Re: [PSES] GFCI Receptacles

2024-04-05 Thread Ralph McDiarmid
NFPA can be viewed free online, however, CSA C22.1, C22.3, and C22.3 appear
to be by purchase only.

 

 

Ralph

 

From: Don Gies <2f2a08db2fba-dmarc-requ...@listserv.ieee.org> 
Sent: Friday, April 5, 2024 11:20 AM
To: EMC-PSTC@LISTSERV.IEEE.ORG
Subject: Re: [PSES] GFCI Receptacles

 

Hi Steve, 

 

Hope all is well with you.  

 

See the National Electrical Code, NFPA 70, Article 210.8 for the list of
locations that require GFCI in the US.

 

In Canada, see Canadian Electrical Code, Part I, CSA C22.1, Rule 26-704 and
26-710, as well as other locations for GFCI requirements.

 

Best regards,

 

DON GIES

Field Service Engineer

 



 

p   +1 346 313 6216

e   donald.g...@non.se.com <mailto:donald.g...@non.se.com> 

w  gutor.com

 

17 Capitol Reef Road

Howell, NJ 07731

United States

 



 

 

 

 

General

From: sgbrody mailto:sgbr...@comcast.net> > 
Sent: Monday, March 25, 2024 21:18
To: EMC-PSTC@LISTSERV.IEEE.ORG <mailto:EMC-PSTC@LISTSERV.IEEE.ORG> 
Subject: [PSES] GFCI Receptacles

 

[External email: Use caution with links and attachments]

  _  

 

Esteemed experts:

 

It has always been what I thought was the requirement for GFCI receptacles
was only when the product or system was intended for a wet or damp location.

 

A system a client is having an NRTL fo a Field Evaluation on had receptacles
and they are being told they need to be GFCI.

 

NFPA-79 15.1.1 requires this only for receptacles to be used for, e.g.,
handheld power tools, test equipment, and other accessories.

 

The questions are:

- What is the definition of accessories as used in NFPA-79,

 - And is it written in any other standard where and when GFCI outlets are
required?

 

Thank you.

 

 

 

 

Sent from my T-Mobile 5G Device

 

  _  

This message is from the IEEE Product Safety Engineering Society emc-pstc
discussion list. To post a message to the list, send your e-mail to
EMC-PSTC@LISTSERV.IEEE.ORG <mailto:EMC-PSTC@LISTSERV.IEEE.ORG>  

All emc-pstc postings are archived and searchable on the web at: 
https://www.mail-archive.com/emc-pstc@listserv.ieee.org/ 

Website: https://ewh.ieee.org/soc/pses/  <https://ewh.ieee.org/soc/pses/> 
Instructions: https://ewh.ieee.org/soc/pses/list.html (including how to
unsubscribe) <https://ewh.ieee.org/soc/pses/list.html> 
List rules: https://ewh.ieee.org/soc/pses/listrules.html 

For help, send mail to the list administrators:
Mike Sherman at: msherma...@comcast.net <mailto:msherma...@comcast.net> 
Rick Linford at: linf...@ieee.org <mailto:linf...@ieee.org>  

For policy questions, send mail to:
Jim Bacher at: j.bac...@ieee.org <mailto:j.bac...@ieee.org>  

  _  

To unsubscribe from the EMC-PSTC list, click the following link:
https://listserv.ieee.org/cgi-bin/wa?SUBED1=EMC-PSTC
<https://listserv.ieee.org/cgi-bin/wa?SUBED1=EMC-PSTC&A=1> &A=1 

  _  

This message is from the IEEE Product Safety Engineering Society emc-pstc
discussion list. To post a message to the list, send your e-mail to
EMC-PSTC@LISTSERV.IEEE.ORG <mailto:EMC-PSTC@LISTSERV.IEEE.ORG>  

All emc-pstc postings are archived and searchable on the web at: 
https://www.mail-archive.com/emc-pstc@listserv.ieee.org/
<https://www.mail-archive.com/emc-pstc@listserv.ieee.org/%20>  

Website: https://ewh.ieee.org/soc/pses/  <https://ewh.ieee.org/soc/pses/> 
Instructions: https://ewh.ieee.org/soc/pses/list.html (including how to
unsubscribe) <https://ewh.ieee.org/soc/pses/list.html> 
List rules: https://ewh.ieee.org/soc/pses/listrules.html 

For help, send mail to the list administrators:
Mike Sherman at: msherma...@comcast.net <mailto:msherma...@comcast.net> 
Rick Linford at: linf...@ieee.org <mailto:linf...@ieee.org>  

For policy questions, send mail to:
Jim Bacher at: j.bac...@ieee.org <mailto:j.bac...@ieee.org>  

  _  

To unsubscribe from the EMC-PSTC list, click the following link:
https://listserv.ieee.org/cgi-bin/wa?SUBED1=EMC-PSTC
<https://listserv.ieee.org/cgi-bin/wa?SUBED1=EMC-PSTC&A=1> &A=1 


-

This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
EMC-PSTC@LISTSERV.IEEE.ORG

All emc-pstc postings are archived and searchable on the web at:
https://www.mail-archive.com/emc-pstc@listserv.ieee.org/

Website:  https://ewh.ieee.org/soc/pses/
Instructions:  https://ewh.ieee.org/soc/pses/list.html (including how to 
unsubscribe)
List rules: https://ewh.ieee.org/soc/pses/listrules.html

For help, send mail to the list administrators:
Mike Sherman at: msherma...@comcast.net
Rick Linford at: linf...@ieee.org

For policy questions, send mail to:
Jim Bacher:  
_
To unsubscribe from the EMC-PSTC list, click the following link: 
https://listserv.ieee.org/cgi-bin/wa?SUBED1=EMC-PSTC&A=1


Re: [PSES] GFCI Receptacles

2024-04-05 Thread Don Gies
Hi Steve,

Hope all is well with you.

See the National Electrical Code, NFPA 70, Article 210.8 for the list of 
locations that require GFCI in the US.

In Canada, see Canadian Electrical Code, Part I, CSA C22.1, Rule 26-704 and 
26-710, as well as other locations for GFCI requirements.

Best regards,

DON GIES
Field Service Engineer

[cid:image001.png@01DA8763.4E110020]

p   +1 346 313 6216
e   donald.g...@non.se.com
w  gutor.com

17 Capitol Reef Road
Howell, NJ 07731
United States

[cid:image002.png@01DA8763.4E110020]





General
From: sgbrody 
Sent: Monday, March 25, 2024 21:18
To: EMC-PSTC@LISTSERV.IEEE.ORG
Subject: [PSES] GFCI Receptacles


[External email: Use caution with links and attachments]




Esteemed experts:

It has always been what I thought was the requirement for GFCI receptacles was 
only when the product or system was intended for a wet or damp location.

A system a client is having an NRTL fo a Field Evaluation on had receptacles 
and they are being told they need to be GFCI.

NFPA-79 15.1.1 requires this only for receptacles to be used for, e.g., 
handheld power tools, test equipment, and other accessories.

The questions are:
- What is the definition of accessories as used in NFPA-79,
 - And is it written in any other standard where and when GFCI outlets are 
required?

Thank you.




Sent from my T-Mobile 5G Device



This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
EMC-PSTC@LISTSERV.IEEE.ORG<mailto:EMC-PSTC@LISTSERV.IEEE.ORG>
All emc-pstc postings are archived and searchable on the web at:
https://www.mail-archive.com/emc-pstc@listserv.ieee.org/

Website: https://ewh.ieee.org/soc/pses/
Instructions: https://ewh.ieee.org/soc/pses/list.html (including how to 
unsubscribe)<https://ewh.ieee.org/soc/pses/list.html>
List rules: https://ewh.ieee.org/soc/pses/listrules.html

For help, send mail to the list administrators:
Mike Sherman at: msherma...@comcast.net<mailto:msherma...@comcast.net>
Rick Linford at: linf...@ieee.org<mailto:linf...@ieee.org>

For policy questions, send mail to:
Jim Bacher at: j.bac...@ieee.org<mailto:j.bac...@ieee.org>



To unsubscribe from the EMC-PSTC list, click the following link: 
https://listserv.ieee.org/cgi-bin/wa?SUBED1=EMC-PSTC&A=1

-

This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
EMC-PSTC@LISTSERV.IEEE.ORG

All emc-pstc postings are archived and searchable on the web at:
https://www.mail-archive.com/emc-pstc@listserv.ieee.org/

Website:  https://ewh.ieee.org/soc/pses/
Instructions:  https://ewh.ieee.org/soc/pses/list.html (including how to 
unsubscribe)
List rules: https://ewh.ieee.org/soc/pses/listrules.html

For help, send mail to the list administrators:
Mike Sherman at: msherma...@comcast.net
Rick Linford at: linf...@ieee.org

For policy questions, send mail to:
Jim Bacher:  
_
To unsubscribe from the EMC-PSTC list, click the following link: 
https://listserv.ieee.org/cgi-bin/wa?SUBED1=EMC-PSTC&A=1


[PSES] GFCI Receptacles

2024-03-25 Thread sgbrody
Esteemed experts:It has always been what I thought was the requirement for GFCI 
receptacles was only when the product or system was intended for a wet or damp 
location.A system a client is having an NRTL fo a Field Evaluation on had 
receptacles and they are being told they need to be GFCI.NFPA-79 15.1.1 
requires this only for receptacles to be used for, e.g., handheld power tools, 
test equipment, and other accessories.The questions are:- What is the 
definition of accessories as used in NFPA-79, - And is it written in any other 
standard where and when GFCI outlets are required?Thank you.Sent from my 
T-Mobile 5G Device

-

This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
EMC-PSTC@LISTSERV.IEEE.ORG

All emc-pstc postings are archived and searchable on the web at:
https://www.mail-archive.com/emc-pstc@listserv.ieee.org/

Website:  https://ewh.ieee.org/soc/pses/
Instructions:  https://ewh.ieee.org/soc/pses/list.html (including how to 
unsubscribe)
List rules: https://ewh.ieee.org/soc/pses/listrules.html

For help, send mail to the list administrators:
Mike Sherman at: msherma...@comcast.net
Rick Linford at: linf...@ieee.org

For policy questions, send mail to:
Jim Bacher:  
_
To unsubscribe from the EMC-PSTC list, click the following link: 
https://listserv.ieee.org/cgi-bin/wa?SUBED1=EMC-PSTC&A=1