Earth Leakage Measurement Circuit per EN 60950

1999-11-25 Thread Peter E. Perkins


Duncan and PSNet

To build the network described in 950 is not trivial if one wishes
to meet all the requirements to achieve adequate performance over the
specified frequency range, in the expected environment in which it must
operate.  

Because this is not a trivial matter, IEC 60990 'Measurement of
Touch Current and Protective Conductor Current' has an entire section
devoted to measuring instruments and another covering calibration to show
adequacy.  If you wish to build such an instrument, I recommend that you
get this standard.  You can order it directly from the IEC website in
Geneva.  

There is one commercial instrument which meets the requirements
described in 950, the Simpson model 228 Leakage Current meter.  Look at
their website.  Incidentally, I use this instrument in my own work.  There
may be others available.  

If you really want to continue to build your own instrument, but
need some additional help, I can recommend an experienced measurement
equipment consultant who would probably help you.  Contact me privately for
this.  

Good luck in your preparation for this project.  

:>) br, Pete Perkins
Convenor, IEC TC74/WG5/IEC 60990

- - - - -

Peter E Perkins
Principal Product Safety Consultant
Tigard, ORe  97281-3427

+1/503/452-1201 phone/fax

p.perk...@ieee.org  email

visit our website:

http://ourworld.compuserve.com/homepages/peperkins

- - - - -

-
This message is coming from the emc-pstc discussion list.
To cancel your subscription, send mail to majord...@ieee.org
with the single line: "unsubscribe emc-pstc" (without the
quotes).  For help, send mail to ed.pr...@cubic.com,
jim_bac...@monarch.com, ri...@sdd.hp.com, or
roger.volgst...@compaq.com (the list administrators).



Re: Copy of: D of C - Who Signs?

1999-11-25 Thread Ralph Cameron

Marin:

Barring non compliant products from entry soon makes its point rather than
trying to untangle the legal liability in such rare cases.

Ralph Cameron
Independant Consulting and EMC suppression in consumer electronics
(after sale)


- Original Message -
From: Martin Green 
To: 'Allan G. Carr' 
Cc: 'Price, Ed' ; 
Sent: Thursday, November 25, 1999 6:05 AM
Subject: RE: Copy of: D of C - Who Signs?


>
> Alan,
>
> As far as the quotation is concerned, I would refer you to the words in
Reg.
> 40(2)(c), Erg 57(2)(c), Erg 70(2)(c) for clauses detailing who signs the
> DoC.  Under the UK regulations it will, as I said in my email, "be signed
by
> or on behalf of the manufacturer or his authorised representative and
> identify that signatory"
>
> As far as going to court is concerned, I too thought that action would be
> taken against the responsible person, but when I discussed this with both
> the DTI and some lawyers they said that as the offence would be "placing
on
> the market a product that did not meet the protection requirements"  - or
> similar words, and it would be a charge raised in a UK court, then it is
the
> person selling it that is charged.  Apparently, there is no cross border
> joint jurisdiction in the EU for CE marking offences.  I understand that
the
> UK authorities would inform the EU commission and they in turn would
inform
> the authorities in Belgium.  The Belgium authorities may then choose to
> investigate the offence to see if an offence had been committed in
Belgium,
> under Belgium law.  However, there is no doubt that the UK courts could
not
> take action against a citizen in Belgium for this type of offence.
>
> Whether the Belgium authorities would be able to charge a Belgium citizen
> with an offence committed in the UK is open the question.  It is like
being
> charged for speeding in Germany and having a UK court hear the case. It
does
> not work.  As many will know to their cost (including me!), if you commit
a
> motoring offence in Germany then you can pay a fine either on the spot or
in
> court.  Usually it on the spot - even if you are British!  The UK courts
do
> not hear motoring offences committed in Germany.
>
> Regards
>
> Martin
> > -Original Message-
> > From: Allan G. Carr [SMTP:e...@acarr.demon.co.uk]
> > Sent: 25 November 1999 13:43
> > To: Martin Green
> > Cc: 'Price, Ed'; 'emc-p...@ieee.org'
> > Subject: Re: Copy of: D of C - Who Signs?
> >
> > Martin
> >
> > Thanks for the comprehensive reply to my post.
> >
> > I have the following comments:-
> >
> > >The UK EMC regulations do not say
> > >the DoC is signed by the responsible person.  They say the DoC must be
> > >"signed by or on behalf of the manufacturer or his authorised
> > representative
> > >and identify that signatory".
> >
> > Sorry to be pedantic but the UK Statutory Instrument 1992 No.2372 does
> > not contain the above quote.   This quote is from EC EMC Guidelines
> > which therefore clarify the issue.
> >
> >
> > >The question always arises as to who ends up in court.  As an example,
if
> > >the DoC is signed in the USA, for a product made in Mexico, being sold
by
> > >distributors in 10 of the member states in the EU, with the authorised
> > rep
> > >in Belgium acting as the responsible person and there is a court case
for
> > >infringement of the UK EMC regulations, who ends up in court?  The
action
> > is
> > >taken in UK by the Trading Standards Officers against the person
placing
> > the
> > >product on the market in the UK.  The answer is the distributor.  The
UK
> > has
> > >no jurisdiction over the authorised rep in Belgium or the manufacturer
> > >outside the EU.
> >
> > UK Trading Standards tell me that in the above example the prosecution
> > would be handed over to the EC country of residence of "the responsible
> > person" who keeps the documentation - in this case Belgium.
> >
> > However the UK distributor could be in the firing line if UK Trading
> > Standards were not happy with the result.
> >
> >
> >
> > Thanks again for your excellent response
> > Allan
> > 
> >
> > In message , Martin Green
> >  writes
> > >It is always interesting to read the "legal" interpretation of these
> > >documents.  I now understand why lawyers make so much money.
> > >
> > >If you have the staying power you might find this or interest/value,
> > >otherwise hit the delete button!
> > >
> > >The interpretation below is incorrect.  The UK EMC regulations do not
say
> > >the DoC is signed by the responsible person.  They say the DoC must be
> > >"signed by or on behalf of the manufacturer or his authorised
> > representative
> > >and identify that signatory".
> > >
> > >They also say the that DoC must give the name and address of the
> > responsible
> > >person and where that person is not the manufacturer, of the
> > manufacturer.
> > >
> > >For those who read this stuff and are not used to the arcane legal
words
> > >inside UK Statutory Ins

Re: Humidity Test

1999-11-25 Thread Richard Haynes

Bill,
Check out ASTM A380 and ASTM A967, 100% humity at 38 C. http://www.astm.org
.
Richard Haynes
609-497-4584



-Original Message-
From: Matthew Meehan 
To: Jacowleff, Bill 
Cc: emc-p...@ieee.org 
List-Post: emc-pstc@listserv.ieee.org
Date: Thursday, November 11, 1999 4:00 AM
Subject: Re: Humidity Test


>
>> Can anyone steer me to an appropriate standard that would specify
>> Humidity tests for a heavy industrial product?
>>
>> Best Regards,
>>
>> Bill Jacowleff
>
>Bill,
>"Appropriate" covers a lot of ground.  Especially since you didn't specify
>your market (country, equipment category (e.g. semiconductor machinery)).
>You also didn't mention if you are interested in compliance - or if you're
>just looking for a little light reading.
>If you're looking for international standards try searching:
>
>http://www.iec.ch/
>
>Since you have not specified I'll just stick with the general standards
>(there may be a more suitable product family standard).
>
>IEC 60204-1 (1997-10)
>Electrical equipment of industrial machines - Part 1: General requirements
>Provides a requirement stating that machines must be capable of correct
>operation at 40 degress C (humidity <=50%).
>This requirement can be altered however by agreement with your customer
(see
>Appendix B).
>
>You might also consider the following standards:
>
>IEC 60068-2-56 - Ed. 1.0 - Bilingual
>Title: Environmental testing - Part 2: Tests. Test Cb: Damp heat, steady
>state, primarily for equipment
>Publication date: 1988-12
>TC: 104 (ENVIRONMENTAL CONDITIONS, CLASSIFICATION AND METHODS OF TEST)
>Pages: 15
>Price: 36.00 CHF (price code : H).
>Abstract: Determines the suitability of electrotechnical products,
>principally equipment, for use and storage under conditions of high
>humidity.
>You would also need the IEC 60068-1 as well.   I imagine a few different
>tests plans are described in the standard.
>
>IEC GUIDE 106 (1996-07)  Ed. 2.0  CHF 27.00 17 pages
>Guide for specifying environmental conditions for equipment performance
>rating
>This standard is listed in the bibliography of the IEC 60204
>
>Hope this helps.
>Regards,
>Matt
>
>
>
>-
>This message is coming from the emc-pstc discussion list.
>To cancel your subscription, send mail to majord...@ieee.org
>with the single line: "unsubscribe emc-pstc" (without the
>quotes).  For help, send mail to ed.pr...@cubic.com,
>jim_bac...@monarch.com, ri...@sdd.hp.com, or
>roger.volgst...@compaq.com (the list administrators).
>
>
>



-
This message is coming from the emc-pstc discussion list.
To cancel your subscription, send mail to majord...@ieee.org
with the single line: "unsubscribe emc-pstc" (without the
quotes).  For help, send mail to ed.pr...@cubic.com,
jim_bac...@monarch.com, ri...@sdd.hp.com, or
roger.volgst...@compaq.com (the list administrators).



EMC simulation software

1999-11-25 Thread Tribellini Giovanni

NOTE: This mail is for the subscribers of EMC-PSTC mailing list that aren't
TREG subscribers.
I have already mailed this mail to TREG group, and I want to thank Rusty,
Jan, and Bechard above all, for their reply.

Hello to EMC-PSTC group!

I have the following info request:

Who can suggest me a reliable EMC simulation tool for  the design of PCB for
mobile telecom equipments, predicting emissions and, possibly, immunity
problems?
In your opinion, is this software really useful for identify and correct EMC
problems before doing lab tests according standards?

Thank you for your attention

Giovanni Tribellini

-
This message is coming from the emc-pstc discussion list.
To cancel your subscription, send mail to majord...@ieee.org
with the single line: "unsubscribe emc-pstc" (without the
quotes).  For help, send mail to ed.pr...@cubic.com,
jim_bac...@monarch.com, ri...@sdd.hp.com, or
roger.volgst...@compaq.com (the list administrators).



Re: Article to UL

1999-11-25 Thread Ralph Cameron

I woudn't take the Washington Post articel seriously but unfortunately in
the struggle for the media to retain readership they act as interpreters of
things they don't fully understand and in the course of publishing spread
technical inaccuracies.  The article is only an opinion, albeit one sided.
I would agree with Peter that not juch is to be gained by negative bashing.

Manufacturers should voluntarily ascribe to saftey as an ethical and moral
obligation and promote the profession of responsible engineering.  The same
should apply to EMC immunity in products.  I'd like to see the Washington
Post write about that.  I could help them.

Keep up the objective comments, they lead to progress.

Ralph Cameron

Independant EMC Consulting for suppression of consumer products lacking EMC.
(After sale).


- Original Message -
From: 
To: 
Sent: Wednesday, November 24, 1999 8:08 PM
Subject: Article to UL


>
> Hello group,
>
> It seems to me that the article in Washington Post, was written by someone
> who really had not done their homework. It sounded as the article was
> criticizing UL for not doing proper testing or not being able to write
their
> standards adequately. Like most of the people in the group, I am certainly
> not a fan of UL for various reasons that are outside the scope of this
> particular subject, but one has to remember that almost majority of the
> standards are written with manufacturers directly involved during the
> generation of the standard. Obviously those of us who are being
represented
> in various standard committee we who are responsible for writing the
> standard, try to influence the standard as much as we can in our industry
> favor and test houses such as UL, CSA , BSI, more or less go along with
it.
> As for testing is concerned, all UL engineers as well as their
counterparts
> in other test houses only test the product to the clauses of the standard
and
> they are not allowed to go any further. On top of that, the way that any
of
> these standard are written it is widely open to interpretation so we as
test
> engineers always try to argue with the test house engineer to try to avoid
> any failure. Another point to bear in mind is that the test house
engineers
> are only human like the rest of us and can make mistake or even overlook
at
> some points. Last but not least, most of us have seen a certified product
> been slightly modified/altered by someone in our company for an unknown
> reason and still bears the safety mark without even informing any of the
test
> houses concerned . So I believe we should look at the root casue of the
> problem and try to improve the situation by
> (a) be honest with the test houses during testing.
> (b) by trying to encourage our designers to make the product almost fool
> proof.
> © do addition in-house testing that exceeds the requirements of the
standard
> (d) by being a truly responsible manufacturer.
>
> Thanks
> Peter
>
> -
> This message is coming from the emc-pstc discussion list.
> To cancel your subscription, send mail to majord...@ieee.org
> with the single line: "unsubscribe emc-pstc" (without the
> quotes).  For help, send mail to ed.pr...@cubic.com,
> jim_bac...@monarch.com, ri...@sdd.hp.com, or
> roger.volgst...@compaq.com (the list administrators).
>
>
>


-
This message is coming from the emc-pstc discussion list.
To cancel your subscription, send mail to majord...@ieee.org
with the single line: "unsubscribe emc-pstc" (without the
quotes).  For help, send mail to ed.pr...@cubic.com,
jim_bac...@monarch.com, ri...@sdd.hp.com, or
roger.volgst...@compaq.com (the list administrators).



RE: Copy of: D of C - Who Signs?

1999-11-25 Thread Martin Green

Alan,

As far as the quotation is concerned, I would refer you to the words in Reg.
40(2)(c), Erg 57(2)(c), Erg 70(2)(c) for clauses detailing who signs the
DoC.  Under the UK regulations it will, as I said in my email, "be signed by
or on behalf of the manufacturer or his authorised representative and
identify that signatory"  

As far as going to court is concerned, I too thought that action would be
taken against the responsible person, but when I discussed this with both
the DTI and some lawyers they said that as the offence would be "placing on
the market a product that did not meet the protection requirements"  - or
similar words, and it would be a charge raised in a UK court, then it is the
person selling it that is charged.  Apparently, there is no cross border
joint jurisdiction in the EU for CE marking offences.  I understand that the
UK authorities would inform the EU commission and they in turn would inform
the authorities in Belgium.  The Belgium authorities may then choose to
investigate the offence to see if an offence had been committed in Belgium,
under Belgium law.  However, there is no doubt that the UK courts could not
take action against a citizen in Belgium for this type of offence.

Whether the Belgium authorities would be able to charge a Belgium citizen
with an offence committed in the UK is open the question.  It is like being
charged for speeding in Germany and having a UK court hear the case. It does
not work.  As many will know to their cost (including me!), if you commit a
motoring offence in Germany then you can pay a fine either on the spot or in
court.  Usually it on the spot - even if you are British!  The UK courts do
not hear motoring offences committed in Germany.

Regards

Martin
> -Original Message-
> From: Allan G. Carr [SMTP:e...@acarr.demon.co.uk]
> Sent: 25 November 1999 13:43
> To:   Martin Green
> Cc:   'Price, Ed'; 'emc-p...@ieee.org'
> Subject:  Re: Copy of: D of C - Who Signs?
> 
> Martin
> 
> Thanks for the comprehensive reply to my post.
> 
> I have the following comments:-
> 
> >The UK EMC regulations do not say
> >the DoC is signed by the responsible person.  They say the DoC must be
> >"signed by or on behalf of the manufacturer or his authorised
> representative
> >and identify that signatory".
> 
> Sorry to be pedantic but the UK Statutory Instrument 1992 No.2372 does
> not contain the above quote.   This quote is from EC EMC Guidelines
> which therefore clarify the issue.
> 
> 
> >The question always arises as to who ends up in court.  As an example, if
> >the DoC is signed in the USA, for a product made in Mexico, being sold by
> >distributors in 10 of the member states in the EU, with the authorised
> rep
> >in Belgium acting as the responsible person and there is a court case for
> >infringement of the UK EMC regulations, who ends up in court?  The action
> is
> >taken in UK by the Trading Standards Officers against the person placing
> the
> >product on the market in the UK.  The answer is the distributor.  The UK
> has
> >no jurisdiction over the authorised rep in Belgium or the manufacturer
> >outside the EU.
> 
> UK Trading Standards tell me that in the above example the prosecution
> would be handed over to the EC country of residence of "the responsible
> person" who keeps the documentation - in this case Belgium.
> 
> However the UK distributor could be in the firing line if UK Trading
> Standards were not happy with the result.
> 
> 
> 
> Thanks again for your excellent response
> Allan
> 
> 
> In message , Martin Green
>  writes
> >It is always interesting to read the "legal" interpretation of these
> >documents.  I now understand why lawyers make so much money.  
> >
> >If you have the staying power you might find this or interest/value,
> >otherwise hit the delete button!
> >
> >The interpretation below is incorrect.  The UK EMC regulations do not say
> >the DoC is signed by the responsible person.  They say the DoC must be
> >"signed by or on behalf of the manufacturer or his authorised
> representative
> >and identify that signatory".
> >
> >They also say the that DoC must give the name and address of the
> responsible
> >person and where that person is not the manufacturer, of the
> manufacturer.  
> >
> >For those who read this stuff and are not used to the arcane legal words
> >inside UK Statutory Instruments this is often difficult to understand.
> The
> >problem is no one else in the EU gives guidance to the manufacturers who
> are
> >trying to CE mark their equipment correctly.  The guidance documents from
> >the EU commission are often confusing as well.  So I have tried to
> explain
> >the "legal" interpretation as understood by some very senior lawyers in
> UK
> >with whom we have dealings.  
> >
> >The way the EU tends to consider this is that the "responsible person" is
> >the person (living body) who issues the DoC and holds the certification
> >documentation, or evidence

Re: Copy of: D of C - Who Signs?

1999-11-25 Thread Allan G. Carr

Martin

Thanks for the comprehensive reply to my post.

I have the following comments:-

>The UK EMC regulations do not say
>the DoC is signed by the responsible person.  They say the DoC must be
>"signed by or on behalf of the manufacturer or his authorised representative
>and identify that signatory".

Sorry to be pedantic but the UK Statutory Instrument 1992 No.2372 does
not contain the above quote.   This quote is from EC EMC Guidelines
which therefore clarify the issue.


>The question always arises as to who ends up in court.  As an example, if
>the DoC is signed in the USA, for a product made in Mexico, being sold by
>distributors in 10 of the member states in the EU, with the authorised rep
>in Belgium acting as the responsible person and there is a court case for
>infringement of the UK EMC regulations, who ends up in court?  The action is
>taken in UK by the Trading Standards Officers against the person placing the
>product on the market in the UK.  The answer is the distributor.  The UK has
>no jurisdiction over the authorised rep in Belgium or the manufacturer
>outside the EU.

UK Trading Standards tell me that in the above example the prosecution
would be handed over to the EC country of residence of "the responsible
person" who keeps the documentation - in this case Belgium.

However the UK distributor could be in the firing line if UK Trading
Standards were not happy with the result.



Thanks again for your excellent response
Allan


In message , Martin Green
 writes
>It is always interesting to read the "legal" interpretation of these
>documents.  I now understand why lawyers make so much money.  
>
>If you have the staying power you might find this or interest/value,
>otherwise hit the delete button!
>
>The interpretation below is incorrect.  The UK EMC regulations do not say
>the DoC is signed by the responsible person.  They say the DoC must be
>"signed by or on behalf of the manufacturer or his authorised representative
>and identify that signatory".
>
>They also say the that DoC must give the name and address of the responsible
>person and where that person is not the manufacturer, of the manufacturer.  
>
>For those who read this stuff and are not used to the arcane legal words
>inside UK Statutory Instruments this is often difficult to understand.  The
>problem is no one else in the EU gives guidance to the manufacturers who are
>trying to CE mark their equipment correctly.  The guidance documents from
>the EU commission are often confusing as well.  So I have tried to explain
>the "legal" interpretation as understood by some very senior lawyers in UK
>with whom we have dealings.  
>
>The way the EU tends to consider this is that the "responsible person" is
>the person (living body) who issues the DoC and holds the certification
>documentation, or evidence of conformity, in the EU (test reports/TCF/EC
>Type examination certificate etc.)
>
>This is not necessarily the person who signs the DoC.  The person signing
>the DoC is the person who legally "binds" the manufacturer to the claims in
>the DoC - as with a contract signatory.
>
>As the only authorities who may want to see the documentation are in the EU,
>the responsible person must be in the EU as well.  If the manufacturer is in
>the EU he does not need an authorised rep (although he may appoint one) and
>by default he would be the responsible person.
>
>Therefore you can think of it rather in the same way as signing a contract
>for buying a house.  The person who is legally purchasing the house signs
>the contract.  The contract can then be given to a third party such as a
>lawyer for safe keeping and making available to anyone who legally needs to
>see it.  Of course if the house, new owner and lawyer all reside in the same
>town, why give the contract to the lawyer to keep?  
>
>So the basic rules are:
>
>1.  If the manufacturer is located outside the EU, (including Switzerland)
>then he must appoint an authorised representative to act on his behalf.  
>
>2.  The manufacturer or his authorised representative in the EU holds the
>documentation and issues the DoC and is therefore the responsible person.
>If the manufacturer does not appoint an authorised representative, or the
>authorised representative is located outside the EU (why have one!) the
>default is that the responsible person becomes the person who supplies
>(places the product on the market) the apparatus.
>
>3.  The person who signs the DoC can be anyone who is authorised by the
>manufacturer to do so.  Usually it is a manager or officer, but that person
>is legally binding the manufacturer to the claims in the DoC, so it must be
>some one authorised to do so.  
>
>Naturally the EU messes things up a bit because the machinery directive
>allows the responsible person to be outside the EU.  But there are very
>special provisions associated with that.  The medical devices directive
>requires the appointment of an authorised re

RE: Copy of: D of C - Who Signs?

1999-11-25 Thread Martin Green

It is always interesting to read the "legal" interpretation of these
documents.  I now understand why lawyers make so much money.  

If you have the staying power you might find this or interest/value,
otherwise hit the delete button!

The interpretation below is incorrect.  The UK EMC regulations do not say
the DoC is signed by the responsible person.  They say the DoC must be
"signed by or on behalf of the manufacturer or his authorised representative
and identify that signatory".

They also say the that DoC must give the name and address of the responsible
person and where that person is not the manufacturer, of the manufacturer.  

For those who read this stuff and are not used to the arcane legal words
inside UK Statutory Instruments this is often difficult to understand.  The
problem is no one else in the EU gives guidance to the manufacturers who are
trying to CE mark their equipment correctly.  The guidance documents from
the EU commission are often confusing as well.  So I have tried to explain
the "legal" interpretation as understood by some very senior lawyers in UK
with whom we have dealings.  

The way the EU tends to consider this is that the "responsible person" is
the person (living body) who issues the DoC and holds the certification
documentation, or evidence of conformity, in the EU (test reports/TCF/EC
Type examination certificate etc.)

This is not necessarily the person who signs the DoC.  The person signing
the DoC is the person who legally "binds" the manufacturer to the claims in
the DoC - as with a contract signatory.

As the only authorities who may want to see the documentation are in the EU,
the responsible person must be in the EU as well.  If the manufacturer is in
the EU he does not need an authorised rep (although he may appoint one) and
by default he would be the responsible person.

Therefore you can think of it rather in the same way as signing a contract
for buying a house.  The person who is legally purchasing the house signs
the contract.  The contract can then be given to a third party such as a
lawyer for safe keeping and making available to anyone who legally needs to
see it.  Of course if the house, new owner and lawyer all reside in the same
town, why give the contract to the lawyer to keep?  

So the basic rules are:

1.  If the manufacturer is located outside the EU, (including Switzerland)
then he must appoint an authorised representative to act on his behalf.  

2.  The manufacturer or his authorised representative in the EU holds the
documentation and issues the DoC and is therefore the responsible person.
If the manufacturer does not appoint an authorised representative, or the
authorised representative is located outside the EU (why have one!) the
default is that the responsible person becomes the person who supplies
(places the product on the market) the apparatus.

3.  The person who signs the DoC can be anyone who is authorised by the
manufacturer to do so.  Usually it is a manager or officer, but that person
is legally binding the manufacturer to the claims in the DoC, so it must be
some one authorised to do so.  

Naturally the EU messes things up a bit because the machinery directive
allows the responsible person to be outside the EU.  But there are very
special provisions associated with that.  The medical devices directive
requires the appointment of an authorised rep in the EU to register Class I
products and some other directives do not mention the need for either an
authorised rep or a responsible person.  It is all very confusing, but the
general recommendations are:

1.  If the manufacturer is outside the EU then appoint an authorised rep to
act on your behalf.  (This person must be inside the EU to hold the
documentation).
2.  Formally appoint the authorised rep to be your responsible person and
hold the technical documentation, hold a copy of the DoC, and issue the DoC
to anyone who needs it.
3.  You can, if you want, have your authorised rep (legally appointed) sign
the DoC.  He is then empowered to bind your company to the claims in the
DoC.  Alternatively you can sign the DoC yourself.  As the DoC is a legal
document then it must be signed by someone who is authorised to do so - as
said before.  If that person is no longer alive or with the company,
contract law does not negate the historical validity of contracts because a
person is no longer living, or doing something whereby he is no longer
authorised to sign documents.  Therefore the DoC remains valid for as long
as the claims are valid.  The signatory signed it on behalf of the company,
not as an individual.  If a new DoC is required, because the equipment has
been modified you cannot get the original person to sign it again because
his signed the first version.  Besides digging up the dead is illegal in the
EU!  Therefore the new DoC is signed to bind the manufacturer and that then
does not require resigning - unless it is reissued.

The question always arises as to who ends up in 

Re: UL in Washington Post - Seagull

1999-11-25 Thread georgea

Several observations on the article and subsequent comments...

Seagull analogy--Isn't this description true of the media at
large in all forms?  I thought that was basically how they sold
their wares and made a profit.

Once upon a time, it might have been appropriate to bash on UL,
even if unwarranted.  After all, they had the monopoly on both
the standards and certifications for the U.S.  Unfortunately,
this history is what makes UL an excellent scapegoat for the
article.  However, now for ITE the UL 1950 standard is basically
harmonized with the international IEC 60950.  Plus there are many
competitors via the NRTL process who can examine and issue the
certifications.  Of course, many of the standards are still UL,
hence they cannot dodge this bullet entirely.

My point is that the indictment is not necessarily just against
UL, but against some international standards and all agencies
authorized to certify against these standards within the U.S.

No matter how much we manufacturers complain about UL and other
certification agencies for their slowness, costs, and differing
interpretive spins on the standards, who really wants a govern-
ment agency to assume these duties?  I believe there are many
documented cases to illustrate that the FDA, FAA, and so on do
not necessarily cater to the best interests of the citizenry, but
to lobbyists with the deepest pockets.  Ever watch 20/20 or
Dateline?

I also note that no ITE products were mentioned in the article.
To my knowledge, the only ITE products recalled in recent times
(or ever?) with the "help" of the CPSC were several AC adapters
shipped with ITE products they were to power.

George Alspaugh



-
This message is coming from the emc-pstc discussion list.
To cancel your subscription, send mail to majord...@ieee.org
with the single line: "unsubscribe emc-pstc" (without the
quotes).  For help, send mail to ed.pr...@cubic.com,
jim_bac...@monarch.com, ri...@sdd.hp.com, or
roger.volgst...@compaq.com (the list administrators).



Article to UL

1999-11-25 Thread Peterhays

Hello group,

It seems to me that the article in Washington Post, was written by someone 
who really had not done their homework. It sounded as the article was 
criticizing UL for not doing proper testing or not being able to write their 
standards adequately. Like most of the people in the group, I am certainly 
not a fan of UL for various reasons that are outside the scope of this 
particular subject, but one has to remember that almost majority of the 
standards are written with manufacturers directly involved during the 
generation of the standard. Obviously those of us who are being represented 
in various standard committee we who are responsible for writing the 
standard, try to influence the standard as much as we can in our industry 
favor and test houses such as UL, CSA , BSI, more or less go along with it. 
As for testing is concerned, all UL engineers as well as their counterparts 
in other test houses only test the product to the clauses of the standard and 
they are not allowed to go any further. On top of that, the way that any of 
these standard are written it is widely open to interpretation so we as test 
engineers always try to argue with the test house engineer to try to avoid 
any failure. Another point to bear in mind is that the test house engineers 
are only human like the rest of us and can make mistake or even overlook at 
some points. Last but not least, most of us have seen a certified product 
been slightly modified/altered by someone in our company for an unknown 
reason and still bears the safety mark without even informing any of the test 
houses concerned . So I believe we should look at the root casue of the 
problem and try to improve the situation by 
(a) be honest with the test houses during testing. 
(b) by trying to encourage our designers to make the product almost fool 
proof. 
© do addition in-house testing that exceeds the requirements of the standard 
(d) by being a truly responsible manufacturer.

Thanks
Peter

-
This message is coming from the emc-pstc discussion list.
To cancel your subscription, send mail to majord...@ieee.org
with the single line: "unsubscribe emc-pstc" (without the
quotes).  For help, send mail to ed.pr...@cubic.com,
jim_bac...@monarch.com, ri...@sdd.hp.com, or
roger.volgst...@compaq.com (the list administrators).



re: Article to UL

1999-11-25 Thread Frank West

As my UL friends are always quick to point out, they
are not-for-profit, not non-profit.  Not being expert,
I assume there is some subtle difference that is lots
on the rest of us.

A more general question is, why is does UL continue to
enjoy special consideration when what they are doing
is not unique?

Regards,

Frank West
Sr. Engineer
TUV Rheinland NA

--- Barry Ma  wrote:
> 
> Chaz, Why do they call UL a non-profit organization?
> Barry
> Anritsu Co.
> 
> From: "Grasso, Charles (Chaz)"
> , on 11/24/99 1:23
> PM:
> 
> Forgive a jaded old man but two things jumped out at
> me when I read the article.
> 
> 1. "In many other countries, standards are set or
> approved by a government entity with industry
> involvement. U.S. safety standards, on the other
> hand, are set primarily by private industry - either
> in independent labs such as UL or by industry
> associations or organizations. The CPSC, an
> independent regulatory agency charged with
> protecting consumers from hazardous products,
> imposes federal regulations only when it believes
> industry's voluntary efforts are insufficient. "
> 
> Oh Boy. Lets see look like UL is ripe for a
> government takeover to me!!
> 
> 2. Many experts interviewed contend that UL's recent
> problems can be traced to the way the company is
> organized and funded - with more than nine-tenths of
> its revenue coming from companies for testing
> products. UL also sets industry safety standards -
> which it then measures products against - but does
> not 
> charge for that. Lets see - if we reorganize and -
> more importantly - change the funding (a euphemism
> for taxation) then we'll all be safer!!
> 
> Sorry - Just could not resist..
> 
> 
>
__
> Open your mind.  Close your wallet.
> Free Internet Access from AltaVista.
> http://www.altavista.com
> 
> 
> -
> This message is coming from the emc-pstc discussion
> list.
> To cancel your subscription, send mail to
> majord...@ieee.org
> with the single line: "unsubscribe emc-pstc"
> (without the
> quotes).  For help, send mail to ed.pr...@cubic.com,
> jim_bac...@monarch.com, ri...@sdd.hp.com, or
> roger.volgst...@compaq.com (the list
> administrators).
> 
> 
> 


=
Frank West
Senior Engineer
TUV Rheinland of North America
NW/Portland OR Office
__
Do You Yahoo!?
Thousands of Stores.  Millions of Products.  All in one place.
Yahoo! Shopping: http://shopping.yahoo.com

-
This message is coming from the emc-pstc discussion list.
To cancel your subscription, send mail to majord...@ieee.org
with the single line: "unsubscribe emc-pstc" (without the
quotes).  For help, send mail to ed.pr...@cubic.com,
jim_bac...@monarch.com, ri...@sdd.hp.com, or
roger.volgst...@compaq.com (the list administrators).



EN60950 3rd Edition?

1999-11-25 Thread Kevin Richardson

Hi Ron,

For Australia and New Zealand, AS/NZS 3260 closed it's public comment
period on 7 Nov 99.  Probably to be published early 2000.  Also it will
probably be numbered AS/NZS 60950 rather than than 3260.

Best regards,
Kevin
>  
> 
> Hello out there,
> 
> I have some questions regarding the adoption if IEC60950 3rd Edition.
> 
> 1) Now that IEC60950 3rd Ed. is now out and UL60950 3rd Ed. is out for
> review, when will EN60950 catch up and follow IEC60950 3rd Ed.?
> 
> 2) And for that matter, how about AS/NZ 3260 and other 950 derivatives?
> 
> 3) When will the CB Scheme adopt IEC60950 3rd Ed.?
> 
> I'm trying to get a time frame when (if ever) the respective standards
will
> be upgraded. And, I'm sure the group would be interested to know more.
> 
> Anyone out there who has their ear into what's happening on these
> questions?
> 
> Best regards,
> Ron Pickard
> rpick...@hypercom.com
> 
> 
> 
> -
> This message is coming from the emc-pstc discussion list.
> To cancel your subscription, send mail to majord...@ieee.org
> with the single line: "unsubscribe emc-pstc" (without the
> quotes).  For help, send mail to ed.pr...@cubic.com,
> jim_bac...@monarch.com, ri...@sdd.hp.com, or
> roger.volgst...@compaq.com (the list administrators).
> 
> 
> 
> 
> 
> 
> --- Internet Header 
> Sender: owner-emc-p...@ieee.org
> Received: from ruebert.ieee.org (ruebert.ieee.org [199.172.136.3])
>   by spdmgaac.compuserve.com (8.9.3/8.9.3/SUN-1.7) with ESMTP id
NAA03479;
>   Tue, 23 Nov 1999 13:56:40 -0500 (EST)
> Received:  by ruebert.ieee.org (8.9.3/8.9.3)  id NAA08716; Tue, 23 Nov
1999 13:52:01 -0500 (EST)
> Subject: EN60950 3rd Edition?
> To: emc-p...@ieee.org
> Cc: 
> X-Mailer: Lotus Notes Release 5.0.1a August 17, 1999
> Message-ID: 
> From: "Ron Pickard/Hypercom/US" 
> Date: Tue, 23 Nov 1999 11:48:45 -0700
> X-Priority: 3 (Normal)
> X-MIMETrack: Serialize by Router on AZPHXN01/Hypercom/US(Release
5.0.1a|August 17, 1999) at
>  11/23/99 11:48:46 AM
> MIME-Version: 1.0
> Content-type: text/plain; charset=us-ascii
> Sender: owner-emc-p...@ieee.org
> Precedence: bulk
> Reply-To: "Ron Pickard/Hypercom/US" 
> X-Resent-To: Multiple Recipients 
> X-Listname: emc-pstc
> X-Info: Help requests to  emc-pstc-requ...@majordomo.ieee.org
> X-Info: [Un]Subscribe requests to  majord...@majordomo.ieee.org
> X-Moderator-Address: emc-pstc-appro...@majordomo.ieee.org
> 
> 


Best regards,
Kevin Richardson

Stanimore Pty Limited
(Technology Products Standards, Regulations and Compliance Specialists)
Ph: 02-4329-4070Fax:02-4328-5639
Int'l:  +61-2-4329-4070 +61-2-4328-5639 
Email:  k...@compuserve.com (Internet)
kevin.richard...@ieee.org (Alternate Internet #1)
k...@technologist.com (Alternate Internet #2)
100356,374 (Compuserve)

-
This message is coming from the emc-pstc discussion list.
To cancel your subscription, send mail to majord...@ieee.org
with the single line: "unsubscribe emc-pstc" (without the
quotes).  For help, send mail to ed.pr...@cubic.com,
jim_bac...@monarch.com, ri...@sdd.hp.com, or
roger.volgst...@compaq.com (the list administrators).



Re: EN60950 Earth Leakage Measurement Circuit.

1999-11-25 Thread Paul McCoy

Duncan,
I will take a stab at this since if I really mess up and get flamed by 
various
and sundry members of the group I at least won't know about it until I get back
from a four day weekend.
Based on my understanding of the requirements there is good news and bad 
news.
The good news is you should not have to meet the tolerance spec; at least not as
far as having to use a precision capacitor RATED at 1% tolerance. You need a
capacitor with the proper voltage rating that's actual value is between 0.uF
and 0.2178uF. Theoretically you can measure the value of a group of 20% 0.22uF
capacitors and find one that is within 1% and use it.
The word "theoretically" above brings me to the bad news. The distribution 
of
values around the mean tends to be skewed, and it is unlikely you will find a 
20%
capacitor that is actually 1% because the manufacturer normally preselects and
sorts a batch, removing the 1%, then the 5%, then the 10%, and finally the 20% 
(or
whatever tolerances they offer). You will get two peaks in the distribution near
the positive and negative bounds.
Luckily there is some more good news (or least not terribly bad) if you can
live with a four capacitor network. Go back to that bin of 20% caps and start
measuring actual values again. This time you are looking for a pair of 
capacitors
whose values add to about 0.44uF. When you find one pair look for a second. 
connect
each pair in parallel (0.44uF), and then connect the two parallel pairs in 
series
(0.22uF). I wouldn't want to design that for a production run product, but a 
little
mix and match for test equipment shouldn't be too bad if you can live with four
capacitors.

I hope this helps,

Paul McCoy


duncan.ho...@snellwilcox.com wrote:

> Group,
> I am trying to construct a simple earth leakage test circuit as in Annex D
> of EN60950. I am finding it impossible to find a capacitor for Cs (0.22uF) as 
> I
> cannot find one that is the required value, tolerence and voltage rating.
>
> Am I missing somthing here? Even if I use a network of capacitors I would have
> to use quite a few of them to get the right value! It would appear that the 1%
> tolerence that is requested is a bit unrealistic given the value and required
> voltage rating.
>
> Has anybody else found this and if so how was it resolved? Are there any
> manufacturers of earth leakage testers who may be able to hint on how they
> manage to overcome this?
> Any suggestions would be greatly recieved...
> thanks,
> Duncan.
>
> -
> This message is coming from the emc-pstc discussion list.
> To cancel your subscription, send mail to majord...@ieee.org
> with the single line: "unsubscribe emc-pstc" (without the
> quotes).  For help, send mail to ed.pr...@cubic.com,
> jim_bac...@monarch.com, ri...@sdd.hp.com, or
> roger.volgst...@compaq.com (the list administrators).


-
This message is coming from the emc-pstc discussion list.
To cancel your subscription, send mail to majord...@ieee.org
with the single line: "unsubscribe emc-pstc" (without the
quotes).  For help, send mail to ed.pr...@cubic.com,
jim_bac...@monarch.com, ri...@sdd.hp.com, or
roger.volgst...@compaq.com (the list administrators).