Re: Surge Suppressors

1997-05-13 Thread Rich Nute


Hi Ray:


In Norway, there is no guarantee that any particular outlet will
include a ground.  At NEMKO's main meeting room, the outlets do
not have a ground!

Consequently, in Norway, the condition of no ground is a NORMAL
condition, not a fault condition.  (Likewise, one-third of USA
homes have no ground, and all Japanese homes have no ground!)

So, Norway prohibits surge suppressors from being connected to
'earthed' parts of equipment.

Now that we've put that issue to bed, let's look at another 
issue:  Does a shock hazard exist because a surge suppressor 
is connected to grounded parts of equipment when the equipment
is not connected to ground?

Let's first define the surge.  Can we assume the "standard"
1.5 x 50 impulse?  If so, we are looking at a "surge" that
decays to 63% of its peak value in 50 microseconds.  It decays
to nearly zero in 250 microseconds.

We can further define the surge amplitude as not exceeding 1.5 
kV.  This is the dielectric withstand value of the primary-to-
ground insulation.  

Let's assume the surge is less than 1.5 kV peak for less than 
250 microseconds.  Is this hazardous?  

Can the human body feel this pulse?  Probably.

Can the human body be "frozen" to the product by this pulse?
No.  "Freezing" requires continuous current through the body.

Can the heart be caused to fibrillate by this pulse?  No.  
Fibrillation requires the current to extend for the full duration
of the T wave, i.e., more than 200 milliseconds.

Can the human body be burned by this pulse.  Yes.  A current of
70 mA peak or more can cause a burn at 1 cm square contacts with
the skin.  It is likely that the body impedance will be less 
than 1500/0.070 = 21,428 ohms during this pulse.

Note that protection against electric shock by the GFCI (aka
ELCB, RCCB, RCD) provides protection by limiting the duration of
the current through the body, not by limiting either the voltage
or the current.  When a GFCI operates, the subject gets the full
voltage and whatever current, but only for a short period of time.
In this way, it prevents fibrillation and "freezing" to the circuit.

So, I submit that the impulse, while it can be felt and may create
a burn, is not a shock hazard.

Now that we've looked at electric shock, let's look at whether the
impulse can appear on the grounded parts of the equipment when the
equipment is not grounded.

Ignoring the surge suppressors, and considering for a moment the
EMC filter capacitors, we have the following circuit:


   L1   <...-+-+
 | |
 | |
  ---+---  |
CY1|
  ---+----
 |   |   |  Rload
 +---+   |   |
 |   |   |   |
  ---+---|   -
CY2  | |
  ---+---| |
 |   | |
 |   | |
 |   | |
   L2 or N  <...-+---)-+
 |
   PE (non-existent) <...+ 
 |
 |  chassis
   -
--- 
 -  

If a surge appears between L1 and N, it will be divided in half
by the action of CY1 and CY2.  So, only one-half of the surge 
voltage will appear on the chassis.

If a surge appears common-mode between L1/N and PE, then the full
voltage will appear on the chassis because there is no current
path (because the ground is open).

We can replace CY1 and CY2 with surge suppressors.  If a surge 
appears between L1 and N, the surge suppressors will not be 
turned on unless the suppressor voltage ratings are less than 
one-half the applied voltage.  In this case, the circuit response 
to the surge remains the same as with the capacitors.  If the 
suppressors are not turned on, then the circuit still behaves the
same as with capacitors because of the capacitance of the 
suppressors.

If a surge appears common mode, the surge suppressors will not
be turned on because there is no connection of the chassis to any
other circuit.  The full surge voltage will appear on the chassis
just as with the capacitors.

I submit that:

1)  There is no electric shock injury hazard from a surge, but 
there may be a burn hazard.

2)  If the unit incorporates surge suppressors and is not grounded,
the hazard is no worse than without the surge suppressors.


Best regards fr

re: US Institute???

1997-05-13 Thread richard . payne
Mike:

By any chance could the U.S. Institute be ANSI - American National 
Standards Institute ?

Richard Payne
Tektronix Inc.
richard.pa...@tek.com


US Institute???

1997-05-13 Thread Mike Mertinooke
Hi;

Has anybody heard of such a thing as the "US Institute"???
I am not sure "US" refers to "United States of America." 

Somebody in South Africa just whacked my boss with "we only
buy products that satisfy the US Institute Protocols". Naturally,
he "managed" the situation by promising an immediate answer,
then dumping the whole thing on my head. *sigh* 

Any and all help will be greatly appreciated.

Cheers!
Mike Mertinooke

Mike Mertinooke  


Uncertainty calculations

1997-05-13 Thread Peter Phillips
I have recently started looking into the uncertainty associated with EMC
measurements, I have three documents published in the UK, NIS 80, 81 and
3003 which cover the topic, but I would like to see any other documents
or examples of calculations that are available.

Thanks in advance for your help

Peter.
-- 
***
Peter Phillips (p.phill...@ftel.co.uk)
Fujitsu Telecommunications Europe Limited
Birmingham B37 7YU
England
Telephone  +44 (0)121 717 6115
Fax +44 (0)121 717 6014/6018
***


Surge Suppressors

1997-05-13 Thread Ray_Russell
 Dear Friends,
 
 It seems that surge suppressers have been a topic of much discussion 
 lately. Must be all of the surge testing to EN61000 4-5! Well at least 
 that's what brought up our issue. 
 
 We have a piece of 230V equipment that failed the surge test, (safety 
 testing will be to EN61010). In reviewing how to install varistors, we 
 have run into some concerns. In Europe the 230V supply is 1 line, 1 
 neutral, and 1 ground wire.  A  varistor connected between line and 
 neutral will suppress a surge, as long as the neutral is grounded. 
 
 For the 230V US voltage, there is 2 hot lines and a ground. To make 
 the varistor effective, it seems that the varistor needs to be 
 connected to ground.
 
 However, I know of a Nordic deviation out of EN60950 that states: 
 
 (DK, FI, NO, SE). Transient protection components shall be installed 
 in such a way that insulation for protection against electric shock 
 will not be bridged. This means that transient protection components 
 must not be connected to protective earthed parts in pluggable 
 equipment or to other accessible parts. 
 
 I think the concern here is the possibility of not having a good 
 ground, and then if the over voltage is shunted to ground, the chassis 
 could become hot. 
 
 Is this a valid concern? It sounds like a "double fault" scenario to 
 me. If so, does anyone have an alternative solution?
 
 Thank you for your consideration.
 
 Happy is the man that finds wisdom and gets understanding!
 
 
 Ray Russell
 
 ray_russ...@leco.com


An Irrational Guide to Electrical Safety and the LVD.

1997-05-13 Thread Bill Lyons
Friends,

I couldn't resist sharing with you this emanation from the fertile brain 
of our good friend Gregg Kervill:


  An Irrational Guide to Electrical Safety and the LVD.

Release date April 1st.

The Low Voltage Directive

We will start by taking a top-level look at the Low Voltage
Directive (LVD) and some of its implications:

Considerations

The LVD has been about since 1973: therefore after more than 24
years we know all there is about it and can therefore safety ignore
it. Alternatively we may consider that there are already a
significant number of people killed by electrocution and that if our
product kills only a few more that it wouldn't make much difference
- statistically speaking - that is.

The CE Mark

Products within the scope of the LVD must be marked with the CE Mark.
The committed Europhile will have included the additional very tiny
letters "a-v-e-a-t" and "m-p-t-o-r" amongst the letters C and E to
produce that universal warning to all of his customers. (Viz. 
"Caveat Emptor"  = Let him beware.)  The advantage of using a "dead"
language for warnings is that will be universally unrecognised by
the very people that they are intended to help - but will favour the
elite and educated and hence protect our own "Kith and Kin".

The Responsible Person

Always appoint the least technically competent employee for the task
of Responsible Person. 

It is equally important to ensure that they can be easily
intimidated; will help suppress concerns that a potential
non-compliant product has been in production for the last 15 years;
and that they will continue to sign Declarations of Conformity
despite a series of memos and reports for the quality department and
other conscientious employees. 

The "Data File"

The "data file", legally required by the LVD is no problem to the
seriously minded.   

True the requirements to hold information that clearly (and
publicly) identifies non-compliances against European Harmonised
standards could be seen as a 'bit negative' (in  marketing terms)
but a careful review of the many hundred of harmonised standards
should yield a few to which we can claim compliance - even if they
relate to the pulp content of our user manuals and not to the
product itself.

It is well known that there is no need to review, test or consider
any safety features of products outside the scope of the LVD - as it
is perfectly reasonable to place potentially dangerous products on
the market: provided that they are not CE Marked. 

Being Sued

Only the 'wimps' worry that they may be sued by people injured by
their products. The "real-men" take confidence in their design
capabilities. If the product is not compromised to pander to the
requirements of product safety - life is beautifully simple: there
will be no survivors and therefore no-one to sue. Hence there is no
problem. Quod Erat Demonstrandum!   Furthermore the lack of
customers is nothing to do with engineering and the blame can be
placed squarely at the door of the marketing and sales departments.

A Look in Detail

Next we will take a look at some of the more detailed requirements
contained in some of the widely used Harmonised Standards - the
Eight Principles relating to Hazards. 

Knowledge: 

Avoid training and employ only junior staff - this will ensure that
product safety is NOT consider early in the design and therefore
will save huge amounts of money.  Having spent the entire budget we
can then bully the Responsible Person (see above) into signing the
release documentation.

Electric Shock 

Committing the purchasing department to buying critical components
(e.g. power supplies) that carry an agency approval is restrictive.
The purchasing department must be given total freedom to buy from
the cheapest - third-world sources. We all know that the final
selling price is the MOST important thing to achieve.

Energy Hazards

It has been scientifically proven that subjecting the Operator to
circuits delivering more than 8 Amps, 240 VA, 60 Volts or 20 Joules 
keeps them more vigilant and they work harder.  True there may be a
few deaths or injuries caused by these energies but these are
usually restricted to the old, ill or infirm. It's nothing to do
with us or with our product.

If we are really clever and have a 48 Volt supply from 200 kg of
lead acid batteries we may be able to get our customer to create the
hazard. All we do is to over-emphasise the fact that the operator
outputs are Safety Extra Low Voltage (SELV).  Most of our clients
will be unaware that only Safety Extra Low Voltage Energy Limited
(SELVEL) may be contacted by the operator: and it shouldn't be long
before someone discovers that the fault current in these external
circuits could be more than 2,000 Amps.

Fire

Use the thinnest section of plastic that it is possible to mould.
Make sure that the purchasing department specify only the colour of
the plastic - this will usually guarantee that the cheapest - most
flammable materials are sourced. Avoid meta

machinery directive forum / list server

1997-05-13 Thread mvaldman
Hello everyone,

does anyone know about a an information source/list server specialising in the 
machinery 
directive?

Do not be offended, but I did receive a considerable amount of information re 
ergonomics 
from a (non emc-pstc) guy who works with the machinery directive. No one 
referred to this 
info on the "emc-pstc".

I will prepare a summary ASAP of course.

thanks
-
Name: moshe valdman
E-mail: mvald...@netvision.net.il
Phone: 052-941200, 03-5496369
List-Post: emc-pstc@listserv.ieee.org
Date: 13/05/97
Time: 0:00:51
You are most welcome to visit my homepage at:

http://www.geocities.com/CapeCanaveral/5233/
-