, and usually for no more than an hour or two, although it
has been down as long as 5 days, either during tornado season, or ice
taking down power lines.  What these people are looking for is Just In Case
a big event happens.  They do not want to have all those panels just
sitting there.



*From:* re-wrenches-boun...@lists.re-wrenches.org [mailto:
re-wrenches-boun...@lists.re-wrenches.org] *On Behalf Of *Jay Peltz
*Sent:* Friday, April 26, 2013 12:25 PM
*To:* RE-wrenches
*Subject:* Re: [RE-wrenches] Battery Back-up and Grid Tie



Hi bill



Just how often is your grid down?



Jay

Peltz power

Sent from my iPhone


On Apr 26, 2013, at 10:01 AM, Bill Turberville billt...@ece-llc.com wrote:

I live in a TVA area where there is a Feed In Tariff.  Everything that is
generated by the PV array feeds into the grid through a Generation Meter
that ties-in ahead of the house meter.  I have started getting calls from
customers who hate having a solar array that does not generate when the
grid is down but the sun is shining, but who also want to get the $.12
premium when the grid is connected.  We have lots of systems with SMA
Sunnyboy inverters, but more with Enphase micro-inverters.  Rather than
trying to reinvent the wheel, what you found to be the best solution for
this type of installation?



W.C. (Bill) Turberville P.E.

President



ECE Solar

Electrical Contracting Enterprises LLC

3080 Stage Post Road Suite 107

Bartlett, TN 38133



901-348-9230 ext 101 phone

901-348-2192 fax

901-289-6346 cell

billt...@ece-llc.com



NABCEP Certified PV Installation Professional 032611-320





___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org


___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org





-- 
Chris Mason

President, Comet Systems Ltd

www.cometenergysystems.com

Cell: 264.235.5670

Skype: netconcepts
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Battery Back-up and Grid Tie

2013-04-26 Thread Chris Mason
The Generac Guardian are field convertible to propane. I imagine you can
install a propane tank as we do here.


On Fri, Apr 26, 2013 at 2:40 PM, Bill Turberville billt...@ece-llc.comwrote:

 I have done that with several customers, but those generators were natural
 gas, and their concern is if we have an earth quake and lose natural gas,
 since we are on the New Madrid fault.



 *From:* re-wrenches-boun...@lists.re-wrenches.org [mailto:
 re-wrenches-boun...@lists.re-wrenches.org] *On Behalf Of *Chris Mason
 *Sent:* Friday, April 26, 2013 1:36 PM

 *To:* RE-wrenches
 *Subject:* Re: [RE-wrenches] Battery Back-up and Grid Tie



 For the price that you would spend on batteries and a Sunny Island system,
 you could buy and install a generator. I would go that route.



 On Fri, Apr 26, 2013 at 1:33 PM, Bill Turberville billt...@ece-llc.com
 wrote:

 Not very often, and usually for no more than an hour or two, although it
 has been down as long as 5 days, either during tornado season, or ice
 taking down power lines.  What these people are looking for is Just In Case
 a big event happens.  They do not want to have all those panels just
 sitting there.



 *From:* re-wrenches-boun...@lists.re-wrenches.org [mailto:
 re-wrenches-boun...@lists.re-wrenches.org] *On Behalf Of *Jay Peltz
 *Sent:* Friday, April 26, 2013 12:25 PM
 *To:* RE-wrenches
 *Subject:* Re: [RE-wrenches] Battery Back-up and Grid Tie



 Hi bill



 Just how often is your grid down?



 Jay

 Peltz power

 Sent from my iPhone


 On Apr 26, 2013, at 10:01 AM, Bill Turberville billt...@ece-llc.com
 wrote:

 I live in a TVA area where there is a Feed In Tariff.  Everything that is
 generated by the PV array feeds into the grid through a Generation Meter
 that ties-in ahead of the house meter.  I have started getting calls from
 customers who hate having a solar array that does not generate when the
 grid is down but the sun is shining, but who also want to get the $.12
 premium when the grid is connected.  We have lots of systems with SMA
 Sunnyboy inverters, but more with Enphase micro-inverters.  Rather than
 trying to reinvent the wheel, what you found to be the best solution for
 this type of installation?



 W.C. (Bill) Turberville P.E.

 President



 ECE Solar

 Electrical Contracting Enterprises LLC

 3080 Stage Post Road Suite 107

 Bartlett, TN 38133



 901-348-9230 ext 101 phone

 901-348-2192 fax

 901-289-6346 cell

 billt...@ece-llc.com



 NABCEP Certified PV Installation Professional 032611-320





 ___
 List sponsored by Home Power magazine

 List Address: RE-wrenches@lists.re-wrenches.org

 Change email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

 List-Archive:
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm

 Check out participant bios:
 www.members.re-wrenches.org


 ___
 List sponsored by Home Power magazine

 List Address: RE-wrenches@lists.re-wrenches.org

 Change email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

 List-Archive:
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm

 Check out participant bios:
 www.members.re-wrenches.org





 --
 Chris Mason

 President, Comet Systems Ltd

 www.cometenergysystems.com

 Cell: 264.235.5670

 Skype: netconcepts

 ___
 List sponsored by Home Power magazine

 List Address: RE-wrenches@lists.re-wrenches.org

 Change email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

 List-Archive:
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm

 Check out participant bios:
 www.members.re-wrenches.org





-- 
Chris Mason
President, Comet Systems Ltd
www.cometenergysystems.com
Cell: 264.235.5670
Skype: netconcepts
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Battery Back-up and Grid Tie

2013-04-26 Thread toddcory

our power outages generally come from bad weather too... and of course when the 
weather is bad the pv does next to nothing. so for emergency backup, i 
recommend a generator.
 
todd
 
 
 
 
 
On Friday, April 26, 2013 10:33am, Bill Turberville billt...@ece-llc.com 
said:




Not very often, and usually for no more than an hour or two, although it has 
been down as long as 5 days, either during tornado season, or ice taking down 
power lines.  What these people are looking for is Just In Case a big event 
happens.  They do not want to have all those panels just sitting there.
 


From: [mailto:re-wrenches-boun...@lists.re-wrenches.org] 
re-wrenches-boun...@lists.re-wrenches.org 
[mailto:[mailto:re-wrenches-boun...@lists.re-wrenches.org] 
re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Jay Peltz
Sent: Friday, April 26, 2013 12:25 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] Battery Back-up and Grid Tie
 

Hi bill

 

Just how often is your grid down?

 

Jay

Peltz power

Sent from my iPhone


On Apr 26, 2013, at 10:01 AM, Bill Turberville [mailto:billt...@ece-llc.com] 
billt...@ece-llc.com wrote:

I live in a TVA area where there is a Feed In Tariff.  Everything that is 
generated by the PV array feeds into the grid through a Generation Meter that 
ties-in ahead of the house meter.  I have started getting calls from customers 
who hate having a solar array that does not generate when the grid is down but 
the sun is shining, but who also want to get the $.12 premium when the grid is 
connected.  We have lots of systems with SMA Sunnyboy inverters, but more with 
Enphase micro-inverters.  Rather than trying to reinvent the wheel, what you 
found to be the best solution for this type of installation?
 
W.C. (Bill) Turberville P.E.
President
 
ECE Solar
Electrical Contracting Enterprises LLC
3080 Stage Post Road Suite 107
Bartlett, TN 38133
 
901-348-9230 ext 101 phone
901-348-2192 fax
901-289-6346 cell
[mailto:billt...@ece-llc.com] billt...@ece-llc.com
 
NABCEP Certified PV Installation Professional 032611-320
 
 

___
List sponsored by Home Power magazine

List Address: [mailto:RE-wrenches@lists.re-wrenches.org] 
RE-wrenches@lists.re-wrenches.org

Change email address  settings:
[http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org] 
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
[http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org] 
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
[http://www.re-wrenches.org/etiquette.htm] www.re-wrenches.org/etiquette.htm

Check out participant bios:
[http://www.members.re-wrenches.org] www.members.re-wrenches.org


Sent from Finest Planet WebMail.
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Battery Back-up and Grid Tie

2013-04-26 Thread SunHarvest
I have a crazy...I mean creative customer who wants a BB system so that he can 
run off-grid during peak and partial-peak rate hours: 1 to 7pm is peak, 7 to 
9pm is partial from PGE. He got this great idea from a tech at a reputable 
power optimizer manufacturer, whom I will not name here, who said, you've got 
the batteries just sitting there; why not put them to work?

Initially he wanted his PV to operate while the sun is shining and the grid is 
down...and his batteries to supply power when the sun and grid is down. But now 
he wants his back-up system to do it all. We've touched on all the obvious 
points: 

- Peak buying is also peak selling
- Physics and efficiency losses determine that the energy he saves will never 
equal the energy he can put back into his system.
- Decreased battery life due to increased cycling
- Costs for batts and special inverters versus generator

What is the definitive argument against BB in general and this peak shaving 
idea in particular?

Thanks pros.

Eric
SunHarvest

- Original Message - 
  From: toddc...@finestplanet.com 
  To: RE-wrenches 
  Sent: Friday, April 26, 2013 11:57 AM
  Subject: Re: [RE-wrenches] Battery Back-up and Grid Tie


  our power outages generally come from bad weather too... and of course when 
the weather is bad the pv does next to nothing. so for emergency backup, i 
recommend a generator.



  todd











  On Friday, April 26, 2013 10:33am, Bill Turberville billt...@ece-llc.com 
said:



  Not very often, and usually for no more than an hour or two, although it has 
been down as long as 5 days, either during tornado season, or ice taking down 
power lines.  What these people are looking for is Just In Case a big event 
happens.  They do not want to have all those panels just sitting there.


  From: re-wrenches-boun...@lists.re-wrenches.org 
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Jay Peltz
  Sent: Friday, April 26, 2013 12:25 PM
  To: RE-wrenches
  Subject: Re: [RE-wrenches] Battery Back-up and Grid Tie



  Hi bill



  Just how often is your grid down?



  Jay

  Peltz power

  Sent from my iPhone


  On Apr 26, 2013, at 10:01 AM, Bill Turberville billt...@ece-llc.com wrote:

I live in a TVA area where there is a Feed In Tariff.  Everything that is 
generated by the PV array feeds into the grid through a Generation Meter that 
ties-in ahead of the house meter.  I have started getting calls from customers 
who hate having a solar array that does not generate when the grid is down but 
the sun is shining, but who also want to get the $.12 premium when the grid is 
connected.  We have lots of systems with SMA Sunnyboy inverters, but more with 
Enphase micro-inverters.  Rather than trying to reinvent the wheel, what you 
found to be the best solution for this type of installation?



W.C. (Bill) Turberville P.E.

President



ECE Solar

Electrical Contracting Enterprises LLC

3080 Stage Post Road Suite 107

Bartlett, TN 38133



901-348-9230 ext 101 phone

901-348-2192 fax

901-289-6346 cell

billt...@ece-llc.com



NABCEP Certified PV Installation Professional 032611-320





___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org




  Sent from Finest Planet WebMail.



--


  ___
  List sponsored by Home Power magazine

  List Address: RE-wrenches@lists.re-wrenches.org

  Change email address  settings:
  http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

  List-Archive: 
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

  List rules  etiquette:
  www.re-wrenches.org/etiquette.htm

  Check out participant bios:
  www.members.re-wrenches.org

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Battery Back-up and Grid Tie

2013-04-26 Thread Bill Turberville
Batteries actually do better if they are cycled than if they just sit
there.  He may actually extend his battery life.  What kind of batteries is
he using?



*From:* re-wrenches-boun...@lists.re-wrenches.org [mailto:
re-wrenches-boun...@lists.re-wrenches.org] *On Behalf Of *SunHarvest
*Sent:* Friday, April 26, 2013 2:25 PM
*To:* RE-wrenches
*Subject:* Re: [RE-wrenches] Battery Back-up and Grid Tie



I have a crazy...I mean *creative* customer who wants a BB system so that
he can run off-grid during peak and partial-peak rate hours: 1 to 7pm is
peak, 7 to 9pm is partial from PGE. He got this great idea from a tech at
a reputable power optimizer manufacturer, whom I will not name here, who
said, you've got the batteries just sitting there; why not put them to
work?



Initially he wanted his PV to operate while the sun is shining and the grid
is down...and his batteries to supply power when the sun *and* grid is
down. But now he wants his back-up system to do it all. We've touched on
all the obvious points:



- Peak buying is also peak selling

- Physics and efficiency losses determine that the energy he saves will
never equal the energy he can put back into his system.

- Decreased battery life due to increased cycling

- Costs for batts and special inverters versus generator



What is the *definitive* argument against BB in general and this peak
shaving idea in particular?



Thanks pros.



Eric

SunHarvest



- Original Message -

*From:* toddc...@finestplanet.com

*To:* RE-wrenches re-wrenches@lists.re-wrenches.org

*Sent:* Friday, April 26, 2013 11:57 AM

*Subject:* Re: [RE-wrenches] Battery Back-up and Grid Tie



our power outages generally come from bad weather too... and of course when
the weather is bad the pv does next to nothing. so for emergency backup, i
recommend a generator.



todd











On Friday, April 26, 2013 10:33am, Bill Turberville billt...@ece-llc.com
said:

Not very often, and usually for no more than an hour or two, although it
has been down as long as 5 days, either during tornado season, or ice
taking down power lines.  What these people are looking for is Just In Case
a big event happens.  They do not want to have all those panels just
sitting there.

*From:* 
*re-wrenches-boun...@lists.re-wrenches.org*re-wrenches-boun...@lists.re-wrenches.org[mailto:
*re-wrenches-boun...@lists.re-wrenches.org*re-wrenches-boun...@lists.re-wrenches.org]
*On Behalf Of *Jay Peltz
*Sent:* Friday, April 26, 2013 12:25 PM
*To:* RE-wrenches
*Subject:* Re: [RE-wrenches] Battery Back-up and Grid Tie



Hi bill



Just how often is your grid down?



Jay

Peltz power

Sent from my iPhone


On Apr 26, 2013, at 10:01 AM, Bill Turberville
*billt...@ece-llc.com*billt...@ece-llc.com
wrote:

I live in a TVA area where there is a Feed In Tariff.  Everything that is
generated by the PV array feeds into the grid through a Generation Meter
that ties-in ahead of the house meter.  I have started getting calls from
customers who hate having a solar array that does not generate when the
grid is down but the sun is shining, but who also want to get the $.12
premium when the grid is connected.  We have lots of systems with SMA
Sunnyboy inverters, but more with Enphase micro-inverters.  Rather than
trying to reinvent the wheel, what you found to be the best solution for
this type of installation?



W.C. (Bill) Turberville P.E.

President



ECE Solar

Electrical Contracting Enterprises LLC

3080 Stage Post Road Suite 107

Bartlett, TN 38133



901-348-9230 ext 101 phone

901-348-2192 fax

901-289-6346 cell

*billt...@ece-llc.com* billt...@ece-llc.com



NABCEP Certified PV Installation Professional 032611-320





___
List sponsored by Home Power magazine

List Address: 
*RE-wrenches@lists.re-wrenches.org*RE-wrenches@lists.re-wrenches.org

Change email address  settings:
*http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org*http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: *
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org*http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
*www.re-wrenches.org/etiquette.htm*http://www.re-wrenches.org/etiquette.htm

Check out participant bios:
*www.members.re-wrenches.org* http://www.members.re-wrenches.org




Sent from Finest Planet WebMail.
--

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re

Re: [RE-wrenches] Battery Back-up and Grid Tie

2013-04-26 Thread SunHarvest
Should've mentioned that, sealed AGM. And his loads, the ones he wants to run 
on his CLP, are such that the batts would be cycling daily at least, with a 
D.O.D. yet to be determined (we're trying to stay above 49%).

Eric

- Original Message - 
  From: Bill Turberville 
  To: RE-wrenches 
  Sent: Friday, April 26, 2013 12:30 PM
  Subject: Re: [RE-wrenches] Battery Back-up and Grid Tie


  Batteries actually do better if they are cycled than if they just sit there.  
He may actually extend his battery life.  What kind of batteries is he using?



  From: re-wrenches-boun...@lists.re-wrenches.org 
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of SunHarvest
  Sent: Friday, April 26, 2013 2:25 PM
  To: RE-wrenches
  Subject: Re: [RE-wrenches] Battery Back-up and Grid Tie



  I have a crazy...I mean creative customer who wants a BB system so that he 
can run off-grid during peak and partial-peak rate hours: 1 to 7pm is peak, 7 
to 9pm is partial from PGE. He got this great idea from a tech at a reputable 
power optimizer manufacturer, whom I will not name here, who said, you've got 
the batteries just sitting there; why not put them to work?



  Initially he wanted his PV to operate while the sun is shining and the grid 
is down...and his batteries to supply power when the sun and grid is down. But 
now he wants his back-up system to do it all. We've touched on all the obvious 
points: 



  - Peak buying is also peak selling

  - Physics and efficiency losses determine that the energy he saves will 
never equal the energy he can put back into his system.

  - Decreased battery life due to increased cycling

  - Costs for batts and special inverters versus generator



  What is the definitive argument against BB in general and this peak shaving 
idea in particular?



  Thanks pros.



  Eric

  SunHarvest



  - Original Message - 

From: toddc...@finestplanet.com 

To: RE-wrenches 

Sent: Friday, April 26, 2013 11:57 AM

Subject: Re: [RE-wrenches] Battery Back-up and Grid Tie



our power outages generally come from bad weather too... and of course when 
the weather is bad the pv does next to nothing. so for emergency backup, i 
recommend a generator.



todd











On Friday, April 26, 2013 10:33am, Bill Turberville 
billt...@ece-llc.com said:

Not very often, and usually for no more than an hour or two, although it 
has been down as long as 5 days, either during tornado season, or ice taking 
down power lines.  What these people are looking for is Just In Case a big 
event happens.  They do not want to have all those panels just sitting there.

From: re-wrenches-boun...@lists.re-wrenches.org 
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Jay Peltz
Sent: Friday, April 26, 2013 12:25 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] Battery Back-up and Grid Tie



Hi bill



Just how often is your grid down?



Jay

Peltz power

Sent from my iPhone


On Apr 26, 2013, at 10:01 AM, Bill Turberville billt...@ece-llc.com wrote:

  I live in a TVA area where there is a Feed In Tariff.  Everything that is 
generated by the PV array feeds into the grid through a Generation Meter that 
ties-in ahead of the house meter.  I have started getting calls from customers 
who hate having a solar array that does not generate when the grid is down but 
the sun is shining, but who also want to get the $.12 premium when the grid is 
connected.  We have lots of systems with SMA Sunnyboy inverters, but more with 
Enphase micro-inverters.  Rather than trying to reinvent the wheel, what you 
found to be the best solution for this type of installation?



  W.C. (Bill) Turberville P.E.

  President



  ECE Solar

  Electrical Contracting Enterprises LLC

  3080 Stage Post Road Suite 107

  Bartlett, TN 38133



  901-348-9230 ext 101 phone

  901-348-2192 fax

  901-289-6346 cell

  billt...@ece-llc.com



  NABCEP Certified PV Installation Professional 032611-320





  ___
  List sponsored by Home Power magazine

  List Address: RE-wrenches@lists.re-wrenches.org

  Change email address  settings:
  http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

  List-Archive: 
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

  List rules  etiquette:
  www.re-wrenches.org/etiquette.htm

  Check out participant bios:
  www.members.re-wrenches.org




Sent from Finest Planet WebMail.




___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://lists.re

Re: [RE-wrenches] Battery Back-up and Grid Tie

2013-04-26 Thread toddcory

this is an incorrect myth.
 
todd
 
 
 
On Friday, April 26, 2013 12:30pm, Bill Turberville billt...@ece-llc.com 
said:




Batteries actually do better if they are cycled than if they just sit there.  
He may actually extend his battery life.  What kind of batteries is he using?
 


From: [mailto:re-wrenches-boun...@lists.re-wrenches.org] 
re-wrenches-boun...@lists.re-wrenches.org 
[mailto:[mailto:re-wrenches-boun...@lists.re-wrenches.org] 
re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of SunHarvest
Sent: Friday, April 26, 2013 2:25 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] Battery Back-up and Grid Tie
 

I have a crazy...I mean creative customer who wants a BB system so that he can 
run off-grid during peak and partial-peak rate hours: 1 to 7pm is peak, 7 to 
9pm is partial from PGE. He got this great idea from a tech at a reputable 
power optimizer manufacturer, whom I will not name here, who said, you've got 
the batteries just sitting there; why not put them to work?

 

Initially he wanted his PV to operate while the sun is shining and the grid is 
down...and his batteries to supply power when the sun and grid is down. But now 
he wants his back-up system to do it all. We've touched on all the obvious 
points: 

 

- Peak buying is also peak selling

- Physics and efficiency losses determine that the energy he saves will never 
equal the energy he can put back into his system.

- Decreased battery life due to increased cycling

- Costs for batts and special inverters versus generator

 

What is the definitive argument against BB in general and this peak shaving 
idea in particular?

 

Thanks pros.

 

Eric

SunHarvest

 

- Original Message -

From: [mailto:toddc...@finestplanet.com] toddc...@finestplanet.com 

To: [mailto:re-wrenches@lists.re-wrenches.org] RE-wrenches 

Sent: Friday, April 26, 2013 11:57 AM

Subject: Re: [RE-wrenches] Battery Back-up and Grid Tie

 
our power outages generally come from bad weather too... and of course when the 
weather is bad the pv does next to nothing. so for emergency backup, i 
recommend a generator.
 
todd
 
 
 
 
 
On Friday, April 26, 2013 10:33am, Bill Turberville 
[mailto:billt...@ece-llc.com] billt...@ece-llc.com said:


Not very often, and usually for no more than an hour or two, although it has 
been down as long as 5 days, either during tornado season, or ice taking down 
power lines.  What these people are looking for is Just In Case a big event 
happens.  They do not want to have all those panels just sitting there.


From: [mailto:re-wrenches-boun...@lists.re-wrenches.org] 
re-wrenches-boun...@lists.re-wrenches.org 
[mailto:[mailto:re-wrenches-boun...@lists.re-wrenches.org] 
re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Jay Peltz
Sent: Friday, April 26, 2013 12:25 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] Battery Back-up and Grid Tie
 

Hi bill

 

Just how often is your grid down?

 

Jay

Peltz power

Sent from my iPhone


On Apr 26, 2013, at 10:01 AM, Bill Turberville [mailto:billt...@ece-llc.com] 
billt...@ece-llc.com wrote:

I live in a TVA area where there is a Feed In Tariff.  Everything that is 
generated by the PV array feeds into the grid through a Generation Meter that 
ties-in ahead of the house meter.  I have started getting calls from customers 
who hate having a solar array that does not generate when the grid is down but 
the sun is shining, but who also want to get the $.12 premium when the grid is 
connected.  We have lots of systems with SMA Sunnyboy inverters, but more with 
Enphase micro-inverters.  Rather than trying to reinvent the wheel, what you 
found to be the best solution for this type of installation?
 
W.C. (Bill) Turberville P.E.
President
 
ECE Solar
Electrical Contracting Enterprises LLC
3080 Stage Post Road Suite 107
Bartlett, TN 38133
 
901-348-9230 ext 101 phone
901-348-2192 fax
901-289-6346 cell
[mailto:billt...@ece-llc.com] billt...@ece-llc.com
 
NABCEP Certified PV Installation Professional 032611-320
 
 

___
 List sponsored by Home Power magazine

List Address: [mailto:RE-wrenches@lists.re-wrenches.org] 
RE-wrenches@lists.re-wrenches.org

Change email address  settings:
[http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org] 
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
[http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org] 
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
[http://www.re-wrenches.org/etiquette.htm] www.re-wrenches.org/etiquette.htm

Check out participant bios:
[http://www.members.re-wrenches.org] www.members.re-wrenches.org



Sent from Finest Planet WebMail.

___
List sponsored by Home Power magazine

List Address: [mailto:RE-wrenches@lists.re-wrenches.org] 
RE-wrenches@lists.re-wrenches.org

Change email address  settings:
[http://lists.re-wrenches.org

Re: [RE-wrenches] Battery Back-up and Grid Tie

2013-04-26 Thread Dan Fink
I agree that this is an incorrect myth, when referring to lead-acid
batteries. The fewer times you cycle them, the longer they last. At this
time, we don't have any other options in the real world, though.

Dan Fink,
Executive Director;
Otherpower
Buckville Energy Consulting
Buckville Publications LLC
NABCEP / IREC accredited Continuing Education Providers
970.672.4342



On Fri, Apr 26, 2013 at 2:23 PM, toddc...@finestplanet.com wrote:

 this is an incorrect myth.



 todd







 On Friday, April 26, 2013 12:30pm, Bill Turberville 
 billt...@ece-llc.com said:

  Batteries actually do better if they are cycled than if they just sit
 there.  He may actually extend his battery life.  What kind of batteries is
 he using?



___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Battery Back-up and Grid Tie

2013-04-26 Thread toddcory

my biggest issue with bbgt systems is the inefficiency. my 4.3 kW (stc) array 
typically sells 2.8 kW.
 
5 years of tracking dc input versus ac output shows the obfx inverter runs 
around 87% efficiency. add battery maintenance and the extra wiring to split 
off backed up loads and the economics just dont work out.
 
then, if you make this scenario even worse by adding battery cycling 
inefficiency and more frequent replacement... (to supposedly make money??) it 
is a no-brainer your customers creative idea is actually a hair brained 
scheme which will result in a net loss and increased consumption of resources. 
his money would be better spent on upgrading to more efficient appliances, 
improvements to his building thermal performance and conservation.
 
i would not do this for a customer... and if they insisted, i'd let them hire 
someone else to implement these stupid (greenwashing) ideas for him. 
 
remember, you are the expert and your integrity and ethics are on the line here.
 
todd
 
 
 
 
 
 
 
On Friday, April 26, 2013 12:24pm, SunHarvest e...@harvesthesun.com said:



 
I have a crazy...I mean creative customer  who wants a BB system so that he can 
run off-grid during peak and partial-peak  rate hours: 1 to 7pm is peak, 7 to 
9pm is partial from PGE. He got this  great idea from a tech at a reputable 
power optimizer manufacturer, whom I will  not name here, who said, you've got 
the batteries just sitting there;  why not put them to work?
 
Initially he wanted his PV to operate while the sun  is shining and the grid is 
down...and his batteries to supply power when the sun  and grid is down. But 
now he wants his back-up system to do it all.  We've touched on all the obvious 
points: 
 
- Peak buying is also peak selling
- Physics and efficiency losses determine that the  energy he saves will 
never equal the energy he can put back into his  system.
- Decreased battery life due to increased  cycling
- Costs for batts and special inverters versus  generator
 
What is the definitive argument against BB  in general and this peak shaving 
idea in particular?
 
Thanks pros.
 
Eric
SunHarvest
 
- Original Message -
From: [mailto:toddc...@finestplanet.com] toddc...@finestplanet.com
To: [mailto:re-wrenches@lists.re-wrenches.org] RE-wrenches
Sent: Friday, April 26, 2013 11:57AM
Subject: Re: [RE-wrenches] BatteryBack-up and Grid Tie
ourpower outages generally come from bad weather too... and of course when 
theweather is bad the pv does next to nothing. so for emergency backup, i   
 recommend a generator.
 
todd
 
 
 
 
 
OnFriday, April 26, 2013 10:33am, Bill Turberville 
[mailto:billt...@ece-llc.com] billt...@ece-llc.comsaid:




Not very often, and usually forno more than an hour or two, although it has 
been down as long as 5 days,either during tornado season, or ice taking 
down power lines.  What thesepeople are looking for is Just In Case a big 
event happens.  They do notwant to have all those panels just sitting there.
 


From: [mailto:re-wrenches-boun...@lists.re-wrenches.org] 
re-wrenches-boun...@lists.re-wrenches.org 
[mailto:[mailto:re-wrenches-boun...@lists.re-wrenches.org] 
re-wrenches-boun...@lists.re-wrenches.org]On Behalf Of Jay Peltz
Sent: Friday,April 26, 2013 12:25 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] Battery Back-up andGrid Tie
 

Hi bill

 

Just how often is your grid down?

 

Jay

Peltz power

Sent from my iPhone


On Apr 26, 2013, at 10:01 AM, Bill Turberville [mailto:billt...@ece-llc.com] 
billt...@ece-llc.comwrote:

I live in a TVA area where there is a Feed In Tariff.   Everything that is 
generated by the PV array feeds into the grid through a  Generation Meter 
that ties-in ahead of the house meter.  I have started  getting calls from 
customers who hate having a solar array that does not  generate when the 
grid is down but the sun is shining, but who also want to  get the $.12 
premium when the grid is connected.  We have lots of  systems with SMA 
Sunnyboy inverters, but more with Enphase  micro-inverters.  Rather than 
trying to reinvent the wheel, what you  found to be the best solution for 
this type of installation?
 
W.C. (Bill) Turberville P.E.
President
 
ECE Solar
Electrical Contracting Enterprises LLC
3080 Stage Post Road Suite 107
Bartlett, TN 38133
 
901-348-9230 ext 101 phone
901-348-2192 fax
901-289-6346 cell
[mailto:billt...@ece-llc.com] billt...@ece-llc.com
 
NABCEP Certified PV Installation Professional 032611-320
 
 

___
List  sponsored by Home Power magazine

List Address: [mailto:RE-wrenches@lists.re-wrenches.org] 
RE-wrenches@lists.re-wrenches.org

Change  email address  settings:
[http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org] 
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:  
[http://lists.re-wrenches.org/pipermail/re-wrenches

Re: [RE-wrenches] Battery Back-up and Grid Tie

2013-04-26 Thread Gary Willett

  
  
Chris, et al:
  
  The EcoGen (6kw) was designed by Generac  the Propane Council
  from the ground up to run on LP, and to be used in an off-grid
  application. I've owned one for about 3 years now and I am very
  pleased with it. My home PV system is a 5.5 kW array into a
  Schneider XW system that is grid-tied battery-backup, with
  generator assist.
  
  Our grid in Irving TX is very reliable, with few outages. I like
  the security of knowing I will have power if/when an outage does
  occur. It's hard to but a price on that when one does a
  cost/benefit analysis. Most, if not all, of the customers I've had
  wanting GTBB systems are motivated in the same way.
  
  Regards,
  
  Gary Willett
  Icarus Solar
  
  On 4/26/13 1:41 PM, Chris Mason wrote:


  The Generac Guardian are fieldconvertibleto
propane. I imagine you can install a propane tank as we do here.
  

On Fri, Apr 26, 2013 at 2:40 PM, Bill
  Turberville billt...@ece-llc.com
  wrote:
  

  
I
have done that with several customers, but those
generators were natural gas, and their concern is if
we have an earth quake and lose natural gas, since
we are on the New Madrid fault.

From:
re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org]
On Behalf Of Chris Mason
Sent: Friday, April 26, 2013 1:36 PM

  
To: RE-wrenches
Subject: Re: [RE-wrenches] Battery Back-up
and Grid Tie


  

  

  For the price that you would
spend on batteries and a Sunny Island system,
you could buy and install a generator. I would
go that route.


  
  
On Fri, Apr 26, 2013 at
  1:33 PM, Bill Turberville billt...@ece-llc.com
  wrote:

  
Not very often,
and usually for no more than an hour or
two, although it has been down as long
as 5 days, either during tornado season,
or ice taking down power lines. What
these people are looking for is Just In
Case a big event happens. They do not
want to have all those panels just
sitting there.


  
From:
re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org]
On Behalf Of Jay Peltz
Sent: Friday, April 26, 2013
12:25 PM
To: RE-wrenches
Subject: Re: [RE-wrenches]
Battery Back-up and Grid Tie
  


  


  
Hi bill


  


  Just how often is
your grid down?


  


  Jay


  Peltz power

Sent from my iPhone


  
On Apr 26, 2013, at 10:01 AM, Bill
Turberville billt...@ece-llc.com
wrote

Re: [RE-wrenches] Battery Back-up and Grid Tie

2013-04-26 Thread Chris Mason
The Ecogen is an excellent unit, but it is not cheap. For the price of the
Ecogen, you can get a 20KW Guardian packaged unit with ATS and not buy all
the batteries and inverters and switchgear.
If you only get very rare outages, how does it make sense?



On Fri, Apr 26, 2013 at 5:14 PM, Gary Willett
g...@icarussolarservices.comwrote:

  Chris, et al:

 The EcoGen (6kw) was designed by Generac  the Propane Council from the
 ground up to run on LP, and to be used in an off-grid application. I've
 owned one for about 3 years now and I am very pleased with it. My home PV
 system is a 5.5 kW array into a Schneider XW system that is grid-tied
 battery-backup, with generator assist.

 Our grid in Irving TX is very reliable, with few outages. I like the
 security of knowing I will have power if/when an outage does occur. It's
 hard to but a price on that when one does a cost/benefit analysis. Most, if
 not all, of the customers I've had wanting GTBB systems are motivated in
 the same way.

 Regards,

 Gary Willett
 Icarus Solar


 On 4/26/13 1:41 PM, Chris Mason wrote:

 The Generac Guardian are field convertible to propane. I imagine you can
 install a propane tank as we do here.


 On Fri, Apr 26, 2013 at 2:40 PM, Bill Turberville billt...@ece-llc.comwrote:

  I have done that with several customers, but those generators were
 natural gas, and their concern is if we have an earth quake and lose
 natural gas, since we are on the New Madrid fault.



 *From:* re-wrenches-boun...@lists.re-wrenches.org [mailto:
 re-wrenches-boun...@lists.re-wrenches.org] *On Behalf Of *Chris Mason
 *Sent:* Friday, April 26, 2013 1:36 PM

 *To:* RE-wrenches
 *Subject:* Re: [RE-wrenches] Battery Back-up and Grid Tie



 For the price that you would spend on batteries and a Sunny Island
 system, you could buy and install a generator. I would go that route.



 On Fri, Apr 26, 2013 at 1:33 PM, Bill Turberville billt...@ece-llc.com
 wrote:

 Not very often, and usually for no more than an hour or two, although it
 has been down as long as 5 days, either during tornado season, or ice
 taking down power lines.  What these people are looking for is Just In Case
 a big event happens.  They do not want to have all those panels just
 sitting there.



 *From:* re-wrenches-boun...@lists.re-wrenches.org [mailto:
 re-wrenches-boun...@lists.re-wrenches.org] *On Behalf Of *Jay Peltz
 *Sent:* Friday, April 26, 2013 12:25 PM
 *To:* RE-wrenches
 *Subject:* Re: [RE-wrenches] Battery Back-up and Grid Tie



 Hi bill



 Just how often is your grid down?



 Jay

 Peltz power

 Sent from my iPhone


 On Apr 26, 2013, at 10:01 AM, Bill Turberville billt...@ece-llc.com
 wrote:

  I live in a TVA area where there is a Feed In Tariff.  Everything that
 is generated by the PV array feeds into the grid through a Generation Meter
 that ties-in ahead of the house meter.  I have started getting calls from
 customers who hate having a solar array that does not generate when the
 grid is down but the sun is shining, but who also want to get the $.12
 premium when the grid is connected.  We have lots of systems with SMA
 Sunnyboy inverters, but more with Enphase micro-inverters.  Rather than
 trying to reinvent the wheel, what you found to be the best solution for
 this type of installation?



 W.C. (Bill) Turberville P.E.

 President



 ECE Solar

 Electrical Contracting Enterprises LLC

 3080 Stage Post Road Suite 107

 Bartlett, TN 38133



 901-348-9230 ext 101 901-348-9230%20ext%20101 phone

 901-348-2192 fax

 901-289-6346 cell

 billt...@ece-llc.com



 NABCEP Certified PV Installation Professional 032611-320





  ___
 List sponsored by Home Power magazine

 List Address: RE-wrenches@lists.re-wrenches.org

 Change email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

 List-Archive:
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm

 Check out participant bios:
 www.members.re-wrenches.org


 ___
 List sponsored by Home Power magazine

 List Address: RE-wrenches@lists.re-wrenches.org

 Change email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

 List-Archive:
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm

 Check out participant bios:
 www.members.re-wrenches.org





 --
 Chris Mason

 President, Comet Systems Ltd

 www.cometenergysystems.com

 Cell: 264.235.5670

 Skype: netconcepts

 ___
 List sponsored by Home Power magazine

 List Address: RE-wrenches@lists.re-wrenches.org

 Change email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

 List-Archive:
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

 List rules  etiquette