Hi Tim.

You wrote:
<If screened mains cable is used, then surly it acts like a coax (a poor
one possibly) and transfers the energy, contained within, to a point
where the cables are not shielded. This would probably be at the mains
wall socket - where the energy could (would?) then radiate! If the
intention is not to cause interference to radiocommunications etc. then
how has the screened mains cable helped? The test might seem OK but how
is "due diligence" served?>

My problems have been that filters are often guilty of resonances at
particular frequencies, providing substantial gain rather than attenuation.
 With 'white noise'  things like phase angle controllers in the box, these
filters put (in one instance) 32MHz out on to the mains cable, which
radiated beautifully.  The screen was sufficient to drop those emissions by
about 15dB, thereby bringing it back into compliance.  The transmission
line characteristics of screened three core cable are very poor, and the
conducted emissions of the 32MHz past the mains lead were clearly very much
reduced by the inductance/capacitance of the cable, in that the -15dB
results were perceived.  The radiated emissions included those from the
mains supply to the equipment.  The mains cable on this thing was 3 metres
long, and made up from component's, not moulded.  The screen was grounded
at the Supply end.

Interesting stuff...

Chris Dupres
Surrey, UK.