Hi
Wire Gauge) Numbers

  Some types of wire

Note: For an understanding of the AWG numbers, you may want to first see the
section: "
American Wire Gauge (AWG) table for annealed copper wire".


A semi-infinite variety of wire and cable is used in modern appliances,
electronics, and construction.  Here is a quick summary of the buzz words
so you will have some idea of what your 12 year old is talking about!

* Solid wire: The current carrying conductor is a single solid piece of 
metal
(usually copper.  It may be bare, tinned (solder coated), silver plated, or
something else.

Solid wire may be used for general hookup inside appliances and electronics,
and building (and higher power wiring) but not for cords that need to be
flexible and flexed repeatedly.

* Stranded wire: The current carrying conductor consists of multiple strands
of copper or tinned copper (though other metals may be found in some cases).
The individual strands are NOT insulated from one-another.  The wire gauge
is determined by the total cross sectional area (which may be a bit greater
than the specified AWG number due to discrete number of strands).  See the
section: "
What about stranded wire?".


Stranded wire is used for general hookup, building wiring, etc.  It is
easier to position than solid wire (but tends not to stay put) and more
robust when flexed repeatedly.  Cordsets always use finely stranded wire
but despite this, may develop problems due to flexing after long use.

* Magnet wire: This is a solid copper (or sometimes aluminum or silver)
conductor insulated with a very thin layer of varnish or high-tech plastic.
This coating must be removed either chemically, by heating in a flame, or
fine sandpaper, before the wire can be connected to anything.

Magnet wire is used where a large number of turns of wire must be packed as
tightly as possible in a limited space - transformers, motors, relays,
solenoids, etc.

The very thin insulation is susceptible to nicks and other damage.

* Litz wire: This is similar to stranded wire EXCEPT that the strands are
individually insulated from each other (like multiple pieces of magnet
wire).

Litz wire is used in high frequency transformers to reduce losses (including
the skin effect which results in current only traveling near the surface
of the wire - using multiple insulated strands increases its effective
surface area).

Like magnet wire, the insulation needs to be removed from all strands before
making connections.

* Tinsel wire: A very thin, metallic conductor is wound around a flexible
cloth or plastic core.

Tinsel wire is found in telephone and headphone cords since it can be made
extremely flexible.

Repair is difficult (but not impossible) since it very fine and the
conductor must be unraveled from the core for soldering.  The area of the
repair must be carefully insulated and will be less robust than the rest of
the cord.

* Shielded wire: An insulated central conductor is surrounded by a metal 
braid
and/or foil shield.

Shielded wire is used for low level audio and video, and other analog or
digital signals where external interference needs to be minimized.

* Coaxial cable: This is similar to shielded wire but may be more robust and
have a specified impedance for transmitting signals over long distances.

* Zip cord: This is 2 or 3 (or sometimes more) conductor cable where the
plastic insulation is scored so that the individual wires can be easily
separated for attachment to the plug or socket.

* 14/2, 12/3, etc.: These are the abbreviations used for building 
(electrical)
wire like Romex (which is one name brand) and for round or zip-type cordset
wire.  The conductor material is usually copper.

Note: Some houses during the '50s and '60s were constructed with aluminum
wiring which has since been found to result in significantly increased risk
of fire and other problems.  For more information, see the references listed
in the section: "
Safe electrical wiring".
However, aluminum wiring is safe
if installed according to very specific guidelines (and is used extensively
in power transmission and distribution - probably for your main connection
to the utility - due to its light weight and low cost).

The first number is the AWG wire gauge.

The second number is the number of insulated conductors (excluding any bare
safety ground if present).  For example:

- A 14/2 Romex cable has white and black insulated solid #14 AWG current
carrying conductors and a bare safety ground (some older similar types of
cable had no safety ground, however).

- A 16/3 cordset has white, black and green insulated stranded #16 AWG wires
(or, overseas, blue, brown, and green or green with yellow stripe).

  17.2) So, where did AWG come from?


Nearly everyone who has done any sort of wiring probably knows that the AWG 
or
American Wire Gauge number refers to the size of the wire somehow.  But how?

(From: Frank ([EMAIL PROTECTED])).

According to the 'Standard Handbook for Electrical Engineers' (Fink and 
Beaty)
the 'gauge' you referenced to is 'American Wire Gauge' or AWG and also known
as Brown & Sharp gauge.

According to above handbook, the AWG designation corresponds to the number 
of
steps by which the wire is drawn. Say the 18 AWG is smaller than 10 AWG and 
is
therefore drawn more times than the 10 AWG to obtain the smaller cross
sectional area.  The AWG numbers were not chosen arbitrary but follows a
mathematical formulation devised by J. R. Brown in 1857!

  17.3) For the marginally mathematically inclined


Each increase of 3 in the gauge halves the cross sectional area.  Each
reduction by 3 doubles it.  So, 2 AWG 14 wires is like one AWG 11.

It seems that everyone has their own pet formula for this (though I prefer
to just check the chart, below!).

(From: Tom Bruhns ([EMAIL PROTECTED])).

As I understand it, AWG is defined to be a geometric progression with AWG 
0000
defined to be 460 mils diameter and 36 gauge defined to be 5.000 mils 
diameter.
This leads directly to the formula:

Diameter(mils) = 5 * 92^((36-AWG)/39)

That is, 460 mils is 92 times 5 mils, and the exponent accounts for 39 steps
of AWG number starting at 36 gauge.

(From: David Knaack ([EMAIL PROTECTED])).

You can get a fairly accurate wire diameter by using the equation:

Diameter(inches) = 0.3252 * e^(-0.116 * AWG)

where 'e' is the base of the natural logarithms, 2.728182....

I don't know where it came from, but it is handy (more so if you can do 
natural
base exponentials in your head).

In its simplest form, the cross sectional area is:

A(circular mils) = 2^((50 - AWG) / 3)

  17.4) American Wire Gauge (AWG) table for annealed copper wire


(Similar tables exist for other types of wire, e.g., aluminum.)

(Table provided by: Peter Boniewicz ([EMAIL PROTECTED])).

Wire Table for AWG 0000 to 40, with diam in mils, circular mils,
square microinches, ohms per foot, ft per lb, etc.

AWG  Dia in  Circ.  Square  Ohm per lbs per Feet/   Feet/    Ohms/
gauge  mils   Mils   MicroIn 1000 ft 1000 ft Pound    Ohm     Pound
-------------------------------------------------------------------------
0000  460.0  211600  166200  0.04901 640.5   1.561   20400   0.00007652
000   409.6  167800  131800  0.06180 507.9   1.968   16180   0.0001217
00    364.8  133100  104500  0.07793 402.8   2.482   12830   0.0001935

0     324.9  105500  82890   0.09827 319.5   3.130   10180   0.0003076
1     289.3  83690   65730   0.1239  253.3   3.947   8070    0.0004891
2     257.6  66370   52130   0.1563  200.9   4.977   6400    0.0007778

3     229.4  52640   41340   0.1970  159.3   6.276   5075    0.001237
4     204.3  41740   32780   0.2485  126.4   7.914   4025    0.001966
5     181.9  33100   26000   0.3133  100.2   9.980   3192    0.003127

6     162.0  26250   20620   0.3951  79.46   12.58   2531    0.004972
7     144.3  20820   16350   0.4982  63.02   15.87   2007    0.007905
8     128.5  16510   12970   0.6282  49.98   20.01   1592    0.01257

9     114.4  13090   10280   0.7921  39.63   25.23   1262    0.01999
10    101.9  10380   8155    0.9989  31.43   31.82   1001    0.03178
11    90.74  8234    6467    1.260   24.92   40.12   794     0.05053

12    80.81  6530    5129    1.588   19.77   50.59   629.6   0.08035
13    71.96  5178    4067    2.003   15.68   63.80   499.3   0.1278
14    64.08  4107    3225    2.525   12.43   80.44   396.0   0.2032

15    57.07  3257    2558    3.184   9.858   101.4   314.0   0.3230
16    50.82  2583    2028    4.016   7.818   127.9   249.0   0.5136
17    45.26  2048    1609    5.064   6.200   161.3   197.5   0.8167

18    40.30  1624    1276    6.385   4.917   203.4   156.6   1.299
19    35.89  1288    1012    8.051   3.899   256.5   124.2   2.065
20    31.96  1022    802.3   10.15   3.092   323.4   98.50   3.283

21    28.46  810.1   636.3   12.80   2.452   407.8   78.11   5.221
22    25.35  642.4   504.6   16.14   1.945   514.2   61.95   8.301
23    22.57  509.5   400.2   20.36   1.542   648.4   49.13   13.20

24    20.10  404.0   317.3   25.67   1.223   817.7   38.96   20.99
25    17.90  320.4   251.7   32.37   0.9699  1031.0  30.90   33.37
26    15.94  254.1   199.6   40.81   0.7692  1300    24.50   53.06

27    14.20  201.5   158.3   51.47   0.6100  1639    19.43   84.37
28    12.64  159.8   125.5   64.90   0.4837  2067    15.41   134.2
29    11.26  126.7   99.53   81.83   0.3836  2607    12.22   213.3

30    10.03  100.5   78.94   103.2   0.3042  3287    9.691   339.2
31    8.928  79.70   62.60   130.1   0.2413  4145    7.685   539.3
32    7.950  63.21   49.64   164.1   0.1913  5227    6.095   857.6

33    7.080  50.13   39.37   206.9   0.1517  6591    4.833   1364
34    6.305  39.75   31.22   260.9   0.1203  8310    3.833   2168
35    5.615  31.52   24.76   329.0   0.09542 10480   3.040   3448

36    5.000  25.00   19.64   414.8   0.07568 13210   2.411   5482
37    4.453  19.83   15.57   523.1   0.06001 16660   1.912   8717
38    3.965  15.72   12.35   659.6   0.04759 21010   1.516   13860

39    3.531  12.47   9.793   831.8   0.03774 26500   1.202   22040
40    3.145  9.888   7.766   1049.0  0.02993 33410   0.9534  35040
41    2.808  7.860   6.175   1319    0.02379 42020   0.758   55440

42    2.500  6.235   4.896   1663    0.01887 53000   0.601   88160
43    2.226  4.944   3.883   2098    0.01497 66820   0.476   140160
44    1.982  3.903   3.087   2638    0.01189 84040   0.379   221760

45    1.766  3.117   2.448   3326    0.00943 106000  0.300   352640
46    1.572  2.472   1.841   4196    0.00748 133640  0.238   560640

Ohms per 1000 ft, ft per Ohm, Ohms per lb, all taken at 20 degC (68 degF).

Note: Values for AWG #41 to #46 extrapolated from AWG #35 to #40 based on 
wire
gauge formula.

  17.5) What about stranded wire?


(From: Calvin Henry-Cotnam ([EMAIL PROTECTED])).

In addition to the cross-section area, there are a few other factors.  First
off, a stranded wire effectively has more surface area than a solid wire of
the same gauge, but much of this surface is "inside" the wire.

I checked out the label of a spool of #18 stranded wire and found it was
comprised of 16 strands of #30 wire.  Given the info above that each 
reduction
of 3 in the gauge, then #18 has a cross-section area that is 16 times 
greater
than #30 -- so it *appears* to translate exactly.

Looking through a catalog for wire, I found that this more-or-less holds 
true,
though the occasional wire might have an extra strand or two.  Here is what 
I
quickly found -- there are many more, but this is a sample:

  17.6) Overall gauge Typical stranded wires made up of

            #32              7 x #40
#30              7 x #38
#28              7 x #36
#26              7 x #34
#24              7 x #32    19 x #36
#22              7 x #30    19 x #34
#20              7 x #28    10 x #30    19 x #32
#18             16 x #30
#16             19 x #29    26 x #30
#14             41 x #30
#12             65 x #30
#10             65 x #28
#8             84 x #27 



------------------------ Yahoo! Groups Sponsor --------------------~--> 
Great things are happening at Yahoo! Groups.  See the new email design.
http://us.click.yahoo.com/TISQkA/hOaOAA/yQLSAA/86xolB/TM
--------------------------------------------------------------------~-> 

To listen to the show archives go to link
 http://acbradio.org/handyman.html
or
ftp://ftp.acbradio.org/acbradio-archives/handyman/

The Pod Cast address for the Blind Handy Man Show is.
http://www.acbradio.org/news/xml/podcast.php?pgm=saturday

The Pod Cast address for the Cooking In The Dark Show is.
http://www.gcast.com/u/cookingindark/main.xml

Visit The New Blind Handy Man Files Page To Review Contributions From Various 
List Members At The Following Address:
http://www.jaws-users.com/handyman/
Visit the new archives page at the following address
http://www.mail-archive.com/blindhandyman@yahoogroups.com/  
For a complete list of email commands pertaining to the Blind Handy Man list 
just send a blank message to:
[EMAIL PROTECTED] 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/blindhandyman/

<*> To unsubscribe from this group, send an email to:
    [EMAIL PROTECTED]

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/
 



Reply via email to