Re: [RE-wrenches] Fwd: Re: Cantilevered array

2024-02-13 Thread William Miller via RE-wrenches
Good question about rain shedding.

My questions for Sky:  were the installations evaluated by a structural
engineer to calculate ability to withstand wind effects and snow load?
What roof anchors were recommended?

William Miller
Miller Solar.com
805-438-5600
www.millersolar.com


On Tue, Feb 13, 2024 at 7:55 AM Drake Chamberlin via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:

> If the array covers the rain gutters, doesn't that prevent the gutters
> from catching rain? Doesn't the edge of the extended modules form a drip
> edge, where water will not be diverted by the gutters, but hit the ground
> directly?
>
> Will the gutters be accessible for future maintenance?
>
>
> *Drake Chamberlin*
>
> *Athens Electric LLC*
>
> *Ohio Electrical Contractor’s License 44810*
>
> *NABCEP Certified PV Installation Professional*
> ---
>
>
>
> On 2024-02-12 11:02, Christopher Warfel wrote:
>
> Hi, in what way?  The loading is obviously less, and the clamps are rated
> for the load.
> On 2/12/2024 10:56 AM, drake.chamber...@redwoodalliance.org wrote:
>
> How do you deal with the rain gutters?
>
>
> Drake Chamberlin
>
> Media & Communication Action Project
>
> https://m-cap.org/
> ---
>
>
>
> On 2024-02-08 16:46, Sky Sims via RE-wrenches wrote:
>
> I've designed and installed several thousand cantilevered arrays over the
> last three decades and never had a single issue. Unfortunately, code
> changes have taken a turn for the worse in most jurisdictions and
> oftentimes disallow cantilevering.
>
> Sky Sims
> Https://EcologicalSystems.org
> 732-462-3858
>
> On Jan 19, 2024, at 3:09 PM, Christopher Warfel via RE-wrenches
>  
> wrote:
>
> I've done a fair amount of roof mounted solar structural compliance, and
> I would say that the cantilevered design looks like a disaster waiting to
> happen. You could not use conventional solar racking products.  Chris
>
>
>
> On 1/13/2024 12:42 PM, William Miller via RE-wrenches wrote:
>
> Drake
>
>
>
> My earlier reply may have been a bit facetious.  What I meant by it was
> that big-box solar contractors can be lazy when it comes to solar design.
> They will rely totally on satellite imagery and not check the design on the
> ground.  This is how you get solar proposed for shaded areas, where
> skylights and roof vents are located, or overhanging thin air.  This may be
> what is happening in the image you shared.
>
>
>
> What is unique here is someone actually specified overhanging panels.
> Looking more closely at the image, a roof outline is shown but it is not
> clear that the outline is actually situated over a building.  It almost
> looks like there is landscaped area inside the outline.
>
>
>
> The solution of course is to get on out there, measure the roof and any
> obstructions and analyze the shading.  I use the Sun Seeker
> 
> app for IOS for the shading analysis.
>
>
>
> William
>
>
>
> Miller Solar
>
> 17395 Oak Road, Atascadero, CA 93422
>
> 805-438-5600
>
> www.millersolar.com
>
> CA Lic. 773985
>
>
>
>
>
> *From:* RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] *On
> Behalf Of *Drake Chamberlin via RE-wrenches
> *Sent:* Saturday, January 13, 2024 8:47 AM
> *To:* RE-wrenches
> *Cc:* drake.chamber...@redwoodalliance.org
> *Subject:* [RE-wrenches] Fwd: Re: Cantilevered array
>
>
>
>
>
>
>
>
>
>
>
>
>
>
>
>
>
>
>
>
>
> Here is a larger snip of the situation.
>
>
>
>
> 
>
> Label says overhang from upper roof.
>
>
>
> *Drake Chamberlin*
>
> *Athens Electric LLC*
>
> *Ohio Electrical Contractor's License 44810*
>
> *NABCEP Certified PV Installation Professional*
>
>
>
> ---
>
>
>
>
>
> On 2024-01-12 07:29, Jason Szumlanski wrote:
>
> Are you sure that's what you're looking at? To me, that looks like there
> was an addition made to the house, and maybe it's a multi-pitch roof. That
> lower part might be a covered wrap-around porch.
>
>
> Jason Szumlanski
>
> Principal Solar Designer | Florida Solar Design Group
> NABCEP Certified Solar Professional (PVIP)
> Florida State Certified Solar Contractor CVC56956
>
>
>
> On Thu, Jan 11, 2024 at 5:59 PM Drake Chamberlin via RE-wrenches <
> re-wrenches@lists.re-wrenches.org> wrote:
>
> I was given a drawing, produced by a very large solar company, showing the
> array cantilevered over the edge of the roof by several feet.
>
> 
>
>
>
> Notice how the array hangs out over the lawn for several feet. Is there
> anyway that this is a legitimate way to mount modules?
>
>
>
> Thanks,
>
>
>
> Drake
>
>
>
> *Drake Chamberlin*
>
> *Athens Electric LLC*
>
> *Ohio Electrical Contractor's License 44810*
>
> *NABCEP Certified PV Installation Professional*
>
>
>
> --
>
>
>
> ___
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/

Re: [RE-wrenches] Fwd: Re: Cantilevered array

2024-02-13 Thread Drake Chamberlin via RE-wrenches

If the array covers the rain gutters, doesn't that prevent the gutters
from catching rain? Doesn't the edge of the extended modules form a drip
edge, where water will not be diverted by the gutters, but hit the
ground directly?  

Will the gutters be accessible for future maintenance? 

_Drake Chamberlin_ 

_Athens Electric LLC_ 

_Ohio Electrical Contractor's License 44810_ 


_NABCEP Certified PV Installation Professional_

---

On 2024-02-12 11:02, Christopher Warfel wrote:


Hi, in what way?  The loading is obviously less, and the clamps are rated for 
the load.

On 2/12/2024 10:56 AM, drake.chamber...@redwoodalliance.org wrote: 

How do you deal with the rain gutters? 

Drake Chamberlin 

Media & Communication Action Project 


https://m-cap.org/

---

On 2024-02-08 16:46, Sky Sims via RE-wrenches wrote: 

I've designed and installed several thousand cantilevered arrays over the last three decades and never had a single issue. Unfortunately, code changes have taken a turn for the worse in most jurisdictions and oftentimes disallow cantilevering.  

Sky Sims 
Https://EcologicalSystems.org 
732-462-3858 


On Jan 19, 2024, at 3:09 PM, Christopher Warfel via RE-wrenches 
 wrote:

I've done a fair amount of roof mounted solar structural compliance, and I would say that the cantilevered design looks like a disaster waiting to happen. You could not use conventional solar racking products.  Chris 

On 1/13/2024 12:42 PM, William Miller via RE-wrenches wrote: 

Drake 

My earlier reply may have been a bit facetious.  What I meant by it was that big-box solar contractors can be lazy when it comes to solar design.  They will rely totally on satellite imagery and not check the design on the ground.  This is how you get solar proposed for shaded areas, where skylights and roof vents are located, or overhanging thin air.  This may be what is happening in the image you shared.  

What is unique here is someone actually specified overhanging panels.  Looking more closely at the image, a roof outline is shown but it is not clear that the outline is actually situated over a building.  It almost looks like there is landscaped area inside the outline. 

The solution of course is to get on out there, measure the roof and any obstructions and analyze the shading.  I use the Sun Seeker [1] app for IOS for the shading analysis. 

William 

Miller Solar 

17395 Oak Road, Atascadero, CA 93422 

805-438-5600 

www.millersolar.com [2] 

CA Lic. 773985 


From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf 
Of Drake Chamberlin via RE-wrenches
Sent: Saturday, January 13, 2024 8:47 AM
To: RE-wrenches
Cc: drake.chamber...@redwoodalliance.org
Subject: [RE-wrenches] Fwd: Re: Cantilevered array 

Here is a larger snip of the situation. 

 

Label says overhang from upper roof. 

_Drake Chamberlin_ 

_Athens Electric LLC_ 

_Ohio Electrical Contractor's License 44810_ 

_NABCEP Certified PV Installation Professional_ 


---

On 2024-01-12 07:29, Jason Szumlanski wrote: 

Are you sure that's what you're looking at? To me, that looks like there was an addition made to the house, and maybe it's a multi-pitch roof. That lower part might be a covered wrap-around porch. 

Jason Szumlanski 


Principal Solar Designer | Florida Solar Design Group
NABCEP Certified Solar Professional (PVIP)
Florida State Certified Solar Contractor CVC56956 

On Thu, Jan 11, 2024 at 5:59 PM Drake Chamberlin via RE-wrenches  wrote: 

I was given a drawing, produced by a very large solar company, showing the array cantilevered over the edge of the roof by several feet. 

 

Notice how the array hangs out over the lawn for several feet. Is there anyway that this is a legitimate way to mount modules? 

Thanks, 

Drake 

_Drake Chamberlin_ 

_Athens Electric LLC_ 

_Ohio Electrical Contractor's License 44810_ 

_NABCEP Certified PV Installation Professional_ 


--

___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org


___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try
the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenche

Re: [RE-wrenches] Fwd: Re: Cantilevered array

2024-02-12 Thread Christopher Warfel via RE-wrenches
Hi, in what way?  The loading is obviously less, and the clamps are 
rated for the load.


On 2/12/2024 10:56 AM, drake.chamber...@redwoodalliance.org wrote:


How do you deal with the rain gutters?


Drake Chamberlin

Media & Communication Action Project

https://m-cap.org/

---


On 2024-02-08 16:46, Sky Sims via RE-wrenches wrote:

I've designed and installed several thousand cantilevered arrays over 
the last three decades and never had a single issue. Unfortunately, 
code changes have taken a turn for the worse in most jurisdictions 
and oftentimes disallow cantilevering.


Sky Sims
Https://EcologicalSystems.org
732-462-3858

On Jan 19, 2024, at 3:09 PM, Christopher Warfel via RE-wrenches 
 wrote:


I've done a fair amount of roof mounted solar structural compliance, 
and I would say that the cantilevered design looks like a disaster 
waiting to happen. You could not use conventional solar racking 
products.  Chris




On 1/13/2024 12:42 PM, William Miller via RE-wrenches wrote:


Drake

My earlier reply may have been a bit facetious.  What I meant by it 
was that big-box solar contractors can be lazy when it comes to 
solar design. They will rely totally on satellite imagery and not 
check the design on the ground.  This is how you get solar proposed 
for shaded areas, where skylights and roof vents are located, or 
overhanging thin air.  This may be what is happening in the image 
you shared.


What is unique here is someone actually specified overhanging 
panels.  Looking more closely at the image, a roof outline is shown 
but it is not clear that the outline is actually situated over a 
building.  It almost looks like there is landscaped area inside the 
outline.


The solution of course is to get on out there, measure the roof and 
any obstructions and analyze the shading.  I use the Sun Seeker 
 
app for IOS for the shading analysis.


William

Miller Solar

17395 Oak Road, Atascadero, CA 93422

805-438-5600

www.millersolar.com 

CA Lic. 773985

*From:*RE-wrenches 
[mailto:re-wrenches-boun...@lists.re-wrenches.org 
] *On Behalf Of 
*Drake Chamberlin via RE-wrenches

*Sent:* Saturday, January 13, 2024 8:47 AM
*To:* RE-wrenches
*Cc:* drake.chamber...@redwoodalliance.org 


*Subject:* [RE-wrenches] Fwd: Re: Cantilevered array

**



**



**



**



Here is a larger snip of the situation.




Label says overhang from upper roof.

/Drake Chamberlin/

/Athens Electric LLC/

/Ohio Electrical Contractor's License 44810/

/NABCEP Certified PV Installation Professional/

---

On 2024-01-12 07:29, Jason Szumlanski wrote:

Are you sure that's what you're looking at? To me, that looks
like there was an addition made to the house, and maybe it's a
multi-pitch roof. That lower part might be a covered
wrap-around porch.


Jason Szumlanski

Principal Solar Designer | Florida Solar Design Group
NABCEP Certified Solar Professional (PVIP)
Florida State Certified Solar Contractor CVC56956

On Thu, Jan 11, 2024 at 5:59 PM Drake Chamberlin via
RE-wrenches mailto:re-wrenches@lists.re-wrenches.org>> wrote:

I was given a drawing, produced by a very large solar
company, showing the array cantilevered over the edge of
the roof by several feet.



Notice how the array hangs out over the lawn for several
feet. Is there anyway that this is a legitimate way to
mount modules?

Thanks,

Drake

/Drake Chamberlin/

/Athens Electric LLC/

/Ohio Electrical Contractor's License 44810/

/NABCEP Certified PV Installation Professional/

-- 


___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org


List Address: RE-wrenches@lists.re-wrenches.org


Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org


There are two list archives for searching. When one doesn't
work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/

http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org


List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm


Check out or update participant bios:
http://www.members.re-wrenches.org
<

Re: [RE-wrenches] Fwd: Re: Cantilevered array

2024-02-12 Thread Drake Chamberlin via RE-wrenches
How do you deal with the rain gutters? 

Drake Chamberlin 

Media & Communication Action Project 


https://m-cap.org/

---

On 2024-02-08 16:46, Sky Sims via RE-wrenches wrote:

I've designed and installed several thousand cantilevered arrays over the last three decades and never had a single issue. Unfortunately, code changes have taken a turn for the worse in most jurisdictions and oftentimes disallow cantilevering.  

Sky Sims 
Https://EcologicalSystems.org 
732-462-3858 


On Jan 19, 2024, at 3:09 PM, Christopher Warfel via RE-wrenches 
 wrote:


I've done a fair amount of roof mounted solar structural compliance, and I would say that the cantilevered design looks like a disaster waiting to happen. You could not use conventional solar racking products.  Chris 

On 1/13/2024 12:42 PM, William Miller via RE-wrenches wrote: 

Drake 

My earlier reply may have been a bit facetious.  What I meant by it was that big-box solar contractors can be lazy when it comes to solar design.  They will rely totally on satellite imagery and not check the design on the ground.  This is how you get solar proposed for shaded areas, where skylights and roof vents are located, or overhanging thin air.  This may be what is happening in the image you shared.  

What is unique here is someone actually specified overhanging panels.  Looking more closely at the image, a roof outline is shown but it is not clear that the outline is actually situated over a building.  It almost looks like there is landscaped area inside the outline. 

The solution of course is to get on out there, measure the roof and any obstructions and analyze the shading.  I use the Sun Seeker [1] app for IOS for the shading analysis. 

William 

Miller Solar 

17395 Oak Road, Atascadero, CA 93422 

805-438-5600 

www.millersolar.com [2] 

CA Lic. 773985 


From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf 
Of Drake Chamberlin via RE-wrenches
Sent: Saturday, January 13, 2024 8:47 AM
To: RE-wrenches
Cc: drake.chamber...@redwoodalliance.org
Subject: [RE-wrenches] Fwd: Re: Cantilevered array 

Here is a larger snip of the situation. 

 

Label says overhang from upper roof. 

_Drake Chamberlin_ 

_Athens Electric LLC_ 

_Ohio Electrical Contractor's License 44810_ 

_NABCEP Certified PV Installation Professional_ 


---

On 2024-01-12 07:29, Jason Szumlanski wrote: 

Are you sure that's what you're looking at? To me, that looks like there was an addition made to the house, and maybe it's a multi-pitch roof. That lower part might be a covered wrap-around porch. 

Jason Szumlanski 


Principal Solar Designer | Florida Solar Design Group
NABCEP Certified Solar Professional (PVIP)
Florida State Certified Solar Contractor CVC56956 

On Thu, Jan 11, 2024 at 5:59 PM Drake Chamberlin via RE-wrenches  wrote: 

I was given a drawing, produced by a very large solar company, showing the array cantilevered over the edge of the roof by several feet. 

 

Notice how the array hangs out over the lawn for several feet. Is there anyway that this is a legitimate way to mount modules? 

Thanks, 

Drake 

_Drake Chamberlin_ 

_Athens Electric LLC_ 

_Ohio Electrical Contractor's License 44810_ 

_NABCEP Certified PV Installation Professional_ 


--

___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org


___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try
the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

--

Christopher Warfel
ENTECH Engineering, Inc.
PO Box 871, Block Island, RI 02807
   401-466-8978
 


 ___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver ema

Re: [RE-wrenches] Fwd: Re: Cantilevered array

2024-02-08 Thread Sky Sims via RE-wrenches
I’ve designed and installed several thousand cantilevered arrays over the last three decades and never had a single issue. Unfortunately, code changes have taken a turn for the worse in most jurisdictions and oftentimes disallow cantilevering. Sky SimsHttps://EcologicalSystems.org732-462-3858On Jan 19, 2024, at 3:09 PM, Christopher Warfel via RE-wrenches  wrote:

  

  
  
I've done a fair amount of roof mounted solar
structural compliance, and I would say that the cantilevered
design looks like a disaster waiting to happen. You could not
use conventional solar racking products.  Chris





On 1/13/2024 12:42 PM, William Miller
  via RE-wrenches wrote:


  
  
  
  
Drake
 
My
earlier reply may have been a bit facetious.  What I meant
by it was that big-box solar contractors can be lazy when it
comes to solar design.  They will rely totally on satellite
imagery and not check the design on the ground.  This is how
you get solar proposed for shaded areas, where skylights and
roof vents are located, or overhanging thin air.  This may
be what is happening in the image you shared.  
 
What
is unique here is someone actually specified overhanging
panels.  Looking more closely at the image, a roof outline
is shown but it is not clear that the outline is actually
situated over a building.  It almost looks like there is
landscaped area inside the outline.
 
The
solution of course is to get on out there, measure the roof
and any obstructions and analyze the shading.  I use the Sun Seeker app for IOS for the
shading analysis.
 
William
 

  Miller
  Solar
  17395
  Oak Road, Atascadero, CA 93422
  805-438-5600
  www.millersolar.com
  CA
  Lic. 773985
   

 

  
From:
RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org]
On Behalf Of Drake Chamberlin via RE-wrenches
Sent: Saturday, January 13, 2024 8:47 AM
To: RE-wrenches
Cc: drake.chamber...@redwoodalliance.org
Subject: [RE-wrenches] Fwd: Re: Cantilevered
array
  

 
 

  

  
 
  
  
 
  


  
 
  
  
 
  


  
 
  
  
 
  


  
 
  
  
 
  

  


  
Here is a
larger snip of the situation.
 

Label
says overhang from upper roof. 
 
Drake
  Chamberlin
Athens
  Electric LLC
Ohio
  Electrical Contractor’s License 44810
NABCEP
  Certified PV Installation Professional
 

  ---
  
 
  

 
On
2024-01-12 07:29, Jason Szumlanski wrote:

  

  

  Are
  you sure that's what you're looking at? To me,
  that looks like there was an addition made to
  the house, and maybe it's a multi-pitch roof.
  That lower part might be a covered wrap-around
  porch.


  

  
  Jason Szumlanski 
  
Principal
Solar Designer | Florida Solar Design
Group
NABCEP Certified Solar Professional
(PVIP)
Florida State Certified Solar Contractor
CVC56956
  

  

  
   
  

  On
  Thu, Jan 11, 2024 at 5:59 PM Drake Chamber