Re: [RE-wrenches] Load size for off-grid lodge
Thanks all for the good suggestions on and off-list. We are going to go with a monitoring program. There were just too many variables to even try to guess with this project. Cheers, Jay Nunatak AES On Fri, May 7, 2010 at 7:59 AM, wrote: > As a bit of a swerve off the path of this stringI am designing a > grid-tie system for a building that is being "greenovated". Trying to lock > down a LEED req'd percentage shaving of annual demand. I know there is a > place to find assumptions from DOE, but I'm not that confident in those > because they can't possibly plug in all factors. Any sources out there that > might drill down the numbers a bit better? Or do I keep trying to hit the > swinging dart board blindfolded? EPRI seems to be designed for > utilities, grid EE's and such - haven't found any pertinent load assumption > info on the website. > Holt E. Kelly > Holtek Fireplace & Solar Products > 500 Jewell Dr. > Waco TX. 76712 > 254-751-9111 > www.holteksolar.com > > - Original Message - > *From:* Allan Sindelar > *To:* RE-wrenches > *Sent:* Thursday, May 06, 2010 11:50 PM > *Subject:* Re: [RE-wrenches] Load size for off-grid lodge > > Jason, > We attempted this about 2-3 years ago for a project on one of Ted Turner's > ranches. This was to be a top-of-the-line eco-lodge at 10,000' below a ridge > in the northern Rockies in New Mexico, with two 7kW Provens and a 3-phase > Sunny Boy/Sunny Island system. Due to the lack of real load analysis, and > the need to have large but essentially unknown capacity at the lodge, the > initial estimate was about $900K, as I recall. > > We never did the project, as they decided to go with dual generators. We > did get compensated for extensive design work. > > You may need to focus on large efficiencies and then put a usage fraction, > like 60%, on the electrical engineer's traditional load calcs. That's what > we did. And write in a section stating that you make no warranties as to the > sufficiency of the system to meet actual loads, as the loads can't be > accurately determined. > > Here's what I wrote in the initial pre-proposal: > > *I. **Load > Profile Methodology and Limitations* > > Typical off-grid PV systems are designed and sized based on a rigorous load > analysis as an essential first step. The load analysis is a detailed listing > of every electricity-consuming device, with power consumption and expected > daily usage figures, used to develop an accurate profile of total expected > daily kilowatt-hour consumption. From this data a power system of specific > design and capacity is developed. > > This approach is not possible for the XX Lodge, so an alternative approach > must be used to establish target design criteria. EPRI (Electric Power > Research Institute, the research arm of the U.S. electric utility industry) > has developed Technology Assessment Guides to predict power use for various > residential and commercial sectors. The comparative sector of lodging at > 12,000 square feet in the western U.S., establishes a figure of 223 > kilowatt-hours per day. This is a base figure, for conventional design > without energy-conserving measures, with adders for electric heat, hot > water, cooking and air conditioning, none of which will be used at XX Lodge. > > > From this *we have estimated that XX Lodge may be expected to have a total > average daily load not exceeding 190 kilowatt-hours per day*, or 85% of > the EPRI figure. This is the figure used in this preliminary budget > analysis. This may be considered to be quite conservative; that is, careful > attention to energy-conserving approaches during design and construction are > likely to considerably reduce this figure. > > Remember too that if they now have generators, they're not likely to > conserve, as generator power is pretty much all-or-nothing, with efficiency > unimportant within the gennie capacity. So there's a fair amount of load > management and education to fit in. > > Hope this little bit helps. > >
Re: [RE-wrenches] Load size for off-grid lodge
Friends: When faced with similar situations, we propose installation of permanent power monitoring equipment. Even if you don't get the job at this time, the client may tire of buying fuel or listening to and maintaining 24/7 generators. When re-contacted, you will have the data you need. In the meantime, the client will have the information needed to begin reducing loads through energy management, appliance upgrade, etc. William Miller At 09:50 PM 5/6/2010, you wrote: We never did the project, as they decided to go with dual generators. We did get compensated for extensive design work. ___ List sponsored by Home Power magazine List Address: RE-wrenches@lists.re-wrenches.org Options & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out participant bios: www.members.re-wrenches.org
Re: [RE-wrenches] Load size for off-grid lodge
As a bit of a swerve off the path of this stringI am designing a grid-tie system for a building that is being "greenovated". Trying to lock down a LEED req'd percentage shaving of annual demand. I know there is a place to find assumptions from DOE, but I'm not that confident in those because they can't possibly plug in all factors. Any sources out there that might drill down the numbers a bit better? Or do I keep trying to hit the swinging dart board blindfolded? EPRI seems to be designed for utilities, grid EE's and such - haven't found any pertinent load assumption info on the website. Holt E. Kelly Holtek Fireplace & Solar Products 500 Jewell Dr. Waco TX. 76712 254-751-9111 www.holteksolar.com - Original Message - From: Allan Sindelar To: RE-wrenches Sent: Thursday, May 06, 2010 11:50 PM Subject: Re: [RE-wrenches] Load size for off-grid lodge Jason, We attempted this about 2-3 years ago for a project on one of Ted Turner's ranches. This was to be a top-of-the-line eco-lodge at 10,000' below a ridge in the northern Rockies in New Mexico, with two 7kW Provens and a 3-phase Sunny Boy/Sunny Island system. Due to the lack of real load analysis, and the need to have large but essentially unknown capacity at the lodge, the initial estimate was about $900K, as I recall. We never did the project, as they decided to go with dual generators. We did get compensated for extensive design work. You may need to focus on large efficiencies and then put a usage fraction, like 60%, on the electrical engineer's traditional load calcs. That's what we did. And write in a section stating that you make no warranties as to the sufficiency of the system to meet actual loads, as the loads can't be accurately determined. Here's what I wrote in the initial pre-proposal: I. Load Profile Methodology and Limitations Typical off-grid PV systems are designed and sized based on a rigorous load analysis as an essential first step. The load analysis is a detailed listing of every electricity-consuming device, with power consumption and expected daily usage figures, used to develop an accurate profile of total expected daily kilowatt-hour consumption. From this data a power system of specific design and capacity is developed. This approach is not possible for the XX Lodge, so an alternative approach must be used to establish target design criteria. EPRI (Electric Power Research Institute, the research arm of the U.S. electric utility industry) has developed Technology Assessment Guides to predict power use for various residential and commercial sectors. The comparative sector of lodging at 12,000 square feet in the western U.S., establishes a figure of 223 kilowatt-hours per day. This is a base figure, for conventional design without energy-conserving measures, with adders for electric heat, hot water, cooking and air conditioning, none of which will be used at XX Lodge. From this we have estimated that XX Lodge may be expected to have a total average daily load not exceeding 190 kilowatt-hours per day, or 85% of the EPRI figure. This is the figure used in this preliminary budget analysis. This may be considered to be quite conservative; that is, careful attention to energy-conserving approaches during design and construction are likely to considerably reduce this figure. Remember too that if they now have generators, they're not likely to conserve, as generator power is pretty much all-or-nothing, with efficiency unimportant within the gennie capacity. So there's a fair amount of load management and education to fit in. Hope this little bit helps.
Re: [RE-wrenches] Load size for off-grid lodge
Jason, We attempted this about 2-3 years ago for a project on one of Ted Turner's ranches. This was to be a top-of-the-line eco-lodge at 10,000' below a ridge in the northern Rockies in New Mexico, with two 7kW Provens and a 3-phase Sunny Boy/Sunny Island system. Due to the lack of real load analysis, and the need to have large but essentially unknown capacity at the lodge, the initial estimate was about $900K, as I recall. We never did the project, as they decided to go with dual generators. We did get compensated for extensive design work. You may need to focus on large efficiencies and then put a usage fraction, like 60%, on the electrical engineer's traditional load calcs. That's what we did. And write in a section stating that you make no warranties as to the sufficiency of the system to meet actual loads, as the loads can't be accurately determined. Here's what I wrote in the initial pre-proposal: I. Load Profile Methodology and Limitations Typical off-grid PV systems are designed and sized based on a rigorous load analysis as an essential first step. The load analysis is a detailed listing of every electricity-consuming device, with power consumption and expected daily usage figures, used to develop an accurate profile of total expected daily kilowatt-hour consumption. From this data a power system of specific design and capacity is developed. This approach is not possible for the XX Lodge, so an alternative approach must be used to establish target design criteria. EPRI (Electric Power Research Institute, the research arm of the U.S. electric utility industry) has developed Technology Assessment Guides to predict power use for various residential and commercial sectors. The comparative sector of lodging at 12,000 square feet in the western U.S., establishes a figure of 223 kilowatt-hours per day. This is a base figure, for conventional design without energy-conserving measures, with adders for electric heat, hot water, cooking and air conditioning, none of which will be used at XX Lodge. From this we have estimated that XX Lodge may be expected to have a total average daily load not exceeding 190 kilowatt-hours per day, or 85% of the EPRI figure. This is the figure used in this preliminary budget analysis. This may be considered to be quite conservative; that is, careful attention to energy-conserving approaches during design and construction are likely to considerably reduce this figure. Remember too that if they now have generators, they're not likely to conserve, as generator power is pretty much all-or-nothing, with efficiency unimportant within the gennie capacity. So there's a fair amount of load management and education to fit in. Hope this little bit helps.
[RE-wrenches] Load size for off-grid lodge
Hey all, I am trying to size a PV/generator system for a 10,000 ft2 off-grid hunting/snowmobile lodge with outbuildings. The goal is to significantly reduce current generator run time. I was wondering if any of you have experience or suggestions for calculating time of use of lights, etc in a lodging situation. My interviews with the rancher have proven fruitless to pin down any time of use of most loads, though I do have an estimated run time for the genny in summer and winter. I did get a pretty good snapshot of his connected load by turning on all I could on and clamping the feeds. The lodge is 18 rooms, 4 for the help, and a few outbuildings. Has anyone sized any off-grid lodges? Any other ways to approach the moving target of such a fluctuating load at a guest lodge? Thanks Jay Pozner Nunatak Alternative Energy Solutions ___ List sponsored by Home Power magazine List Address: RE-wrenches@lists.re-wrenches.org Options & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out participant bios: www.members.re-wrenches.org