 speaking of UPS's...

 I -almost- ordered $300 worth of UPS replacement batteries today, but on
 a hunch, I swapped electronic modules with a twin UPS (the ERM is
 hotswappable on these 2U 3000VA units), and lo and behold, its the ERM
 thats faulty, not the battery pack.   found a fleabay ERM for $250  (OEM
 wants $1000).I have 3 of them, all about 5 years old, with 3 2U
 expansion battery packs, for a total of 9 battery packs, $2000-3000 to
 replace all of them.

Um, well The beginning of the year, we had a utility shutdown for
repairs, so we shut all our servers down, and the UPSs as well. Brought
them back up after the long weekend... and it took over a month for the
red light to come back. Watch out that the one you swapped doesn't come
back in a few weeks.

mark

___
CentOS mailing list
CentOS@centos.org
http://lists.centos.org/mailman/listinfo/centos


Re: [CentOS] Back to apcupsd

2010-03-17 Thread John R Pierce
m.r...@5-cent.us wrote:
 speaking of UPS's...

 I -almost- ordered $300 worth of UPS replacement batteries today, but on
 a hunch, I swapped electronic modules with a twin UPS (the ERM is
 hotswappable on these 2U 3000VA units), and lo and behold, its the ERM
 thats faulty, not the battery pack.   found a fleabay ERM for $250  (OEM
 wants $1000).I have 3 of them, all about 5 years old, with 3 2U
 expansion battery packs, for a total of 9 battery packs, $2000-3000 to
 replace all of them.
 

 Um, well The beginning of the year, we had a utility shutdown for
 repairs, so we shut all our servers down, and the UPSs as well. Brought
 them back up after the long weekend... and it took over a month for the
 red light to come back. Watch out that the one you swapped doesn't come
 back in a few weeks.
   

when I put the suspect ERM module in the other UPS it faulted.   when I 
put the 'good' ERM back in its own UPS it was good.  when I reinstalled 
the suspect ERM in the original UPS, it faulted.

btw, fwiw, these are HP R3000XR UPS's 
http://h18000.www1.hp.com/products/servers/proliantstorage/power-protection/rackups/r3000xr/index.html,
They have been quite good for me, this one ERM failure at 5 years old 
has been their only problem.  with the battery expansion bay, they have 
like 20 minutes at full load (but I only have like 30-40% load on 
them).  high efficiency, they run cool.  





___
CentOS mailing list
CentOS@centos.org
http://lists.centos.org/mailman/listinfo/centos


Re: [CentOS] Back to apcupsd

2010-03-16 Thread Scott Silva
on 3-2-2010 2:13 PM m.r...@5-cent.us spake the
following:
 Ok, so another apc UPS 3000 complained about bad batteries, and I changed
 them out from the same order that I'd gotten in a couple of months ago.
 
 The APC SmartUPS 3000 started connecting and disconnecting the USB
 connection. I brought down and up the service, no joy.
 
 Finally, after googling, I found a *completely* undocumented way to start
 apcupsd, that a few years ago someone was told to try, so as to log
 debugging info, to send to a developer:
apcupsd -d1000 -T
 I've just skimmed the man page, and the online docs, and there is *no*
 mention of either parm. I found nothing in the logs.
 
 However, when I kill -HUPped it, and restarted the service, the USB stuff
 had stopped. Ok, one problem down.
 
 The change battery light's still on. I'll see if it still is in the
 morning. One thing I did note, while skimming the docs, and comparing my
 results from apcaccess, was that while the nominal voltage for the APC
 SmartUPS 3000 is 48V, the new batteries are showing 55.4V. Anyone have any
 idea if this could be why the replace battery light's on - it's more than
 5V difference?
 
   mark
The light might stay on until either the next battery test, or re-setting the
stored battery change date. I never have been able to get the date changed
from *nix. I usually used a windows laptop with APC software installed. It can
probably be done, just never spent a long time trying.



signature.asc
Description: OpenPGP digital signature
___
CentOS mailing list
CentOS@centos.org
http://lists.centos.org/mailman/listinfo/centos


Re: [CentOS] Back to apcupsd

2010-03-16 Thread m . roth
 on 3-2-2010 2:13 PM m.r...@5-cent.us spake the
 following:
 Ok, so another apc UPS 3000 complained about bad batteries, and I
 changed them out from the same order that I'd gotten in a couple of
 months ago.

 The APC SmartUPS 3000 started connecting and disconnecting the USB
 connection. I brought down and up the service, no joy.
snip
 The change battery light's still on. I'll see if it still is in the
 morning. One thing I did note, while skimming the docs, and comparing my
 results from apcaccess, was that while the nominal voltage for the APC
 SmartUPS 3000 is 48V, the new batteries are showing 55.4V. Anyone have
 any idea if this could be why the replace battery light's on - it's more
 than 5V difference?

 The light might stay on until either the next battery test, or re-setting
 the stored battery change date. I never have been able to get the date
 changed from *nix. I usually used a windows laptop with APC software
 installed. It can probably be done, just never spent a long time trying.

Thanks, but no joy. I had no problem using apcupsd to reset the battery
change date... but that didn't do it. I've done numerous battery tests,
both from apctest, with apcupsd down, and by pushing the button.

*sigh*

We've ordered another set of batteries for one of these, this time the
exact same make and model that were in them, though still not the full OEM
cartridge, and we'll see if it does need HR (high rate) batteries. If so,
then what was advertised as a replacement kit is untrue.

   mark

___
CentOS mailing list
CentOS@centos.org
http://lists.centos.org/mailman/listinfo/centos


Re: [CentOS] Back to apcupsd

2010-03-16 Thread Scott Silva
on 3-16-2010 8:43 AM m.r...@5-cent.us spake the
following:
 on 3-2-2010 2:13 PM m.r...@5-cent.us spake the
 following:
 Ok, so another apc UPS 3000 complained about bad batteries, and I
 changed them out from the same order that I'd gotten in a couple of
 months ago.

 The APC SmartUPS 3000 started connecting and disconnecting the USB
 connection. I brought down and up the service, no joy.
 snip
 The change battery light's still on. I'll see if it still is in the
 morning. One thing I did note, while skimming the docs, and comparing my
 results from apcaccess, was that while the nominal voltage for the APC
 SmartUPS 3000 is 48V, the new batteries are showing 55.4V. Anyone have
 any idea if this could be why the replace battery light's on - it's more
 than 5V difference?

 The light might stay on until either the next battery test, or re-setting
 the stored battery change date. I never have been able to get the date
 changed from *nix. I usually used a windows laptop with APC software
 installed. It can probably be done, just never spent a long time trying.
 
 Thanks, but no joy. I had no problem using apcupsd to reset the battery
 change date... but that didn't do it. I've done numerous battery tests,
 both from apctest, with apcupsd down, and by pushing the button.
 
 *sigh*
 
 We've ordered another set of batteries for one of these, this time the
 exact same make and model that were in them, though still not the full OEM
 cartridge, and we'll see if it does need HR (high rate) batteries. If so,
 then what was advertised as a replacement kit is untrue.
 
mark
Yeah... Been burned by OEM batteries in the past... Usually buy direct from
APC anymore... Not worth it




signature.asc
Description: OpenPGP digital signature
___
CentOS mailing list
CentOS@centos.org
http://lists.centos.org/mailman/listinfo/centos


Re: [CentOS] Back to apcupsd

2010-03-16 Thread Bowie Bailey
Scott Silva wrote:
 on 3-16-2010 8:43 AM m.r...@5-cent.us spake the
 following:
   
 on 3-2-2010 2:13 PM m.r...@5-cent.us spake the
 following:
   
 Ok, so another apc UPS 3000 complained about bad batteries, and I
 changed them out from the same order that I'd gotten in a couple of
 months ago.

 The APC SmartUPS 3000 started connecting and disconnecting the USB
 connection. I brought down and up the service, no joy.
 
 snip
 
 The change battery light's still on. I'll see if it still is in the
 morning. One thing I did note, while skimming the docs, and comparing my
 results from apcaccess, was that while the nominal voltage for the APC
 SmartUPS 3000 is 48V, the new batteries are showing 55.4V. Anyone have
 any idea if this could be why the replace battery light's on - it's more
 than 5V difference?

 
 The light might stay on until either the next battery test, or re-setting
 the stored battery change date. I never have been able to get the date
 changed from *nix. I usually used a windows laptop with APC software
 installed. It can probably be done, just never spent a long time trying.
   
 Thanks, but no joy. I had no problem using apcupsd to reset the battery
 change date... but that didn't do it. I've done numerous battery tests,
 both from apctest, with apcupsd down, and by pushing the button.

 *sigh*

 We've ordered another set of batteries for one of these, this time the
 exact same make and model that were in them, though still not the full OEM
 cartridge, and we'll see if it does need HR (high rate) batteries. If so,
 then what was advertised as a replacement kit is untrue.

mark
 
 Yeah... Been burned by OEM batteries in the past... Usually buy direct from
 APC anymore... Not worth it

I don't have a 3000, but I've got a few SU2200's and a pile of SU700's. 
I get all my replacement batteries from Batteries Plus (Werker brand)
and have never had a problem.  The replace battery light stays on until
I do a battery test (let it charge for 24 hours, then test it via the
button).

-- 
Bowie
___
CentOS mailing list
CentOS@centos.org
http://lists.centos.org/mailman/listinfo/centos


Re: [CentOS] Back to apcupsd

2010-03-16 Thread John R Pierce
speaking of UPS's...

I -almost- ordered $300 worth of UPS replacement batteries today, but on 
a hunch, I swapped electronic modules with a twin UPS (the ERM is 
hotswappable on these 2U 3000VA units), and lo and behold, its the ERM 
thats faulty, not the battery pack.   found a fleabay ERM for $250  (OEM 
wants $1000).I have 3 of them, all about 5 years old, with 3 2U 
expansion battery packs, for a total of 9 battery packs, $2000-3000 to 
replace all of them.
___
CentOS mailing list
CentOS@centos.org
http://lists.centos.org/mailman/listinfo/centos


Re: [CentOS] Back to apcupsd

2010-03-02 Thread John R Pierce
m.r...@5-cent.us wrote:
 ...that while the nominal voltage for the APC
 SmartUPS 3000 is 48V, the new batteries are showing 55.4V. 


lead acid batteries are 2.1-2.15V per cell when fully charged, and the 
trickle charging float voltage is more like 2.3V per cell.  2.3 * 6 
cells/battery * 4 batteries == 55 V

to read the batteries charge state, you would need to disconnect them 
from the charger(UPS) for about 4-6 hours before reading the voltage, 
this lets the surface charge dissipate.   After doing this, you should 
see 12.6-12.8V per 12v battery, or 50.4 to 51.2V for your stack of 4 * 
12V.  All these voltages assume 68-72F battery temperature.48V is 
nearly totally discharged